color=#0000ff size=2>Timothy, I respectfully disagree with some of your opinions 
(and Brandon's) about how Appendix G unfairly penalizes building 
designs.  First off calling it a "penalty" mis-represents what Appendix G 
is trying to accomplish.  The goal of Appendix G is  to 
create a theoretical energy budget for a building based on the minimum 
requirements of ASHRAE 90.1.  A methodology for creating an energy 
budget has to be the same for every building that uses it.  This 
is the reason why Appendix G originally required banded windows and is the 
reason it is important to have a building rotation requirement to represent 
orientation. </FONT></SPAN></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007>Timothy, you're right, architects often have little 
control over building sites and often there is nothing that can be done 
about how a building gets sited in an urban environment.  However the 
building energy budget should be blind to that fact. The same building (use 
type, sq.ft., # of floors) in the same climate zone should have the 
same energy budget regardless of its location/orientation.   In 
some cases building orientation will make it easier for a building to have a 
lower EUI and in other cases it will be more difficult but no matter what the 
orientation the basis for making a comparison has to be the 
same.  Designing and constructing a building is an exercise in 
compromise and owners and design teams need to make the hard decisions about 
what is most important.  We have to admit that building a building on 
certain sites is more difficult (from an energy perspective) and then 
use energy modeling as a tool to help architects and engineers improve their 
designs.  We shouldn't be re-writing rules making things easier 
because it sends the message to owners, architects and engineers that they 
don't really have to change the status-quo.</SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007>I agree that Appendix G is still "clunky", I constantly 
wrestle with how to interpret the different aspects of the methodology and get 
frustrated at the effort required to complete the 
modeling.  </SPAN></FONT></FONT></FONT><FONT face=Arial><FONT 
size=2><FONT color=#0000ff><SPAN class=125345014-05122007>The greater flaw (this 
is said with the greatest respect for the countless volunteer hours 
put into creating Appendix G by the ASHRAE 90.1 folks) I see with Appendix 
G is that its genesis was the ECB methodology (Timothy, I think we are in 
agreement about this point) which is intended for demonstrating 
compliance with ASHRAE 90.1.  </SPAN></FONT></FONT></FONT><FONT 
face=Arial><FONT size=2><FONT color=#0000ff><SPAN class=125345014-05122007><FONT 
color=#0000ff>In my opinion revisions to Appendix G need to occur, these changes 
need to take Appendix G away from its "code compliance" roots and towards a 
methodology that is easier to automate via software rule 
sets in a reliable, repeatable way.  Having automated rule sets will 
reduce the chance for gaming and will hopefully make it easier to establish 
an energy budget early in the design process which is what we really 
need.</FONT></SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007>Mike</SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007> 
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=2>Tillou Engineering, 
LLC</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=1>Williamstown, MA 
01267</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=1>P: 
413-458-9870</FONT> <FONT face="Arial Black" size=1>C: 
413-652-1087</FONT></DIV></SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007> </SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT size=2><FONT color=#0000ff><SPAN 
class=125345014-05122007></SPAN></FONT></FONT></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT><FONT face=Arial color=#0000ff 
size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2></FONT><FONT 
face=Arial color=#0000ff size=2></FONT><FONT face=Arial color=#0000ff 
size=2></FONT><FONT face=Arial color=#0000ff size=2></FONT><BR></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com 
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Timothy Moore<BR><B>Sent:</B> 
Tuesday, December 04, 2007 10:43 PM<BR><B>To:</B> 
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] LEED Building 
Orientation<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT face=Arial color=#000080 size=2>Indeed, count me in on submitting a 
change proposal. If I recall, everything we need is on the ASHRAE web site. I 
would be happy to have what I posted used a starting point or initial draft for 
that and hope that others have ideas for making the proposed changes better 
still. After all, if incorporated, you would all be working with it somewhere 
down the road. Now is thus a great time to comment or make 
suggestions.</FONT></DIV>
<DIV><FONT size=2><FONT face=Arial color=#000080 
size=2></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT color=#000080 size=2>Thanks, Jason, for your 
questions regarding my proposal. In response to your last question asking, 
"would it be fair for two identical buildings that are located on two different 
sites, one constrained and one not, to get different scores?: There are many 
situations in which the opportunities related to a site dictate some aspects of 
how well optimized the design can be. Given what I proposed, the situation 
you're asking about would occur only when the <EM>more</EM> constrained site of 
the two was such that it forced a beneficial orientation. In such cases, the 
team with the unconstrained site would be able to compare to a worse baseline 
building, and thus could get a higher score for the same design. They would be 
permitted to do so only because their site included to opportunity to 
neglect orientation---and thus they could have done worse, but they chose to 
make the best of it and chose to do the extra work to get credit for that. The 
incentive is a carrot, not a stick, and LEED is full of carrots that are not 
consistently available to everyone at all times.</FONT></FONT></DIV>
<DIV><FONT size=2><FONT face=Arial color=#000080 
size=2></FONT></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>Thanks, Brandon, for your comments 
(pasted in below) in response to Jason's point/question about how "perhaps 
choosing a bad site that offers limited opportunities to face the building in a 
good direction should carry a negative consequence." I couldn't agree more with 
what you had to say.</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>The idea of punishment for a choice 
that we do not always have the luxury of making is at the root of the issues 
discussed over the last few days. If one <EM>does</EM> overlook the opportunity 
to choose a better site, they will already be faced with the 
consequences of having to design for a worse condition than they could have. 
