<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>I've recently coded 
the equations in ASHRAE 55 (2004) for calculating PMV and PPD and cross 
referenced these to ISO 7730:2005 (the reference ASHRAE gives).  There are 
several differences:</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>1) line 250 - ASHRAE 
has an extra factor of 6.45 in the equation</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>2) line 300 - ISO 
has (TRA/100)*4, ASHRAE (TRA/100)**4</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>3) line 480 - ISO 
has (TRA/100**4), ASHRAE has (TRA/100)**4</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>4) line 520 - ISO 
does not define a value for HL6 (ASHRAE has this on line 
490)</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>I believe that 
difference (1) is unimportant as its setting the initial guess for an iterative 
loop.  However, for the other three differences I believe that ASHRAE is 
correct and ISO has typos.</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>I also have 
differences in the output from the example cases.  The differences 
are:</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>1) ASHRAE cases 3 
and 6 give 11% PPD (the standard has 10%)</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>2) ISO case 7 gives 
8% PPD (the standard has 10%)</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>The ASHRAE cases do 
not concern me too much as the PMV is the same to one decimal place, but the PMV 
in the ISO standard is quite different (0.50 in the std, 0.36 by my 
calculations).</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>Does 
anyone:</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>1) disagree with my 
conclusions as to the differences in the printed code (i.e. you do not think ISO 
has typos)?</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial size=2>2) have any insights 
as to the numerical differences (I think that there may be a typo in the ISO 
standard)?</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2>Thanks,</FONT></SPAN></DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=000573514-05022008><FONT face=Arial 
size=2>Iain</FONT></SPAN></DIV>
<DIV> </DIV>
<DIV align=left>
<DIV align=left><FONT size=1><FONT face=Arial><FONT color=#808080><SPAN 
class=265514018-30052006>Dr. </SPAN>Iain Macdonald, 
Ph.D.</FONT></FONT></FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Research Officer / Agent 
de recherches</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Indoor Environment 
Research program / Programme de recherche sur l'environnement 
intérieur</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Institute for Research in 
Construction / Institut de recherche en construction</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>National Research Council 
Canada / Conseil national de recherches Canada</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>1200 Montréal Road / 1200 
chemin Montréal</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Ottawa Ontario K1A 
0R6</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Phone/Tél: (613) 
993-9676</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Fax: (613) 
954-3733</FONT></DIV>
<DIV align=left><FONT face=Arial color=#808080 size=1>Email: </FONT><A 
href="mailto:iain.macdonald@nrc-cnrc.gc.ca"><FONT face=Arial color=#808080 
size=1>iain.macdonald@nrc-cnrc.gc.ca</FONT></A></DIV></DIV>
<DIV> </DIV></BODY></HTML>