<HTML xmlns="http://www.w3.org/TR/REC-html40" xmlns:v = "urn:schemas-microsoft-com:vml" xmlns:o = "urn:schemas-microsoft-com:office:office" xmlns:w = "urn:schemas-microsoft-com:office:word" xmlns:m = "http://schemas.microsoft.com/office/2004/12/omml"><HEAD>
<META http-equiv=Content-Type content="text/html; charset=utf-8">
<META content="MSHTML 6.00.2900.3243" name=GENERATOR>
<STYLE>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        mso-believe-normal-left:yes;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</STYLE>
</HEAD>
<BODY lang=EN-US style="MARGIN: 4px 4px 1px; FONT: 10pt Tahoma" vLink=purple link=blue>
<DIV>Short answer:&nbsp;Yes.&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>The temperature &amp; humidity&nbsp;of the dummy/duct zone is used in place of the outside air to the system/zones which include the OA-FROM-SYS command. With no loads in this zone, its conditions should be the same as the supply air. To&nbsp;simulate proper&nbsp;dehumidification&nbsp;when modeling a DOAS as PSZ, the zone cooling setpoint schedule&nbsp;would need to be set to 55F or so, and the real DOAS&nbsp;capacities should probably be entered manually. Other model system/zone combinations generally&nbsp;better represent&nbsp;actual&nbsp;DOAS&nbsp;operation, and should be provided as discussion or example by the program authors.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Fred Porter</DIV>
<DIV>AEC</DIV>
<DIV>&nbsp;</DIV>
<DIV><BR>&gt;&gt;&gt; "Kevin Kyte" &lt;kkyte@robsonwoese.com&gt; 1/8/2008 10:02 AM &gt;&gt;&gt;<BR></DIV>
<DIV class=Section1>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">I understand that doe2.2 cannot accurately model energy recovery in these conditions.&nbsp; Would the zones receiving the outside air from the system at least receive the same tempered air as the dummy zone in the system?&nbsp; <o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">Kevin<o:p></o:p></SPAN></P>
<DIV>
<DIV style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p>&nbsp;</o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">From:</SPAN></B><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'"> Fred Porter [mailto:FPorter@archenergy.com] <BR><B>Sent:</B> Friday, December 14, 2007 3:30 PM<BR><B>To:</B> bldg-sim@lists.onebuilding.org; Kevin Kyte<BR><B>Subject:</B> Re: Equest: ERU with added heat and vfd's<o:p></o:p></SPAN></P></DIV></DIV>
<P class=MsoNormal><o:p>&nbsp;</o:p></P>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">Folks;<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">Whatever else maybe wrong or right with these approaches, eQ/DOE-2.2 cannot generally&nbsp;correctly model energy recovery in the OA-FROM-SYS.&nbsp; This is because the exhaust/return air to the OA-FROM-SYS in a DOE-2 model&nbsp;is&nbsp;NOT from the&nbsp;occupied spaces, it is&nbsp;from the dummy/duct zone, which should never be&nbsp;at the room/return air conditions in either the model or reality. (It will usually&nbsp;be substantially cooler.)&nbsp;Too bad, because many&nbsp;real&nbsp;DOAS systems, (which would appear to&nbsp;be best represented&nbsp;with&nbsp;DOE-2's OA-FROM-SYS) include&nbsp;heat recovery and pre-conditioning.<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">&nbsp;<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">Anyone know if&nbsp;any of the other "typical" simulation programs (TRACE, E+)&nbsp;represent a&nbsp;DOAS supplying zonal&nbsp;HVAC more correctly? Obviously one could model&nbsp;them in TRNSYS, and IES-VE.<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">&nbsp;<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">Fred Porter<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">AEC<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">&nbsp;<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">P.S. I did actually once whip up a convoluted DOE-2.2&nbsp;"workaround" for this arrangement. But I will not post it here because it really does not qualify as "simulation;" calling it a brittle kludge would be charitable. <o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">&nbsp;<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'"><BR>&gt;&gt;&gt; "Kevin Kyte" &lt;kkyte@robsonwoese.com&gt; 12/14/2007 11:59 AM &gt;&gt;&gt;<BR><BR><BR>I am attempting to model an energy recovery unit (ERU) supplying outside air<BR>for 5 air handling units (AHUs).&nbsp; I have attempted to do this thus far by<BR>making the ERU a separate system PSZ with dumbo zone and the AHUs use ERU<BR>for OA-FROM-SYSTEM.&nbsp; <BR><BR><BR><BR>The problem lies within energy recovery capacities, the ERV report<BR>capacities are nowhere near as high as the designed energy recovered so the<BR>coiling coil is undersized and I am getting a lot of inadequate cooling<BR>capability warnings.&nbsp; The ERU has an additional gas furnace but no<BR>additional cooling.<BR><BR><BR><BR>This is where I may be getting it mixed up because I set the<BR>COOLING-SCHEDULE flagged to off for the entire year and I end up with no<BR>energy recover on the cooling side.