And, someone else will get the opportunity of choosing the better site they 
overlooked. My take on this is that added design challenge and lost return on 
investment are sufficiently negative consequences (if and when one actually has 
the option to choose otherwise). </FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>It seems to me that the language of 
negative consequences stems in part from the historical regulatory compliance 
perspective of 90.1, which is to prevent designers and builders from making 
really bad buildings, rather than to encourage them to make really good ones. 
Where it is feasible to take advantage of building and/or glazing orientation, 
this needs to be rewarded. My proposal is aimed at doing this without 
problematic attempts to punish those who are less attentive to (or less 
fortunate) regarding this aspects of site selection.</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>If 90.1 Appendix G is to be 
effective, it is essential to avoid provisions that inevitably do as much or 
more harm than good. A penalty for having a large west-facing 
exposure to deal with is very different than, for example, a penalty to 
using excessive glass area or requirement for a given level of insulation 
in a particular climate, since the design team will, in <EM>all</EM> cases, have 
the opportunity to reduce glazing area and to select insulation with an 
appropriate R-value. However, in the case of building sites, if, for example, 
they were all distributed evenly along different sides of a rectangular 
city block with high development density, then, depending on climate and 
building type, somewhere between 50% and 75% of the sites would be penalized for 
being "bad." If this city block happened to be in an established 
part of Chicago or Milwaukee, for example, where city blocks tend to have 
their long axis oriented N-S, the odds of having to build on a "bad" site are 
even higher. Where then is the incentive for making the most of a 
less-than-ideal situation?</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>Where the starting point, and thus 
opportunities to "do the right thing," may vary with arbitrary external 
conditions, the Performance Rating Method needs to focus on positive incentives 
for encouraging teams to make the most of what they have to work with. After 
all, someone has to build on that SW corner site. So, let's re-focus the method 
on rewarding designs that turn a crummy site into a great building. Those who 
are fortunate enough to be able to choose a really good site will still get the 
added benefit of being able to design for that condition and, in some cases, 
lowering their operating costs, improving return on investment, and racking up a 
few more percentage points toward EAc1.</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>Does anyone else have comments or 
suggestions in support of a continuous maintenance/change proposal to ASHRAE? As 
I suggested above, now would be a good time to make your voice 
heard.</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#000080 size=2>Regards,</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2>Timothy</FONT></DIV>
<DIV><FONT face=Arial color=#000080 size=2></FONT> </DIV>
<DIV><FONT size=2>******************************************<BR>Timothy 
Moore<BR>Integrated Sustainable Design Consultant<BR>LEED AP</FONT></DIV>
<DIV> </DIV>
<DIV><FONT size=2>Whole Systems Design<BR>910 Indian Rock Ave.<BR>Berkeley, CA 
94707<BR>Ph: (510) 525-4809<BR>Fx: (413) 480-7252<BR>Cell: (303) 324-1044<BR><A 
href="mailto:tmoore@whole-systems-design.com">tmoore@whole-systems-design.com</A></FONT></DIV>
<DIV><FONT size=2></FONT> </DIV>
<DIV><FONT size=2></FONT> </DIV>
<DIV><FONT size=2></FONT> </DIV>
<DIV>Jason,<BR><BR>The paradigm that we must 'punish bad sites' is one of the 
actual thorns on the burr under my saddle.  Why MUST we punish bad 
sites?  Why not reward designs making the best of a bad site, and sites 
where changing the building orientation is an achievable option?<BR><BR>In my 
humble opinion Timothy's proposals are right on the money in terms of how 
projects work in the real world, and what LEED/ASHRAE 90.1's objectives ought to 
be -- namely, reward achievement of attainable objectives.  On the 
contrary, it's the arbitrary enforcement of this rotation requirement and the 
whole punishment-mindset behind it that actually "misses" something.<BR><BR>OK, 
who wants to collaborate with me in drafting-up a change proposal?  First 
off, does anyone have a copy of a previous change proposal for formatting, 
contact info etc. reference?  Enough talk, time for 
action!<BR><BR>Regards<BR> <BR>Brandon Nichols, PE, LEED® 
AP<BR>Mechanical<BR>HARGIS ENGINEERS<BR>600 Stewart Street<BR>Suite 
1000<BR>Seattle, WA 98101<BR><BR><A 
href="http://www.hargis.biz/">www.hargis.biz</A><BR>d | 206.436.0400  c | 
206.228.8707<BR>o | 206.448.3376  f  | 
206.448.4450<BR><BR><BR>-----Original Message-----<BR>From: Jason Glazer 
[mailto:jglazer@gardanalytics.com] <BR>Sent: Tuesday, December 04, 2007 5:47 
AM<BR>To: <A href="mailto:tcm@berkeley.edu">tcm@berkeley.edu</A><BR>Cc: Brandon 
Nichols; <A href="mailto:Peter.Simmonds@ibece.net">Peter.Simmonds@ibece.net</A>; 
'Leonard Sciarra'; <A 
href="mailto:chien.harriman@iesve.com">chien.harriman@iesve.com</A><BR>Subject: 
Re: [BLDG-SIM] LEED Building Orientation</DIV>
<DIV><FONT size=2></FONT> </DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=BrandonN@Hargis.biz href="mailto:BrandonN@Hargis.biz">Brandon 
  Nichols</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Tuesday, December 04, 2007 3:42 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] LEED Building 
  Orientation</DIV>
  <DIV><BR></DIV><BR>All,<BR><BR>Enough talk, time for action!  Who wants 
  to collaborate in drafting-up a change proposal?  Timothy, it sounds like 
  you're on board.  <BR><BR>First off, does anyone have a copy of a 
  previous change proposal for formatting, contact info etc. 
