I believe RESNET allows for credit for infiltration reduction below 0.35 ACH for confirmed construction (blower door tested).<br><br>In my opinion, leaving out infiltration is a major fault of ASHRAE 90.1 and Appendix G (and LEED).&nbsp; Reducing infiltration through good building techniques and attention to detail can have an enormous impact on building energy use.&nbsp; Yes, the building must be tested in order to receive credit, but infiltration needs to be brought to the attention for designers and owners.&nbsp; Also, ensuring that the air barrier is OUTSIDE the insulation (not the interior sheetrock) is essential to ensuring the performance of the insulation.<br>
<br>I recently completed an evaluation for an existing historic building about to undergo renovations.&nbsp; The biggest single potential energy saver?&nbsp; Infiltration reduction.&nbsp; Will we get LEED credit for this?&nbsp; No.<br><br>~karen~<br>
<br><div class="gmail_quote">On Feb 13, 2008 11:17 AM, Michael Tillou &lt;<a href="mailto:michael.tillou@gmail.com">michael.tillou@gmail.com</a>&gt; wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
Nick,<br><br>ASHRAE 90.1 doesn&#39;t allow any credit for infiltration savings for commercial<br>buildings and doesn&#39;t have any specific guidance about an allowable air<br>tightness value. &nbsp;When using Appendix G or Chapter 11 ECB you need to keep<br>
infiltration the same in both the proposed design and the energy budget.<br><br>The IECC and RESNET HERS offer a method for infiltration savings in<br>Low-Rise/Single Family Residential. &nbsp;I believe both methods allow a minimum<br>
as-designed infiltration of ACH = 0.35. &nbsp;The baseline uses weather factors<br>from ASHRAE 136 and a Normalized Leakage value of 0.57. &nbsp;The IECC also<br>requires a post-construction blower door test to verify the savings.<br>
<br>You could probably propose an exception calculation for infiltration credit<br>if it followed the IECC residential method and the proposed building was a<br>small building with simple systems. &nbsp;I certianly don&#39;t think it would be<br>
applicable for a large multi-story building with complex systems. &nbsp; I think<br>that you would also need to be able to demonstrate the as-built (post<br>construction) infiltration rate, through blower door testing or other<br>
appropriate means, as part of proposed exception calculation.<br><br>Best regards,<br><br>Mike<br><div class="Ih2E3d"><br><br><br>-----Original Message-----<br>From: <a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>] On Behalf Of Nick Doylend<br>Sent: Tuesday, February 12, 2008 3:58 PM<br>To: <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: [Bldg-sim] 90.1 and infiltration/air-tightness?<br><br></div><div><div></div><div class="Wj3C7c">Hi, I&#39;m wondering if 90.1 makes any stipulations regarding building air<br>infiltration, for example can there be a difference between proposed design<br>
and energy budget building? &nbsp;I can&#39;t seem to find any reference to facade<br>air tightness but the standard is a pretty dense document to wade though.<br>Is there a more easily digested summary available anywhere?<br>
<br>Thanks,<br><br>Nick<br>_______________________________________________<br>Bldg-sim mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send &nbsp;a blank message to<br><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br>_______________________________________________<br>Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>To unsubscribe from this mailing list send &nbsp;a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>