style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Jason, 
<?xml:namespace prefix = st1 ns = "urn:schemas-microsoft-com:office:smarttags" 
/><st1:City w:st="on"><st1:place w:st="on">Brandon</st1:place></st1:City>, and 
others doing building simulation for LEED:</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><?xml:namespace 
prefix = o ns = "urn:schemas-microsoft-com:office:office" 
/><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Great 
to see all of the discussion this topic is generating. It seems well worth 
considering how better to provide an incentive for orientation without needless 
hassles and penalties. If you’re interested in doing so, please read on and 
comment.<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><SPAN 
style="mso-spacerun: yes"> </SPAN><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">The 
90.1-2004 Appendix G requirement for averaging the results of four baseline 
building orientations is, as described by previous comments in this 
discussion, a somewhat arbitrary and often problematic means of 
attempting to give credit (or penalty) for building orientation. It can 
also be a time-consuming pain either when overshadowing from adjacent buildings 
is modeled (fixed shades), and thus the site shape and coordinate origin may not 
make sense for a rotated building, or when attempting to compare benefits 
over the baseline model related to specific strategies (i.e., baseline+X vs. 
baseline+Y, acknowledging that relative comparisons of strategies can and should 
most often still be made without ever rotating anything).  </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><SPAN 
style="mso-spacerun: yes"> </SPAN></SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Of 
potentially even greater concern, in some cases, such as on a very narrow 
site with N-S major axis, the current requirement needlessly penalizes (i.e., <I 
style="mso-bidi-font-style: normal">deducts</I> credit from) a design that may 
be making the best of a constrained situation. Thus, even if the process of 
generating and averaging baseline performance results for all four orientations 
were <I style="mso-bidi-font-style: normal">fully</I> automated in the 
simulation tools, which would alleviate the time and hassle, the current 
approach would still impose an unfair and unhelpful penalty on certain projects 
that are forced to orient their building along a N-S axis or with 
a large SE, SW, or W exposure, etc. </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><SPAN 
class=125503403-01122007>However, </SPAN>I agree that we <I 
style="mso-bidi-font-style: normal">do</I> need some method of encouraging 
and rewarding beneficial building orientations where 
applicable. </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: black; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">It 
appears the draft Addendum R language that was never approved was one idea 
for how to address some of the issues described above. I would hazard a 
guess<SPAN class=125503403-01122007> </SPAN>that it was not approved because of 
the tendency for such language of "exceptions" to become a loophole open to 
interpretation and gaming, and thus something likely to weaken the performance 
rating method and generate more work for reviewers, not to mention 
superfluous LEED credit interpretation rulings. <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: black; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">I 
support the idea of a positive incentive or opportunity offered by the 
<I><U>option</U></I> for comparing to the averaged results for the rotated 
baseline building, plus a similar <EM><U>option</U></EM> with respect 
to glazing orientation, <I style="mso-bidi-font-style: normal">if</I> and <I 
style="mso-bidi-font-style: normal">when</I> permitted by straightforward 
criteria. I would propose the following requirements be met for the 
<I>optional</I> use of such averaged values for the baseline 
building…<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: black; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">The 
project would need to show simple documentation that <SPAN 
style="mso-bidi-font-style: italic">one</SPAN> of the two options was 