  reference?<BR><BR>Regards<BR> <BR>Brandon Nichols, PE, LEED® 
  AP<BR>Mechanical<BR>HARGIS ENGINEERS<BR>600 Stewart Street<BR>Suite 
  1000<BR>Seattle, WA 98101<BR><BR><A 
  href="http://www.hargis.biz">www.hargis.biz</A><BR>d | 206.436.0400  c | 
  206.228.8707<BR>o | 206.448.3376  f  | 
  206.448.4450<BR><BR><BR>-----Original Message-----<BR>From: Jason Glazer 
  [mailto:jglazer@gardanalytics.com]<BR>Sent: Tuesday, December 04, 2007 5:47 
  AM<BR>To: <A href="mailto:tcm@berkeley.edu">tcm@berkeley.edu</A><BR>Cc: 
  Brandon Nichols; <A 
  href="mailto:Peter.Simmonds@ibece.net">Peter.Simmonds@ibece.net</A>; 'Leonard 
  Sciarra'; <A 
  href="mailto:chien.harriman@iesve.com">chien.harriman@iesve.com</A><BR>Subject: 
  Re: [BLDG-SIM] LEED Building Orientation<BR><BR>Timothy,<BR><BR>One issue that 
  your proposals miss is that perhaps choosing a bad site that offers limited 
  opportunities to face the building in a good direction should carry a negative 
  consequence. Shouldn't a building that is on a good site and oriented in such 
  a way to reduce energy use be rated better than a building located on a poor 
  site that cannot be oriented well?  Also would it be fair for two 
  identical buildings that are located on two different sites, one constrained 
  and one not, to get different scores?<BR><BR>Again, please feel free to submit 
  a continuous maintenance proposal to ASHRAE.<BR><BR>Jason<BR><BR>On 12/3/2007 
  3:06 AM, Timothy Moore wrote:<BR>> Jason, Brandon, and others doing 
  building simulation for LEED:<BR>> <BR>>  <BR>> <BR>> Great 
  to see all of the discussion this topic is generating. It seems <BR>> well 
  worth considering how better to provide an incentive for <BR>> orientation 
  without needless hassles and penalties. If you're <BR>> interested in doing 
  so, please read on and comment.<BR>> <BR>>  <BR>> <BR>> The 
  90.1-2004 Appendix G requirement for averaging the results of four <BR>> 
  baseline building orientations is, as described by previous comments <BR>> 
  in this discussion, a somewhat arbitrary and often problematic means <BR>> 
  of attempting to give credit (or penalty) for building orientation. It 
  <BR>> can also be a time-consuming pain either when overshadowing from 
  <BR>> adjacent buildings is modeled (fixed shades), and thus the site shape 
  <BR>> and coordinate origin may not make sense for a rotated building, or 
  <BR>> when attempting to compare benefits over the baseline model related 
  to <BR>> specific strategies (i.e., baseline+X vs. baseline+Y, 
  acknowledging <BR>> that relative comparisons of strategies can and should 
  most often <BR>> still be made without ever rotating anything).<BR>> 
  <BR>>  <BR>> <BR>> Of potentially even greater concern, in some 
  cases, such as on a very <BR>> narrow site with N-S major axis, the current 
  requirement needlessly <BR>> penalizes (i.e., /deducts/ credit from) a 
  design that may be making <BR>> the best of a constrained situation. Thus, 
  even if the process of <BR>> generating and averaging baseline performance 
  results for all four <BR>> orientations were /fully/ automated in the 
  simulation tools, which <BR>> would alleviate the time and hassle, the 
  current approach would still <BR>> impose an unfair and unhelpful penalty 
  on certain projects that are <BR>> forced to orient their building along a 
  N-S axis or with a large SE, SW, or W exposure, etc.<BR>> <BR>>  
  <BR>> <BR>> However, I agree that we /do/ need some method of 
  encouraging and <BR>> rewarding beneficial building orientations where 
  applicable.<BR>> <BR>>  <BR>> <BR>> It appears the draft 
  Addendum R language that was never approved was <BR>> one idea for how to 
  address some of the issues described above. I <BR>> would hazard a guess 
  that it was not approved because of the tendency <BR>> for such language of 
  "exceptions" to become a loophole open to <BR>> interpretation and gaming, 
  and thus something likely to weaken the <BR>> performance rating method and 
  generate more work for reviewers, not to <BR>> mention superfluous LEED 
  credit interpretation rulings.<BR>> <BR>>  <BR>> <BR>> I 
  support the idea of a positive incentive or opportunity offered by <BR>> 
  the /_option_/ for comparing to the averaged results for the rotated <BR>> 
  baseline building, plus a similar /_option_/ with respect to glazing <BR>> 
  orientation, /if/ and /when/ permitted by straightforward criteria. I <BR>> 
  would propose the following requirements be met for the /optional/ use 
  <BR>> of such averaged values for the baseline building...<BR>> 
  <BR>>  <BR>> <BR>> The project would need to show simple 
  documentation that one of the <BR>> two options was indeed applicable, and 
  thus they should be permitted <BR>> to use the associated method for 
