<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=iso-8859-1">
<TITLE></TITLE>

<META content="MSHTML 6.00.6000.16608" name=GENERATOR></HEAD>
<BODY>
<P><FONT size=2>Ying,<BR><BR>If you have a heating coil in the air 
handler&nbsp;one needs to inputm the HOT DECK MAX LEAVING TEMP (HEAT SET-T)- and 
this enable the Heat Control input. The HOT DECK MAX LEAVING TEMP (HEAT SET-T) 
should be set to the primary air temperature leaving the air handler. If the 
HEAT SET-T air temperature is not specified, the primary air temperature will be 
the mixed air temperature, which could result in a significant increase in 
reheat energy depending on the climate. <BR>Hope this 
helps,<BR>Mitch<BR><BR><BR>Mitchell J. Dec<BR>Senior Energy Analyst<BR>LEEDŽ 
Accredited Professional<BR><BR>320 SW Washington, Suite 200<BR>Portland, OR 
97204-2640<BR>T.&nbsp; 503.227.5280&nbsp; F. 503.274.7674<BR>Direct: 
503.345.6283<BR><BR>Thinking. Inside the building.<BR><A 
href="http://www.glumac.com/" 
target=_blank>http://www.glumac.com/</A><BR><BR><BR><BR>-----Original 
Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[<A 
href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</A>]On 
Behalf Of<BR>yizhao1@vt.edu<BR>Sent: Thursday, February 28, 2008 5:00 PM<BR>To: 
bldg-sim@lists.onebuilding.org<BR>Subject: [Bldg-sim] Supply temperature reset 
in ASHRAE baseline<BR><BR><BR>Hi -<BR>In the baseline, ASHRAE requires a supply 
air temperature reset for system 5,<BR>packaged rooftop VAV w/ reheat 
(G3.1.3.12). In the air side system level, I can<BR>set up a schedule for cool 
control, but heat control is in grey.<BR>Does anyone know how to input the reset 
in the system? Economizer is 
inlcuded.<BR><BR>Thanks!<BR><BR>Ying<BR><BR>_______________________________________________<BR>Bldg-sim 
mailing list<BR><A 
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" 
target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To 
unsubscribe from this mailing list send&nbsp; a blank message to 
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR></FONT></P></BODY></HTML>