<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.2900.3243" name=GENERATOR></HEAD>
<BODY text=#000000 bgColor=#ffffff>
<DIV dir=ltr align=left><SPAN class=770592215-30012008><FONT face=Arial 
color=#0000ff size=2>I cannot comment on Energy+.  However, as far as 
eQUEST, I've modeled a natatorium (indoor pool) including the latent load.  
In one of the ASHRAE books, there's a methodology for determining the latent 
loads of a pool as a function of activity, water temperature, and I believe a 
few other factors.  I ran through these calculations and inputted this load 
into the "Internal Energy Sources" under the Equipment internal gains tab.  
I created a schedule based on when the proposed pool cover would be off (pool in 
use), and called it a "process" load. I believe I set the Latent HG ratio to 1.0 
and Sensible to 0.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=770592215-30012008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=770592215-30012008><FONT face=Arial 
color=#0000ff size=2>The results of my model seemed to be reasonable.  
</FONT></SPAN></DIV>
<DIV> </DIV>
<DIV><SPAN class=770592215-30012008></SPAN><FONT face=Arial><FONT 
color=#0000ff><FONT size=2>M<SPAN class=770592215-30012008>aybe with this 
methodology, it might allow you figure something out with Energy+; otherwise, 
eQUEST may be your best, closest approximation, for this 
project.</SPAN></FONT></FONT></FONT><BR></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Dusko 
Nikolic<BR><B>Sent:</B> Wednesday, January 30, 2008 2:20 AM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Swimming pool 
modeling<BR></FONT><BR></DIV>
<DIV></DIV>Hi,<BR><BR>Is it possible to model swimming pool in Energy+? I could 
not find the way to model latent loads due to water 
evaporation<BR><BR><BR><BR>Thanks<BR><BR><FONT face=sans-serif 
size=2><BR></FONT><IMG src="cid:770592215@30012008-00CF"><FONT 
face="Arial Narrow" color=#5f5f5f size=3><B><BR>Dusko Nikolic</B></FONT><FONT 
face="Arial Narrow" color=#5f5f5f size=2><B><BR>Mechanical Building Services 
Engineer</B></FONT><FONT face="Arial Narrow" color=#5f5f5f size=1><BR>MWH New 
Zealand 
Ltd               
          DDI:  (64-9) 580 
4531<BR>Level 2, Building C, Millennium Centre    Fax: (64-9) 580 
7600<BR>600 Great South Road<BR>PO Box 12-941, Penrose<BR>Auckland, New 
Zealand<BR><BR></FONT><A href="http://www.mwhglobal.com/nz"><FONT 
face="Arial Narrow" color=#5f5f5f 
size=1><U>http://www.mwhglobal.com/nz</U></FONT></A><FONT face="Arial Narrow" 
color=#5f5f5f size=2><BR></FONT><IMG src="cid:770592215@30012008-00D6"><FONT 
face="Arial Narrow" color=#5f5f5f size=2><BR></FONT><FONT face=sans-serif 
size=2><BR></FONT><BR></BODY></HTML>