indeed applicable, and thus they should be permitted to use the 
associated method for adjusting the baseline building 
results: <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: black; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B 
style="mso-bidi-font-weight: normal"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Option 
1)</SPAN></B><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> 
Demonstrate via a simple sketch or other graphic representation that there is 
space on the site for the same total building footprint area to be re-shaped to 
be either more nearly square in terms of solar orientation OR to be rotated 
at least 60 degrees (or similar value TBD) from the design orientation---thus 
<U>it would have been possible and plausible to neglect building 
orientation</U>. In this case the team would be permitted to compare to an 
average of rotated baseline building results as in 90.1-2004 Appendix G. As with 
Appendix G, overshadowing from adjacent buildings, etc. <SPAN 
class=125503403-01122007>would </SPAN>need to be modeled as a fixed shading item 
that does not rotate with the building. For cases where the proposed building 
orientation is elongated and rotated by something less than 60 degrees 
(or whatever similar threshold was established for this option)---for 
example, rotated 45 degrees from the orientation of the major axis of the 
site, adjacent road, adjacent buildings, etc.---and there is not enough 
space on the site to rotate it a full 60 degrees, the team should be 
permitted (if they see fit) to compare to a baseline result that is the 
average of just two orientations of the very same footprint: the proposed 
orientation and whatever they believe to be the worst orientation of the 
</SPAN><I><SPAN 
style="COLOR: navy; mso-bidi-font-family: Arial">same</SPAN></I><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> 
</SPAN><I><SPAN style="COLOR: navy; mso-bidi-font-family: Arial">footprint 
shape</SPAN></I><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> 
that would actually still fit on the site. If Option #1 were selected, 
doing so would eliminate Option #2 in order to avoid double 
counting.</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B 
style="mso-bidi-font-weight: normal"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Option 
2)</SPAN></B><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"> 
Demonstrate with simple table of summed values that the glazing fraction or 
window-to-wall ratio (WWR) for the facades on the proposed design is 
asymmetric in terms of orientation (e.g., differences are greater than 5%), AND 
confirm that this is NOT an outcome forced by an immediately adjacent building 
or other constraint of the physical building site, but rather a deliberate 
design strategy---thus <U>the design <I 
style="mso-bidi-font-style: normal">could</I> have neglected any such 
orientation of WWR</U>. In this case the team would be permitted to 
compare their design to a baseline with <I 
style="mso-bidi-font-style: normal">identical</I> WWR for all façade 
orientations---i.e., evenly distributed glazing as indicated by WWR (but 
<I>not</I> a rotated building, as in Option #1).<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><SPAN 
style="mso-spacerun: yes"> </SPAN><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">The 
idea here is to permit teams to get credit for either building 
orientation <SPAN class=125503403-01122007>OR </SPAN>glazing orientation on 
the building <U>if they believe it to be significant</U> AND <U>it would have 
been possible to neglect it</U>. </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><o:p> </o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">If 
neither of these options were applicable and implemented, the baseline building 
would simply be modeled in the same orientation as the proposed design and 
with the same proportional distribution of WWR, in keeping with 90.1 WWR 
limits.  </SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">I 
do not believe it is workable to penalize those who neglect orientation, as the 
present Appendix G attempts to do, without creating other inappropriate 
penalties and deterrents that we all really could do without. The penalty for 