&nbsp; Even if I were to change the ERU to<BR>type PVAVS or SZRH it shows minimal or no recovery.&nbsp; How should I schedule<BR>cooling?<BR><BR><BR><BR>Are any other parameters that I may be missing, I have included the enthalpy<BR>wheel effectiveness and a control sequence.&nbsp; How about humidity controls?<BR>Since this suppose to be a LEED certified building will ECMs be necessary?<BR>Or should I go back to doing individual heat recovery for each AHU?&nbsp; So many<BR>questions.<BR><BR><BR><BR>Kevin<BR><BR><BR><BR>From: Brian Fountain [mailto:bfountain@greensim.com] <BR>Sent: Wednesday, November 21, 2007 11:27 AM<BR>To: kkyte@robsonwoese.com; BLDG-SIM@gard.com<BR>Subject: RE: [BLDG-SIM] Equest: ERU with added heat and vfd's<BR><BR><BR><BR>The way I would do it is to use the OA-FROM-SYSTEM keyword and add the ERU<BR>as a separate system with ventilation heat recovery.&nbsp; In this way, you can<BR>define the heat recovery and power and flow characteristics of the ERU<BR>explicitly.&nbsp; <BR><BR><BR><BR>I usually do this by first creating a very small (1 sq-ft) dummy space, then<BR>a dummy thermal zone for that space.&nbsp; Then, create the ERU as a 100% OA<BR>constant volume system serving that thermal zone.&nbsp; Now comes the fun part.<BR>You close eQUEST, open the .inp with a text editor and cut the new system<BR>and all its keywords from the bottom of the list of systems and paste it to<BR>the top of the system list.&nbsp; If you don't do this, when you run the<BR>simulation, it will complain that the OA-FROM-SYSTEM system referenced does<BR>not precede the current system and will abort the sim.&nbsp; Now, reopen eQUEST<BR>and in your 6 systems, use the OA-FROM-SYSTEM keyword on the system, OA tab<BR>to define that the ventilation air is coming from your ERU.&nbsp; <BR><BR><BR><BR>Hope this helps.<BR><BR><BR><BR>-----Original Message-----<BR>From: BLDG-SIM@gard.com [mailto:BLDG-SIM@gard.com] On Behalf Of Kevin Kyte<BR>Sent: November 21, 2007 10:55 AM<BR>To: BLDG-SIM@gard.com<BR>Subject: [BLDG-SIM] Equest: ERU with added heat and vfd's<BR><BR><BR><BR>Simulating an energy recovery unit which serves six air handling units.&nbsp; I<BR>suppose this is simply enough, I split the total cfm into percentages for<BR>each unit and incorporate into each unit's heat recovery, yes?&nbsp; Is there any<BR>way to include additional heat from the energy recovery unit? Perhaps split<BR>the total heat into percentages and include this in each unit's heating<BR>capacity.&nbsp; How about variable frequency drives on supply and exhaust fans<BR>for energy recovery unit?&nbsp; Perhaps this could be modeled as a 10% reduction<BR>in the fan power similar to occupancy sensors on lights?&nbsp; Regarding LEED,<BR>would usgbc need a credit interpretation request for something like this or<BR>maybe just mentioning it as a default overridden in the submittal would<BR>suffice.&nbsp; Would anyone who has encountered this care to chime in?&nbsp; Any<BR>suggestions would be forthcoming.&nbsp; Thank you.<BR><BR><BR><BR>Kevin Kyte, LEED AP<BR><BR>Jr. Mechanical Engineer<BR><BR>RobsonWoese, Inc.<BR><BR>T:&nbsp; 716-636-1800<BR><BR>F:&nbsp; 716-636-1856<BR><BR><BR><BR>From: BLDG-SIM@gard.com [mailto:BLDG-SIM@gard.com] On Behalf Of Zhen Tian<BR>Sent: Tuesday, November 20, 2007 5:38 PM<BR>To: BLDG-SIM@gard.com<BR>Subject: [BLDG-SIM] add ceiling in eQUEST<BR><BR><BR><BR>Dear all,<BR><BR>When I model a one-floor building in eQUEST, I found that adding the "lay-in<BR>acoustic tile" ceiling (no insulation added) will cause the peak load<BR>through roof to zero. When eliminate the ceiling, a large part of the<BR>building heat flow will go through the roof.<BR><BR>I also tried several buildings. When added ceiling, then the heat flow<BR>through roof turns to zero. Does anyone have an idea why this happens? <BR><BR>Thanks a lot.<BR><BR>Regards,<BR><BR>David<BR><BR>&nbsp; <BR><BR>&nbsp; _____&nbsp; <BR><BR>Be a better sports nut! Let your teams follow you with Yahoo Mobile. Try<BR>&lt;<A href="http://us.rd.yahoo.com/evt=51731/*http:/mobile.yahoo.com/sports;_ylt=At9_qD">http://us.rd.yahoo.com/evt=51731/*http:/mobile.yahoo.com/sports;_ylt=At9_qD</A><BR>KvtAbMuh1G1SQtBI7ntAcJ &gt;&nbsp; it now.<BR><BR><BR><BR>==================<BR>You received this e-mail because you are subscribed <BR>to the BLDG-SIM@GARD.COM mailing list.&nbsp; To unsubscribe <BR>from this mailing list send a blank message to <BR>BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>-------------- next part --------------<BR>An HTML attachment was scrubbed...<BR>URL: <A href="http://lists.onebuilding.org/pipermail/bldg">http://lists.onebuilding.org/pipermail/bldg</A>-sim-onebuilding.org/attachments/20071214/ed8e4973/attachment.htm <BR>_______________________________________________<BR>Bldg-sim mailing list<BR>Bldg-sim@lists.onebuilding.org<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<o:p></o:p></SPAN></P></DIV></DIV></BODY></HTML>