<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2>On the "Project & Site" tab, under "Simulation 
Options" where it says "Entire Year" you can set the start and end 
dates of your simulation.  The default is Jan 1 to Dec 31.  If you are 
going to simulate less than a 12 month period I suggest you also specify heating 
and cooling design days for equipment sizing.  If you don't use design 
days I believe equest will autosize based on the 3-4 day simulation period you 
specify.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2>regards,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2>mike</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008>
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left>
<DIV align=left><FONT face="Arial Black" size=1></FONT></DIV><FONT 
face="Arial Black" size=1>P: 413-458-9870</FONT> <FONT face="Arial Black" 
size=1>C: 413-652-1087</FONT></DIV></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=796443616-25032008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Cory 
Abramowicz<BR><B>Sent:</B> Tuesday, March 25, 2008 12:11 AM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Building Flush-out 
Simulation<BR></FONT><BR></DIV>
<DIV></DIV>Hello Everyone,<BR><BR>I recently constructed my building in eQuest 
and with it, one of the things I would like to do is figure out how much energy 
is used when abiding by the criteria of LEED EQ credit 3.2.  14,000 cubic 
feet of outside air must be provided while maintaining the building at 60 
degrees F and RH of no higher than 60%.  The systems would be on for 3-4 
days and I was thinking of simulating it during the spring sometime.  Does 
anyone have any ideas to go about this? Thank you for your help.<BR 
clear=all><BR>-- <BR>Cory J. Abramowicz<BR>Penn State Architectural Engineering 