those who neglect orientation where there was a significant potential to 
benefit from doing otherwise would, in what I have proposed, simply be 
the foregone opportunity to do better and get credit for it. Thus 
building orientation would be recognized and treated in much the same 
manner as most other performance-related architectural design 
strategies.</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">  
<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">I'm 
interested in what others think of these ideas as possible means of addressing 
concerns raised in this discussion. Perhaps, Jason, you could forward this to 
the 90.1 committee people that are involved specifically with the Performance 
Rating Method (along with related or subsequent comments from others on the 
BLDG-SIM forum). Hopefully we can move this forward.<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><o:p> </o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Best,<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: navy; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Timothy<o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p> </o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Timothy 
Moore,</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">LEED 
AP, Design Consultant, Building Performance Simulation</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Whole 
Systems Design</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><st1:Street 
w:st="on"><st1:address w:st="on"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">910 
Indian Rock Ave.</SPAN></st1:address></st1:Street><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><st1:place w:st="on"><st1:City 
w:st="on"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Berkeley</SPAN></st1:City><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">, 
<st1:State w:st="on">CA</st1:State> <st1:PostalCode 
w:st="on">94707</st1:PostalCode></SPAN></st1:place><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"> <o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Office: 
510-525-4809</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><st1:City w:st="on"><st1:place 
w:st="on"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">Mobile</SPAN></st1:place></st1:City><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">: 
303-324-1044</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial">eFax: 
413-480-7252</SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="COLOR: green; mso-bidi-font-size: 10.0pt; mso-bidi-font-family: Arial"><A 
href="mailto:tmoore@whole-systems-design.com"><SPAN 
style="mso-bidi-font-size: 12.0pt">tmoore@whole-systems-design.com</SPAN></A></SPAN><SPAN 
style="FONT-SIZE: 12pt; COLOR: navy; FONT-FAMILY: 'Times New Roman'"><o:p></o:p></SPAN></P>
<P class=MsoNormal 
style="MARGIN: 0in 0in 0pt"></SPAN></SPAN></FONT></SPAN></FONT><BR> </P></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com 
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Brandon Nichols<BR><B>Sent:</B> 
Friday, November 30, 2007 11:22 AM<BR><B>To:</B> BLDG-SIM@gard.com<BR><B>Cc:</B> 
Peter.Simmonds@ibece.net; Leonard Sciarra<BR><B>Subject:</B> [BLDG-SIM] LEED 
Building Orientation<BR></FONT><BR></DIV>
<DIV></DIV><!-- Converted from text/plain format -->
<P><FONT size=2><FONT face="Courier New">Thanks Jason,<BR><BR>The 'burr' under 
my saddle on this issue is that the 'averaged buiilding', and therefore the 
baseline to which all project EEMs are to be compared, <EM><U>does not 
exist</U></EM>, not even in the simulation software.</FONT></FONT></P>
<P><FONT size=2><FONT face="Courier New">While we may have four perfectly good 
orientations, any one of which could be used as a baseline (think .SIM file), 
there simply exists <EM><U>no .SIM file for the averaged 
building</U></EM>.  It would need to be created (as of this writing) 
manually, and the result could not be used easily, let alone seamlessly, as the 
baseline for alternative comparisons within eQuest.</FONT></FONT></P>
<P><FONT size=2><FONT face="Courier New">Suggestions:</FONT></FONT></P>
<P><FONT size=2><FONT face="Courier New">1. Allow selecting the orientation 
closest to, without performing worse than, the 'average total annual energy 
