Hello all,<br><br>I am modeling a building with eQUEST that has a
tankless, a.k.a. instantaneous, gas-fired hot water heater.  I am
uncertain of how to baseline the system according to ASHRAE 90.1-2004
Appendix G. The standard states that for a 180,000 BTU/h system the EF
(Energy Factor) = 0.62-0.0019V.  So, I set V equal to zero for the
tankless/instantaneous gas water heater and get an EF =0.62.  <br>
<br>
The question I have for everyone is: How do I translate this baseline
EF to HIR (Heat-input-ratio) for eQUEST?  Is there an accepted method
for doing so?  I saw in a previous post from David Eldridge on 3/21/07 that
calculating HIR = 1/EF leads to unreasonably high values for HIR (In my
example, 1/0.62 = 1.61), but I'm having trouble seeing how else to come
up with a baseline.<br>
<br>
Thanks in advance for your help.<br>