  adjusting the baseline building results:<BR>> <BR>>  <BR>> 
  <BR>> *Option 1)* Demonstrate via a simple sketch or other graphic <BR>> 
  representation that there is space on the site for the same total <BR>> 
  building footprint area to be re-shaped to be either more nearly <BR>> 
  square in terms of solar orientation OR to be rotated at least 60 <BR>> 
  degrees (or similar value TBD) from the design orientation---thus _it <BR>> 
  would have been possible and plausible to neglect building <BR>> 
  orientation_. In this case the team would be permitted to compare to <BR>> 
  an average of rotated baseline building results as in 90.1-2004 <BR>> 
  Appendix G. As with Appendix G, overshadowing from adjacent buildings, 
  <BR>> etc. would need to be modeled as a fixed shading item that does not 
  <BR>> rotate with the building. For cases where the proposed building 
  <BR>> orientation is elongated and rotated by something less than 60 
  degrees <BR>> (or whatever similar threshold was established for this 
  option)---for <BR>> example, rotated 45 degrees from the orientation of the 
  major axis of <BR>> the site, adjacent road, adjacent buildings, etc.---and 
  there is not <BR>> enough space on the site to rotate it a full 60 degrees, 
  the team <BR>> should be permitted (if they see fit) to compare to a 
  baseline result <BR>> that is the average of just two orientations of the 
  very same<BR>> footprint: the proposed orientation and whatever they 
  believe to be <BR>> the worst orientation of the /same/ /footprint shape/ 
  that would <BR>> actually still fit on the site. If Option #1 were 
  selected, doing so <BR>> would eliminate Option #2 in order to avoid double 
  counting.<BR>> <BR>>  <BR>> <BR>> *Option 2)* Demonstrate 
  with simple table of summed values that the <BR>> glazing fraction or 
  window-to-wall ratio (WWR) for the facades on the <BR>> proposed design is 
  asymmetric in terms of orientation (e.g., <BR>> differences are greater 
  than 5%), AND confirm that this is NOT an <BR>> outcome forced by an 
  immediately adjacent building or other constraint <BR>> of the physical 
  building site, but rather a deliberate design <BR>> strategy---thus _the 
  design /could/ have neglected any such <BR>> orientation of WWR_. In this 
  case the team would be permitted to <BR>> compare their design to a 
  baseline with /identical/ WWR for all façade <BR>> orientations---i.e., 
  evenly distributed glazing as indicated by WWR (but /not/ a rotated building, 
  as in Option #1).<BR>> <BR>>  <BR>> <BR>> The idea here is to 
  permit teams to get credit for either building <BR>> orientation OR glazing 
  orientation on the building _if they believe it <BR>> to be significant_ 
  AND _it would have been possible to neglect it_.<BR>> <BR>>  
  <BR>> <BR>> If neither of these options were applicable and implemented, 
  the <BR>> baseline building would simply be modeled in the same orientation 
  as <BR>> the proposed design and with the same proportional distribution of 
  <BR>> WWR, in keeping with 90.1 WWR limits.<BR>> <BR>>  <BR>> 
  <BR>> I do not believe it is workable to penalize those who neglect 
  <BR>> orientation, as the present Appendix G attempts to do, without 
  <BR>> creating other inappropriate penalties and deterrents that we all 
  <BR>> really could do without. The penalty for those who neglect 
  orientation <BR>> where there was a significant potential to benefit from 
  doing <BR>> otherwise would, in what I have proposed, simply be the 
  foregone <BR>> opportunity to do better and get credit for it. Thus 
  building <BR>> orientation would be recognized and treated in much the same 
  manner as <BR>> most other performance-related architectural design 
  strategies.<BR>> <BR>>  <BR>> <BR>> I'm interested in what 
  others think of these ideas as possible means <BR>> of addressing concerns 
  raised in this discussion. Perhaps, Jason, you <BR>> could forward this to 
  the 90.1 committee people that are involved <BR>> specifically with the 
  Performance Rating Method (along with related or <BR>> subsequent comments 
  from others on the BLDG-SIM forum). Hopefully we <BR>> can move this 
  forward.<BR>> <BR>>  <BR>> <BR>> Best,<BR>> <BR>> 
  Timothy<BR>> <BR>>  <BR>> <BR>> Timothy Moore,<BR>> 
  <BR>> LEED AP, Design Consultant, Building Performance Simulation<BR>> 
  <BR>>  <BR>> <BR>> Whole Systems Design<BR>> <BR>> 910 
  Indian Rock Ave.<BR>> <BR>> Berkeley, CA 94707<BR>> <BR>>  
  <BR>> <BR>> Office: 510-525-4809<BR>> <BR>> Mobile: 
  303-324-1044<BR>> <BR>> eFax: 413-480-7252<BR>> <BR>> <A 
  href="mailto:tmoore@whole-systems-design.com">tmoore@whole-systems-design.com</A><BR>> 
  <<A 
  href="mailto:tmoore@whole-systems-design.com">mailto:tmoore@whole-systems-design.com</A>><BR>> 