consumption' as the baseline.  This simple change would allow all baseline 
numbers to reside within the analysis software.</FONT></FONT></P>
<P><FONT face="Courier New" size=2>2. Make this requirement optional, for those 
buildings which can benefit from orientation optimization.  In other words, 
promote achievable incentives instead of enforcing arbitrary 
punishments.</FONT></P>
<DIV><FONT size=2><FONT face="Courier New">Wish I had more time to help out with 
90.1 -- maybe next year!<BR></FONT></FONT></DIV>
<DIV><FONT size=2><FONT face="Courier New">Regards<BR><BR>Brandon Nichols, PE, 
LEED® AP<BR>Mechanical<BR>HARGIS ENGINEERS<BR><BR>600 Stewart Street<BR>Suite 
1000<BR>Seattle, WA 98101<BR>www.hargis.biz<BR><BR>d | 206.436.0400  c | 
206.228.8707<BR>o | 206.448.3376  f  | 
206.448.4450<BR><BR></FONT><BR><BR>-----Original Message-----<BR>From: Jason 
Glazer [<A 
href="mailto:jglazer@gardanalytics.com">mailto:jglazer@gardanalytics.com</A>]<BR>Sent: 
Friday, November 30, 2007 8:04 AM<BR>To: Peter.Simmonds@ibece.net; Brandon 
Nichols<BR>Subject: Re: [BLDG-SIM] LEED Building Orientation<BR><BR>Peter and 
Brandon,<BR><BR>This looks like an issue that you have a strong opinion so 
perhaps consider contributing a better solution. Anyone can propose a change to 
90.1. Further, if you examine this history of the ECB subcommittee, I think you 
would find that we are open to good ideas and are trying to balance multiple 
needs. The building rotation concept replaced a much worse concept of spreading 
the windows around the building evenly.<BR>  Maybe you can find a better 
solution. I believe we need to reward those that do make an effort to orient 
their building<BR>  and windows to save energy and penalize those that make 
poor design choices about building orientation and window placement.  The 
building rotation idea has traction because most of the effort needed for each 
rotation is just to rerun the simulation with the building azimuth changed. We 
thought that was simple.  It is an issue that has been discussed many times 
in the ECB subcommittee and a few times at the full committee level.<BR><BR>I 
look forward to your suggestions.<BR><BR>Jason<BR><BR><BR><BR>On 11/30/2007 8:34 
AM, Peter Simmonds wrote:<BR>> Here here Brandon. A building is a building 
and that’s that. I have<BR>> sat through many charette’s  on ‘tree 
hugging’ projects to hear how<BR>> the buildings orientation can affect the 
cooling and heating load, let<BR>> alone natural daylighting. Only to hear 
the wise men of 90.1 (who have<BR>> never designed a building) to come up 
with some ‘weighted’ average to<BR>> change the results. The designer ends up 
doing four different runs<BR>> only to find out that the architect didn’t 
have clue what he was<BR>> trying to do in the first 
place.<BR>><BR>> <BR>><BR>> Long live 
sanity.<BR>><BR>> <BR>><BR>> Peter Simmonds 
Ph.D.<BR>><BR>> Associate<BR>> IBE Consulting Engineers<BR>><BR>> 
14130 Riverside Drive Suite 201<BR>><BR>> Sherman Oaks, CA 91423<BR>> 
p:   (818) 377-8220<BR>> f:    (818) 
377-8230<BR>> m:  (818) 219-1284<BR>> IDEAS FOR THE BUILT ENVIRONMENT 
<BLOCKED::<A 
href="http://www.ibece.com/">http://www.ibece.com/</A>><BR>><BR>> This 
e-mail message, including any attachments, is for the sole use of<BR>> the 
intended recipient(s) and may contain confidential and privileged<BR>> 
information. Any unauthorized review, use, disclosure, or distribution<BR>> 
is prohibited. If you are not the intended recipient, please contact<BR>> the 
sender by reply e-mail and destroy all copies of the original 
message.<BR>><BR>> 
----------------------------------------------------------------------<BR>> 
--<BR>><BR>> *From:* BLDG-SIM@gard.com [<A 
href="mailto:BLDG-SIM@gard.com">mailto:BLDG-SIM@gard.com</A>] *On Behalf 
Of<BR>> *Brandon Nichols<BR>> *Sent:* Thursday, November 29, 2007 5:48 
PM<BR>> *To:* BLDG-SIM@gard.com<BR>> *Subject:* [BLDG-SIM] LEED Building 
Orientation<BR>><BR>> <BR>><BR>> 
All,<BR>><BR>> <BR>><BR>> The building rotation requirement is 
utterly nonsensical.  For a<BR>> full-text rant on the subject, see my 
previous post:<BR>><BR>> <BR>><BR>> <A 
href="http://www.gard.com/ml/bldg-sim-archive/msg04038.html">http://www.gard.com/ml/bldg-sim-archive/msg04038.html</A><BR>><BR>> <BR>><BR>> 
