<DIV dir=ltr align=left><SPAN class=265574215-15022008>Matthew</SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008>Please remember that 
ASHRAE 90.1 defines fenestration area as the rough opening for any window 
assembly including glazing , frame and sash, see the definitions in Section 3 of 
the standard.  The minimum performance requirements for fenestration 
include the performance of the frames.  The frame 
area should be accounted for in your calculation of fenestration area and 
performance.</SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008>Michael</SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008>
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left>
<DIV align=left><FONT face="Arial Black" size=1></FONT></DIV><FONT 
face="Arial Black" size=1>P: 413-458-9870</FONT> <FONT face="Arial Black" 
size=1>C: 413-652-1087</FONT></DIV>  </SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=265574215-15022008></SPAN> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Leonard 
Sciarra<BR><B>Sent:</B> Thursday, February 14, 2008 7:07 PM<BR><B>To:</B> 
Michael Rosenberg; Higgins, Matthew<BR><B>Cc:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] Glas Curtain 
Wall - Appendix G<BR><BR></DIV>
<DIV></DIV>
<DIV dir=ltr align=left><SPAN class=598085323-14022008>Matthew, </SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=598085323-14022008>If the clear glass, 
vision glass, daylight glass or whatever is greater than 40% reduce it 
proportionally to 40% and use the prescriptive 90.1 chapter 5 values.  For 
the remainder of the building (opaque portions) you then use (for U-factor) 
the 'steel framed' wall values.</SPAN></DIV>
<DIV dir=ltr align=left><SPAN lang=en-us><U><FONT face=Verdana 
color=#b7b7b7>          </FONT><FONT 
face=Verdana 
color=#b6b6b6>                                          <BR></FONT></U><B><FONT 
face=Verdana>Leonard Sciarra,</FONT></B><FONT face=Arial></FONT> <FONT 
face=Verdana>AIA, LEED<SUP>®</SUP> 
ap<BR>Associate<BR>312.577.6580  Direct<BR>312.456.0123  Main</FONT><FONT 
face=Arial><BR></FONT></SPAN><A title=mailto:leonard_sciarra@gensler.com 
href="mailto:leonard_sciarra@gensler.com"><SPAN lang=en-us 
title=mailto:leonard_sciarra@gensler.com><U 
title=mailto:leonard_sciarra@gensler.com></U><U 
title=mailto:leonard_sciarra@gensler.com><FONT 
title=mailto:leonard_sciarra@gensler.com face=Arial 
color=#0000ff>leonard_sciarra@gensler.com</FONT></U></SPAN></A><SPAN 
lang=en-us><BR><U></U><U></U><U><FONT face=Verdana 
color=#bbbbbb>                                                     <BR></FONT></U><B><FONT 
face=Verdana color=#f40000>Gensler<BR></FONT></B><FONT face=Verdana>30 West 
Monroe<BR>Suite 400<BR>Chicago, Illinois 60603<BR>USA</FONT><FONT 
face=Arial> </FONT></SPAN></DIV>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Michael 
Rosenberg<BR><B>Sent:</B> Thursday, February 14, 2008 1:33 PM<BR><B>To:</B> 
Higgins, Matthew<BR><B>Cc:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> 
Re: [Bldg-sim] Glas Curtain Wall - Appendix G<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>Matthew,</DIV>
<DIV> </DIV>
<DIV>I think what you need to do is pull the opaque portion of the curtain wall 
out. If the remaining glazing fraction is above 40%, than that portion needs to 
be reduced in you baseline model. </DIV>
<DIV> </DIV>
<DIV>Mike</DIV>
<DIV> </DIV>
<DIV>Michael Rosenberg<BR>Oregon Department of Energy<BR>625 Marion St. 
N.E.<BR>Salem, OR 97301-3742<BR>Phone : (503) 373-7809<BR>Fax: (503) 
373-7806<BR><BR>>>> Matthew Higgins <higgins@edi-arch.com> 
2/14/2008 10:29:05 AM >>><BR></DIV>
<DIV style="COLOR: #000000">Michael - I assume you saw my previous post? 
(Below).... What I am wondering is how LEED/ASHRAE 90.1-2004 Appendix-G treats 
glass curtain walls in baseline models: either as a curtain wall with 90.1 
climate-specific glass properties or if I need to reduce the amount of glazing 
to 40% (the prescriptive maximum Window/Wall ratio).<BR><BR>Your 
thoughts?<BR><BR>*PREVIOUS POST*<BR><BR>Has anyone modeled, submitted, and 
certified a LEED building with a <BR>glass curtain wall?<BR><BR>I ask because I 
am wondering how to treat the curtain wall in the <BR>baseline model. I've tried 
two scenarios thus far and there is a 10% <BR>consumption difference between 
them. The only thing that differs between <BR>the two is that the lower 
consuming model has a 40% window-to-wall area <BR>where the other is still a 
glass curtain wall, but using Appendix G <BR>window properties. And to put this 
in perspective the curtain wall is <BR>facing NNE and is 3 stories 
high.<BR><BR>I would also truly appreciate any reference to a LEED CIR regarding 
this <BR>issue, if there is one.<BR><BR>Matthew Higgins, LEED AP<BR>Technical 
Specialist<BR>Environmental Dynamics, Inc.<BR>Architecture and Sustainability 
Consulting Services<BR>505.242.2851<BR><BR><BR><BR>Matthew Higgins 
wrote:<BR><BR>>Has anyone modeled, submitted, and certified a LEED building 
with a <BR>>glass curtain wall?<BR>><BR>>I ask because I am wondering 
how to treat the curtain wall in the <BR>>baseline model. I've tried two 
scenarios thus far and there is a 10% <BR>>consumption difference between 
them. The only thing that differs between <BR>>the two is that the lower 
consuming model has a 40% window-to-wall area <BR>>where the other is still a 
glass curtain wall, but using Appendix G <BR>>window properties. And to put 
this in perspective the curtain wall is <BR>>facing NNE and is 3 stories 
high.<BR>><BR>>I would also truly appreciate any reference to a LEED CIR 
regarding this <BR>>issue, if there is one.<BR>><BR>>  
<BR>><BR><BR>_______________________________________________<BR>Bldg-sim 
mailing list<BR><A 
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To 
unsubscribe from this mailing list send  a blank message to 
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR></DIV></BODY></HTML>