  <BR>> <BR>>  <BR>> <BR>> 
  ----------------------------------------------------------------------<BR>> 
  --<BR>> *From:* <A href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of <BR>> *Brandon Nichols<BR>> 
  *Sent:* Friday, November 30, 2007 11:22 AM<BR>> *To:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A><BR>> *Cc:* <A 
  href="mailto:Peter.Simmonds@ibece.net">Peter.Simmonds@ibece.net</A>; Leonard 
  Sciarra<BR>> *Subject:* [BLDG-SIM] LEED Building Orientation<BR>> 
  <BR>> Thanks Jason,<BR>> <BR>> The 'burr' under my saddle on this 
  issue is that the 'averaged <BR>> buiilding', and therefore the baseline to 
  which all project EEMs are <BR>> to be compared, /_does not exist_/, not 
  even in the simulation software.<BR>> <BR>> While we may have four 
  perfectly good orientations, any one of which <BR>> could be used as a 
  baseline (think .SIM file), there simply exists <BR>> /_no .SIM file for 
  the averaged building_/.  It would need to be <BR>> created (as of 
  this writing) manually, and the result could not be <BR>> used easily, let 
  alone seamlessly, as the baseline for alternative comparisons within 
  eQuest.<BR>> <BR>> Suggestions:<BR>> <BR>> 1. Allow selecting the 
  orientation closest to, without performing <BR>> worse than, the 'average 
  total annual energy consumption' as the baseline.<BR>> This simple change 
  would allow all baseline numbers to reside within <BR>> the analysis 
  software.<BR>> <BR>> 2. Make this requirement optional, for those 
  buildings which can <BR>> benefit from orientation optimization.  In 
  other words, promote <BR>> achievable incentives instead of enforcing 
  arbitrary punishments.<BR>> <BR>> Wish I had more time to help out with 
  90.1 -- maybe next year!<BR>> Regards<BR>> <BR>> Brandon Nichols, PE, 
  LEED® AP<BR>> Mechanical<BR>> HARGIS ENGINEERS<BR>> <BR>> 600 
  Stewart Street<BR>> Suite 1000<BR>> Seattle, WA 98101<BR>> <A 
  href="http://www.hargis.biz">www.hargis.biz</A><BR>> <BR>> d | 
  206.436.0400  c | 206.228.8707<BR>> o | 206.448.3376  f  | 
  206.448.4450<BR>> <BR>> <BR>> <BR>> -----Original 
  Message-----<BR>> From: Jason Glazer 
  [mailto:jglazer@gardanalytics.com]<BR>> Sent: Friday, November 30, 2007 
  8:04 AM<BR>> To: <A 
  href="mailto:Peter.Simmonds@ibece.net">Peter.Simmonds@ibece.net</A>; Brandon 
  Nichols<BR>> Subject: Re: [BLDG-SIM] LEED Building Orientation<BR>> 
  <BR>> Peter and Brandon,<BR>> <BR>> This looks like an issue that you 
  have a strong opinion so perhaps <BR>> consider contributing a better 
  solution. Anyone can propose a change <BR>> to 90.1. Further, if you 
  examine this history of the ECB subcommittee, <BR>> I think you would find 
  that we are open to good ideas and are trying <BR>> to balance multiple 
  needs. The building rotation concept replaced a <BR>> much worse concept of 
  spreading the windows around the building evenly.<BR>>   Maybe 
  you can find a better solution. I believe we need to reward <BR>> those 
  that do make an effort to orient their building<BR>>   and 
  windows to save energy and penalize those that make poor design <BR>> 
  choices about building orientation and window placement.  The building 
  <BR>> rotation idea has traction because most of the effort needed for each 
  <BR>> rotation is just to rerun the simulation with the building azimuth 
  <BR>> changed. We thought that was simple.  It is an issue that has 
  been <BR>> discussed many times in the ECB subcommittee and a few times at 
  the <BR>> full committee level.<BR>> <BR>> I look forward to your 
  suggestions.<BR>> <BR>> Jason<BR>> <BR>> <BR>> <BR>> On 
  11/30/2007 8:34 AM, Peter Simmonds wrote:<BR>>  > Here here 
  Brandon. A building is a building and that's that. I have<BR>> > sat 
  through many charette's  on 'tree hugging' projects to hear how <BR>> 
  > the buildings orientation can affect the cooling and heating 
  load,<BR>> let  > alone natural daylighting. Only to hear the wise 
  men of 90.1 <BR>> (who have  > never designed a building) to come 
  up with some <BR>> 'weighted' average to  > change the results. The 
  designer ends up <BR>> doing four different runs  > only to find 
  out that the architect <BR>> didn't have clue what he was  > trying 
  to do in the first place.<BR>>  ><BR>>  ><BR>>  
  ><BR>>  > Long live sanity.<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Peter Simmonds Ph.D.<BR>>  
  ><BR>>  > Associate<BR>>  > IBE Consulting 
  Engineers<BR>>  ><BR>>  > 14130 Riverside Drive Suite 
  201<BR>>  ><BR>>  > Sherman Oaks, CA 91423<BR>>  
  > p:   (818) 377-8220<BR>>  > f:    
  (818) 377-8230<BR>>  > m:  (818) 219-1284<BR>>  > 
  IDEAS FOR THE BUILT ENVIRONMENT <BLOCKED::http://www.ibece.com/>  
  ><BR>> > This e-mail message, including any attachments, is for the 