In summary:<BR>><BR>> <BR>><BR>> 1) In the case of many new 
buildings (90% or more I would estimate),<BR>> there is very little latitude 
for changing the orientation.<BR>> For example the main street and therefore 
the lobby and entryway may<BR>> be on one side and one side only of the 
building, the aspect ratio of<BR>> the building may not fit on the lot in two 
of the four orientations, etc.<BR>><BR>> <BR>><BR>> 2) The 
fictitious, etheral 'averaged' building does not exist even in<BR>> the 
computer code of the best analysis programs we have at our<BR>> disposal to 
date.<BR>><BR>> <BR>><BR>> 3) All baseline numbers for each of 
the four orientations would need<BR>> to be extracted from the analysis 
software, and averaged on a spreadsheet.<BR>> Similarly each and every EEM 
would need to be extracted, and the<BR>> project's comparative analysis done 
on a spreadsheet instead of the<BR>> within the analysis software 
itself.  Thanks, but I have a life, wife<BR>> and 
family.<BR>><BR>> <BR>><BR>> 4) If this requirement still 
sounds like a good idea from the comfort<BR>> of your tenured office, I say 
come on out and run couple of dozen<BR>> real-life energy code and LEED 
compliance simulations for me within<BR>> budget and on deadline in Q1-Q2 
2008 and you'll begin to understand<BR>> what I'm talking 
about.<BR>><BR>> <BR>><BR>> Why not simply allow selecting the 
orientation closest to, without<BR>> performing worse than, the 'average' as 
the baseline?  This simple<BR>> change would allow the baseline numbers 
to reside within the analysis<BR>> 
software.<BR>><BR>> <BR>><BR>> Alternatively the eQuest 
developers are rumored to be working on a<BR>> 90.1 Appendix G compliance 
module.  Upon release, if it automates the<BR>> averaging I may be 
inclined retire some portion of this 
diatribe.<BR>><BR>> <BR>><BR>> Best idea yet, drop this as a 
requirement, and make it optional where<BR>> it makes sense to do so. Utilize 
by default the far more intuitive<BR>> (and useful in terms of energy 
incentives) 'code minimum' baseline<BR>> building, oriented identically to 
the proposed.  This is the approach<BR>> I've been able to convince our 
state energy code and utility rebate<BR>> reviewers to accept -- its just 
hardened LEED extremists who still<BR>> seem to have their head in the sand 
on this.<BR>><BR>> <BR>><BR>> <BR>><BR>> 
Regards<BR>><BR>> <BR>><BR>> <BR>><BR>> Brandon 
Nichols, PE, LEED^® AP<BR>><BR>> Mechanical<BR>><BR>> **HARGIS 
ENGINEERS**<BR>><BR>> 600 Stewart Street<BR>><BR>> Suite 
1000<BR>><BR>> Seattle, WA 98101<BR>><BR>> 
www.hargis.biz<BR>><BR>> <BR>><BR>> *d |* 206.436.0400  *c 
| *206.228.8707<BR>><BR>> *o |* 206.448.3376  *f  |* 
206.448.4450<BR>><BR>> <BR>><BR>> <BR>><BR>> <BR>><BR>> 
----------------------------------------------------------------------<BR>> 
--<BR>><BR>> *From:* BLDG-SIM@gard.com [<A 
href="mailto:BLDG-SIM@gard.com">mailto:BLDG-SIM@gard.com</A>] *On Behalf 
Of<BR>> *Edward.A.Decker@jci.com<BR>> *Sent:* Thursday, November 29, 2007 
3:59 PM<BR>> *To:* BLDG-SIM@gard.com<BR>> *Cc:* BLDG-SIM@gard.com<BR>> 
*Subject:* [BLDG-SIM] LEED Building Orientation<BR>><BR>><BR>> Can you 
not apply various fenestrations and shading to the model<BR>> without having 
to change its orientation? For an existing building,<BR>> including LEED EB, 
what additional benefit could be gained by rotating<BR>> the model since you 
