Hi Franc,<br><br>I too have spent many hours struggling with ERVs in eQuest.<br><br>First of all, a sensible heat recovery ventilator will not recover much energy during the cooling season. Remember that energy recovery ventilators recover nearly no energy at dT less than 5F. Also, in the summer, the moisture content of the air is usually higher, so much of the energy available to be recovered is latent.<br>
<br>Second, running an HRV requires additional fan power. I have found eQuests default fan power to be a bit high, so check the these numbers to make sure they are appropriate for your project.<br><br>Third, if a building is equipped with an HRV, but no economizer, the HRV will be recovering energy when it is not desired.<br>
<br>If the HRV has a bypass for outdoor air, you can set the HRV controls to allow bypass of OA, set ERV-CAP-CTRL to "bypass OA". If the air handler also has an economizer, set ERV-RUN-CTRL to "when minimum OA"<br>
<br>This should bring the cooling energy close to the baseline (and perhaps slightly lower). The fan energy will increase. Savings will vary by climate. You may want to experiment with a sensible heat exchanger, if it is appropriate for the application. We usually use total energy recovery wheels, unless they are inappropriate for the application (lab buildings, for example).<br>
<br><br>hope this helps.<br><br>~karen~<br><br><div class="gmail_quote">On Feb 13, 2008 10:12 AM, Sever, Franc <<a href="mailto:SeverFranc@karpinskieng.com">SeverFranc@karpinskieng.com</a>> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div>
<p><span lang="en-us"><font face="Arial" size="2">Hello All,</font></span>
</p>
<p><span lang="en-us"><font face="Arial" size="2">I am fairly new to eQuest and this is my first post to this group. I am modeling a university building which has an air handling unit with a heating coil and chilled water coil supplied by campus steam and chilled water. My problem is that when I add energy recovery to the air system the space heating energy goes down but my cooling energy goes up as compared to the proposed building without energy recovery. I am using a sensible HX with OA DT of 10 F, OA heating and cooling, mixed air reset, and modulating the hx. I hope all this makes sense, but I also tried setting the energy recovery to only OA heating and the cooling load still went up considerably. </font></span></p>
<p><span lang="en-us"><font face="Arial" size="2">Any help would be greatly appreciated. Thank you and have a great day.</font></span><span lang="zu"></span>
</p>
<p><span lang="en-us"><font color="#000000" face="Arial" size="2">Franc J. Sever</font></span>
<br><span lang="en-us"><font color="#000000" face="Arial" size="2">Engineer, Mechanical</font></span>
</p>
<p><span lang="en-us"><font color="#ff0000" face="Arial">Karpinski</font></span>
<br><span lang="en-us"><font color="#000000" face="Arial" size="1">ENGINEERING</font></span>
<br><span lang="en-us"><font color="#000000" face="Arial" size="2">3135 Euclid Avenue</font></span>
<br><span lang="en-us"><font color="#000000" face="Arial" size="2">Cleveland, OH 44115</font></span>
<br><span lang="en-us"><font color="#ff0000" face="Arial" size="2">P</font><font color="#000000" face="Arial" size="2"> 216-391-3700</font></span>
<br><span lang="en-us"><font color="#ff0000" face="Arial" size="2">F</font><font color="#000000" face="Arial" size="2"> 216-391-0108</font></span>
<br><span lang="en-us"><font color="#ff0000" face="Arial" size="2">E</font><font color="#000000" face="Arial" size="2"> </font><u> <font color="#0000ff" face="Arial" size="2"><a href="mailto:FSever@karpinskieng.com" target="_blank">FSever@karpinskieng.com</a></font></u></span>
</p>
<br>
<br>
</div>
<br>_______________________________________________<br>Bldg-sim mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br><br>