  sole use<BR>> of  > the intended recipient(s) and may contain 
  confidential and <BR>> privileged  > information. Any unauthorized 
  review, use, disclosure, <BR>> or distribution  > is prohibited. If 
  you are not the intended <BR>> recipient, please contact  > the 
  sender by reply e-mail and destroy <BR>> all copies of the original 
  message.<BR>>  ><BR>>  ><BR>> 
  ----------------------------------------------------------------------<BR>>  
  > --<BR>>  ><BR>>  > *From:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of<BR>> > *Brandon Nichols  
  > *Sent:* Thursday, November 29, 2007 5:48 PM  ><BR>> *To:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>  > *Subject:* 
  [BLDG-SIM] LEED Building <BR>> Orientation  >  >  
  >  > All,  >  >  >  > The building 
  rotation <BR>> requirement is utterly nonsensical.  For a  > 
  full-text rant on the <BR>> subject, see my previous post:<BR>>  
  ><BR>>  ><BR>>  ><BR>>  > <A 
  href="http://www.gard.com/ml/bldg-sim-archive/msg04038.html">http://www.gard.com/ml/bldg-sim-archive/msg04038.html</A><BR>>  
  ><BR>>  ><BR>>  ><BR>>  > In 
  summary:<BR>>  ><BR>>  ><BR>>  
  ><BR>>  > 1) In the case of many new buildings (90% or more I 
  would <BR>> estimate),  > there is very little latitude for 
  changing the orientation.<BR>>  > For example the main street and 
  therefore the lobby and entryway <BR>> may  > be on one side and 
  one side only of the building, the aspect <BR>> ratio of  > the 
  building may not fit on the lot in two of the four orientations, 
  etc.<BR>>  ><BR>>  ><BR>>  ><BR>>  
  > 2) The fictitious, etheral 'averaged' building does not exist even 
  <BR>> in  > the computer code of the best analysis programs we have 
  at our<BR>> > disposal to date.<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > 3) All baseline numbers for each of 
  the four orientations would <BR>> need  > to be extracted from the 
  analysis software, and averaged on a <BR>> spreadsheet.<BR>>  > 
  Similarly each and every EEM would need to be extracted, and the  > 
  <BR>> project's comparative analysis done on a spreadsheet instead of 
  the  > <BR>> within the analysis software itself.  Thanks, but 
  I have a life, wife<BR>> > and family.<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > 4) If this requirement still sounds 
  like a good idea from the <BR>> comfort  > of your tenured office, 
  I say come on out and run couple of <BR>> dozen  > real-life energy 
  code and LEED compliance simulations for me <BR>> within  > budget 
  and on deadline in Q1-Q2 2008 and you'll begin to <BR>> understand  
  > what I'm talking about.<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Why not simply allow selecting the 
  orientation closest to, without<BR>> > performing worse than, the 
  'average' as the baseline?  This simple <BR>> > change would allow 
  the baseline numbers to reside within the<BR>> analysis  > 
  software.<BR>>  ><BR>>  ><BR>>  
  ><BR>>  > Alternatively the eQuest developers are rumored to be 
  working on a<BR>> > 90.1 Appendix G compliance module.  Upon 
  release, if it automates<BR>> the  > averaging I may be inclined 
  retire some portion of this diatribe.<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Best idea yet, drop this as a 
  requirement, and make it optional <BR>> where  > it makes sense to 
  do so. Utilize by default the far more <BR>> intuitive  > (and 
  useful in terms of energy incentives) 'code minimum'<BR>> baseline  
  > building, oriented identically to the proposed.  This is <BR>> 
  the approach  > I've been able to convince our state energy code and 
  <BR>> utility rebate  > reviewers to accept -- its just hardened 
  LEED <BR>> extremists who still  > seem to have their head in the 
  sand on this.<BR>>  ><BR>>  ><BR>>  
  ><BR>>  ><BR>>  ><BR>>  > 
  Regards<BR>>  ><BR>>  ><BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Brandon Nichols, PE, LEED^® 
  AP<BR>>  ><BR>>  > Mechanical<BR>>  
  ><BR>>  > **HARGIS ENGINEERS**<BR>>  ><BR>>  
  > 600 Stewart Street<BR>>  ><BR>>  > Suite 
  1000<BR>>  ><BR>>  > Seattle, WA 98101<BR>>  
  ><BR>>  > <A 
  href="http://www.hargis.biz">www.hargis.biz</A><BR>>  
  ><BR>>  ><BR>>  ><BR>>  > *d |* 
  206.436.0400  *c | *206.228.8707  >  > *o |* 
  206.448.3376  *f<BR>> |* 206.448.4450  >  >  
  >  >  >  >  >  ><BR>> 
  ----------------------------------------------------------------------<BR>>  
  > --<BR>>  ><BR>>  > *From:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of<BR>> > <A 
  href="mailto:*Edward.A.Decker@jci.com">*Edward.A.Decker@jci.com</A>  > 
  *Sent:* Thursday, November 29, 2007 3:59<BR>> PM  > *To:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>  > *Cc:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>  > *Subject:* 