cannot change the orientation?<BR>> 
_____________________________________________<BR>> Edward A. 
Decker<BR>><BR>><BR>> *"Leonard Sciarra" 
<leonard_sciarra@gensler.com>* Sent by:<BR>> 
BLDG-SIM@gard.com<BR>><BR>> 11/29/2007 06:18 PM<BR>><BR>> Please 
respond to<BR>> leonard_sciarra@gensler.com<BR>><BR>> 
     <BR>><BR>> To<BR>><BR>> 
     <BR>><BR>> 
<BLDG-SIM@gard.com><BR>><BR>> cc<BR>><BR>> 
     <BR>><BR>> <BR>><BR>> 
Subject<BR>><BR>>      <BR>><BR>> 
[BLDG-SIM] LEED Building 
Orientation<BR>><BR>> <BR>><BR>> <BR>><BR>> 
     <BR>><BR>> <BR>><BR>><BR>><BR>><BR>> 
This is true, however, even with an existing building, you as the<BR>> 
designer/engineer have the option of "working" the facades and<BR>> applying 
appropriate fenestration, shading, etc... you can still make<BR>> good/bad 
decisions and the fact that your footprint is fixed should<BR>> not give the 
design team a waiver from the fact that the sun still<BR>> rises in the east 
and sets in the west.  In fact it may be a benefit<BR>> if perhaps your 
building is shaded on the west by itself.<BR>> <BR>> Leonard Sciarra, 
AIA, LEED ap<BR>> 312.577.6580 (Dir)<BR>> G E N S L E R | Architecture 
& Design Worldwide 30 West Monroe Street<BR>> Chicago IL, 60603<BR>> 
312.456.0123<BR>> 
leonard_sciarra@gensler.com<BR>><BR>> <BR>><BR>> 
----------------------------------------------------------------------<BR>> 
--<BR>><BR>> *From:* BLDG-SIM@gard.com [<A 
href="mailto:BLDG-SIM@gard.com">mailto:BLDG-SIM@gard.com</A>] *On Behalf 
Of<BR>> *Ross-Bain, Jeff*<BR>> Sent:* Thursday, November 29, 2007 2:40 
PM*<BR>> To:* BLDG-SIM@gard.com*<BR>> Cc:* keith_lane@g-g-d.com*<BR>> 
Subject:* [BLDG-SIM] LEED Building Orientation<BR>><BR>> Here is my 
question to and response from the USGBC regarding this 
issue:<BR>> <BR>> <BR>> Dear LEED Info,<BR>> <BR>> 
There has been a lot of chat on this item and I wonder if there is a<BR>> 
USGBC position – I found no reference to this in the 
CIR’s:<BR>> <BR>> Do existing buildings undergoing renovation require 
the four-point<BR>> compass orientation 
analysis?<BR>> <BR>> <BR>> <BR>> 
Jeffrey,<BR>> <BR>> If the existing building being renovated is 
pursuing LEED-NC rather<BR>> than LEED-EB, then it would indeed be required 
to undergo the<BR>> specified analysis.  This analysis is used to 
establish the baseline<BR>> for energy performance using the ASHRAE 
standard.  LEED doesn’t have<BR>> any specific exemptions for existing 
buildings in this requirement,<BR>> but if ASHRAE has some kind of exemption, 
we will honor that.<BR>> <BR>> <BR>> So I guess the question 
then becomes an interpretation of the Appendix<BR>> G (Table G3.1 (f)) 
comment for existing buildings. Rotate or not?<BR>> <BR>> My take has 
always been that new buildings have the option to consider<BR>> orientation 
but existing buildings cannot be re-oriented so rotating<BR>> the model does 
not really prove anything.<BR>> <BR>> Any 90.1 code committee members 
or others out there have an interpretation?<BR>> <BR>> 
Regards,<BR>><BR>> */Jeffrey G. Ross-Bain, PE, LEED/*<BR>> Smith Dalia 
Architects<BR>> 621 North Ave NE<BR>> Suite C-140<BR>> Atlanta, GA, 
30308<BR>> 404-892-2443 _<BR>> _www.smithdalia.com <<A 
href="http://www.smithdalia.com/">http://www.smithdalia.com/</A>><BR>><BR>> 
P *Consider the environment.* *Please don't print this e-mail unless<BR>> you 