  <BR>> [BLDG-SIM] LEED Building Orientation  >  >  > 
  Can you not apply <BR>> various fenestrations and shading to the 
  model  > without having to <BR>> change its orientation? For an 
  existing building,  > including LEED <BR>> EB, what additional 
  benefit could be gained by rotating  > the model <BR>> since you 
  cannot change the orientation?<BR>>  > 
  _____________________________________________<BR>>  > Edward A. 
  Decker<BR>>  ><BR>>  ><BR>>  > *"Leonard 
  Sciarra" <<A 
  href="mailto:leonard_sciarra@gensler.com">leonard_sciarra@gensler.com</A>>* 
  Sent by:<BR>>  > <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A><BR>>  
  ><BR>>  > 11/29/2007 06:18 PM<BR>>  ><BR>>  
  > Please respond to<BR>>  > <A 
  href="mailto:leonard_sciarra@gensler.com">leonard_sciarra@gensler.com</A><BR>>  
  ><BR>>  >      <BR>>  
  ><BR>>  > To<BR>>  ><BR>>  
  >      <BR>>  ><BR>>  > 
  <<A href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>><BR>>  
  ><BR>>  > cc<BR>>  ><BR>>  
  >      <BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Subject<BR>>  
  ><BR>>  >      <BR>>  
  ><BR>>  > [BLDG-SIM] LEED Building Orientation  >  
  >  >  >  ><BR>>  
  >      <BR>>  ><BR>>  
  ><BR>>  ><BR>>  ><BR>>  ><BR>>  
  ><BR>>  > This is true, however, even with an existing building, 
  you as the<BR>> > designer/engineer have the option of "working" the 
  facades and  ><BR>> applying appropriate fenestration, shading, 
  etc... you can still make<BR>> > good/bad decisions and the fact that 
  your footprint is fixed should <BR>> > not give the design team a waiver 
  from the fact that the sun still <BR>> > rises in the east and sets in 
  the west.  In fact it may be a benefit <BR>> > if perhaps your 
  building is shaded on the west by itself.<BR>>  ><BR>>  
  > Leonard Sciarra, AIA, LEED ap<BR>>  > 312.577.6580 
  (Dir)<BR>>  > G E N S L E R | Architecture & Design Worldwide 
  30 West Monroe <BR>> Street  > Chicago IL, 60603  > 
  312.456.0123  > <BR>> <A 
  href="mailto:leonard_sciarra@gensler.com">leonard_sciarra@gensler.com</A>  
  >  >  >  ><BR>> 
  ----------------------------------------------------------------------<BR>>  
  > --<BR>>  ><BR>>  > *From:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of<BR>> > *Ross-Bain, Jeff*  
  > Sent:* Thursday, November 29, 2007 2:40 PM*  ><BR>> To:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>*  > Cc:* <A 
  href="mailto:keith_lane@g-g-d.com">keith_lane@g-g-d.com</A>*  > 
  Subject:* <BR>> [BLDG-SIM] LEED Building Orientation  >  > 
  Here is my question to and <BR>> response from the USGBC regarding this 
  issue:<BR>>  ><BR>>  ><BR>>  > Dear LEED 
  Info,<BR>>  ><BR>>  > There has been a lot of chat on 
  this item and I wonder if there is <BR>> a  > USGBC position - I 
  found no reference to this in the CIR's:<BR>>  ><BR>>  > 
  Do existing buildings undergoing renovation require the four-point<BR>> 
  > compass orientation analysis?<BR>>  ><BR>>  
  ><BR>>  ><BR>>  > Jeffrey,<BR>>  
  ><BR>>  > If the existing building being renovated is pursuing 
  LEED-NC rather<BR>> > than LEED-EB, then it would indeed be required to 
  undergo the  ><BR>> specified analysis.  This analysis is used 
  to establish the baseline<BR>> > for energy performance using the ASHRAE 
  standard.  LEED doesn't have <BR>> > any specific exemptions for 
  existing buildings in this requirement, <BR>> > but if ASHRAE has some 
  kind of exemption, we will honor that.<BR>>  ><BR>>  
  ><BR>>  > So I guess the question then becomes an interpretation 
  of the <BR>> Appendix  > G (Table G3.1 (f)) comment for existing 
  buildings. Rotate or not?<BR>>  ><BR>>  > My take has 
  always been that new buildings have the option to <BR>> consider  > 
  orientation but existing buildings cannot be re-oriented <BR>> so 
  rotating  > the model does not really prove anything.<BR>>  
  ><BR>>  > Any 90.1 code committee members or others out there 
  have an <BR>> interpretation?<BR>>  ><BR>>  > 
  Regards,<BR>>  ><BR>>  > */Jeffrey G. Ross-Bain, PE, 
  LEED/*<BR>>  > Smith Dalia Architects<BR>>  > 621 North 
  Ave NE<BR>>  > Suite C-140<BR>>  > Atlanta, GA, 
  30308<BR>>  > 404-892-2443 _<BR>>  > _www.smithdalia.com 
  <<A 
  href="http://www.smithdalia.com/">http://www.smithdalia.com/</A>>  
  >  > P *Consider <BR>> the environment.* *Please don't print 
  this e-mail unless  > you really <BR>> need to.*  >  
  >  >  ><BR>> 
  ----------------------------------------------------------------------<BR>>  
  > --<BR>>  ><BR>>  ><BR>>  > *From:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of<BR>> > *Neuhauser, Ken*  
  > Sent:* Thursday, November 29, 2007 2:31 PM*  ><BR>> To:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>*  > Cc:* <A 
  href="mailto:keith_lane@g-g-d.com">keith_lane@g-g-d.com</A>*  > 
  Subject:* <BR>> [BLDG-SIM] LEED Building Orientation  >  > 
  I am not the authority, <BR>> Keith, but I believe that your 
  interpretation  > (that existing <BR>> buildings do not get rotated 
  in the baseline) is  > consistent with <BR>> the intent of Appendix 
  G.  In new construction, the  > decisions <BR>> regarding 
  building orientation will affect performance and  > that <BR>> 
  performance should be measured against the baseline (although,  > 
  <BR>> there are cases, such as a building that adjoins buildings to 
  either<BR>> > side, where rotating the baseline through all four 
  orientations does <BR>> > not make sense).  If you're improving an 
  existing building, the  ><BR>> existing conditions of building 
  enclosure components, including  > <BR>> orientation, are an 
  appropriate baseline.  When we apply Appendix G to<BR>> > existing 
  buildings, we have also found that "existing building envelopes"<BR>>  
  > sometimes needs to be parsed into existing building envelope 
  components.<BR>>  >  For example, in a mill rehab, the bearing 
  walls may be serviceable<BR>> > and appropriately modeled "as is" in the 
  baseline, but missing<BR>> windows  > or windows that are clearly 
  not serviceable we model as per <BR>> the ASHRAE  > minimum 
  compliance.<BR>>  ><BR>>  > You should note, also, that 
  an addendum to the standard has removed<BR>> > the provision in the 
  table under G3.1, 5c to distribute windows  ><BR>> uniformly in 
  horizontal bands across the four orientations.  That  > <BR>> 
  should make all of our lives easier.<BR>>  ><BR>>  > 
  Regards,<BR>>  > Ken Neuhauser, M.Arch, MSc.Arch, LEED AP 
  /Architectural Project  > <BR>> Manager/ Conservation Services 
  Group, Inc.<BR>>  > 40 Washington Street<BR>>  > 
  Westborough, MA 01581<BR>>  > Ph. 508 836-9500 ext. 
  13226<BR>>  > Fax 508 836-3181<BR>>  > <A 
  href="http://www.csgrp.com">www.csgrp.com</A> <<A 
  href="http://www.csgrp.com/">http://www.csgrp.com/</A>>  >  
  >  >  >  >  >  ><BR>> 
  ----------------------------------------------------------------------<BR>>  
  > --<BR>>  ><BR>>  ><BR>>  > *From:* <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> 
  [mailto:BLDG-SIM@gard.com] *On Behalf Of<BR>> > *Keith Lane*  > 
  Sent:* Tuesday, November 27, 2007 2:40 PM*  > To:*<BR>> <A 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A>*  > Subject:* 
  [BLDG-SIM] LEED Building Orientation<BR>> >  > I am modeling an 
  existing building for Energy & Atmosphere Credit<BR>> 1:<BR>>  
  > Optimize Energy Performance. In LEED and table G3.1 No. 5(a) of <BR>> 
  ASHREA  > Standard 90.1-2004, it states that "the baseline building 
  <BR>> performance  > shall be generated by simulating the building 
  with its <BR>> actual  > orientation and again after rotating the 
  entire building 90, <BR>> 180, 270  > degrees, then averaging the 
  results". However table G3.1 <BR>> No. 5(f) of  > ASHREA Standard 
  90.1-2004 states: "for existing <BR>> building envelopes,  > the 
  baseline building design shall reflect <BR>> existing conditions 
  prior  > to any revisions that are part of the scope of work being 
  evaluated."<BR>>  > Would this mean that you do not need to 
  simulate the building for <BR>> the  > four orientations? It just 
  doesn't seem to make sense to <BR>> simulate the  > building in 
  such a manner if it is existing. I am new <BR>> energy modeling  > 
  for LEED credit and sincerely appreciate any assistance.<BR>>  
  ><BR>>  > Thank you,<BR>>  ><BR>>  > 
  */Keith Lane, LEED AP/*<BR>>  > */Mechanical 
  Engineer/*<BR>>  > Garcia.Galuska.DeSousa<BR>>  > 
  /Consulting 
  Engineers                     
  Inc.                        
  /<BR>>  > 370 Faunce Corner Road, Dartmouth, MA 02747<BR>>  
  > 
  p.508.998.5700                          
  f. 508.998.0883<BR>>  ><BR>>  ><BR>>  
  ><BR>>  > ==================<BR>>  > You received 
  this e-mail because you are subscribed to the  > <BR>> <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To 
  unsubscribe from this mailing list<BR>> > send a blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>  
  >  >  ><BR>> ==================  > You received 
  this e-mail because you are <BR>> subscribed to the  > <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To 
  unsubscribe <BR>> from this mailing list  > send a blank message to 
  <BR>> <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>  
  >  > ==================  > You received <BR>> this 
  e-mail because you are subscribed to the  > <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> <BR>> mailing 
  list.  To unsubscribe from this mailing list  > send a blank 
  <BR>> message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>  
  >  >  >  > <BR>> 
  =====================================================You received this<BR>> 
  > e-mail because you are subscribed to the <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing <BR>> > 
  list.  To unsubscribe from this mailing list send a blank message to 
  <BR>> > <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>  
  >  >  >  >  >  > 
  ==================  <BR>> > > You received this e-mail because 
  you are subscribed  >  > to the<BR>> <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To 
  unsubscribe  >  > from this <BR>> mailing list send a blank 
  message to  >  > <BR>> <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>  
  >  >  > <BR>> 
  ======================================================<BR>>  > You 
  received this e-mail because you are subscribed to the  > <BR>> <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To 
  unsubscribe from this mailing list<BR>> > send a blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A><BR>> 
  <BR>> --<BR>> Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin 
  of BLDG-SIM <BR>> list for building simulation users<BR>> <BR>> 
  ==================<BR>> You received this e-mail because you are subscribed 
  to the <BR>> <A href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> 
  mailing list.  To unsubscribe from this mailing list <BR>> send a 
  blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A><BR><BR>--<BR>Jason 
  Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin of BLDG-SIM list for 
  building simulation users<BR><BR><BR><BR>==================<BR>You received 
  this e-mail because you are subscribed <BR>to the <A 
  href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To 
  unsubscribe <BR>from this mailing list send a blank message to <BR><A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A><BR></BLOCKQUOTE><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>