really need to.*<BR>><BR>> <BR>><BR>> 
----------------------------------------------------------------------<BR>> 
--<BR>><BR>><BR>> *From:* BLDG-SIM@gard.com [<A 
href="mailto:BLDG-SIM@gard.com">mailto:BLDG-SIM@gard.com</A>] *On Behalf 
Of<BR>> *Neuhauser, Ken*<BR>> Sent:* Thursday, November 29, 2007 2:31 
PM*<BR>> To:* BLDG-SIM@gard.com*<BR>> Cc:* keith_lane@g-g-d.com*<BR>> 
Subject:* [BLDG-SIM] LEED Building Orientation<BR>> <BR>> I am not 
the authority, Keith, but I believe that your interpretation<BR>> (that 
existing buildings do not get rotated in the baseline) is<BR>> consistent 
with the intent of Appendix G.  In new construction, the<BR>> decisions 
regarding building orientation will affect performance and<BR>> that 
performance should be measured against the baseline (although,<BR>> there are 
cases, such as a building that adjoins buildings to either<BR>> side, where 
rotating the baseline through all four orientations does<BR>> not make 
sense).  If you’re improving an existing building, the<BR>> existing 
conditions of building enclosure components, including<BR>> orientation, are 
an appropriate baseline.  When we apply Appendix G to<BR>> existing 
buildings, we have also found that “existing building envelopes”<BR>> 
sometimes needs to be parsed into existing building envelope 
components.<BR>>  For example, in a mill rehab, the bearing walls may be 
serviceable<BR>> and appropriately modeled “as is” in the baseline, but 
missing windows<BR>> or windows that are clearly not serviceable we model as 
per the ASHRAE<BR>> minimum compliance.<BR>> <BR>> You should 
note, also, that an addendum to the standard has removed<BR>> the provision 
in the table under G3.1, 5c to distribute windows<BR>> uniformly in 
horizontal bands across the four orientations.  That<BR>> should make 
all of our lives easier.<BR>> <BR>> Regards,<BR>> Ken Neuhauser, 
M.Arch, MSc.Arch, LEED AP /Architectural Project<BR>> Manager/ Conservation 
Services Group, Inc.<BR>> 40 Washington Street<BR>> Westborough, MA 
01581<BR>> Ph. 508 836-9500 ext. 13226<BR>> Fax 508 836-3181<BR>> 
www.csgrp.com <<A 
href="http://www.csgrp.com/">http://www.csgrp.com/</A>><BR>> <BR>> <BR>> <BR>><BR>> <BR>><BR>> 
----------------------------------------------------------------------<BR>> 
--<BR>><BR>><BR>> *From:* BLDG-SIM@gard.com [<A 
href="mailto:BLDG-SIM@gard.com">mailto:BLDG-SIM@gard.com</A>] *On Behalf 
Of<BR>> *Keith Lane*<BR>> Sent:* Tuesday, November 27, 2007 2:40 
PM*<BR>> To:* BLDG-SIM@gard.com*<BR>> Subject:* [BLDG-SIM] LEED Building 
Orientation<BR>> <BR>> I am modeling an existing building for Energy 
& Atmosphere Credit 1:<BR>> Optimize Energy Performance. In LEED and 
table G3.1 No. 5(a) of ASHREA<BR>> Standard 90.1-2004, it states that “the 
baseline building performance<BR>> shall be generated by simulating the 
building with its actual<BR>> orientation and again after rotating the entire 
building 90, 180, 270<BR>> degrees, then averaging the results”. However 
table G3.1 No. 5(f) of<BR>> ASHREA Standard 90.1-2004 states: “for existing 
building envelopes,<BR>> the baseline building design shall reflect existing 
conditions prior<BR>> to any revisions that are part of the scope of work 
being evaluated.”<BR>> Would this mean that you do not need to simulate the 
building for the<BR>> four orientations? It just doesn’t seem to make sense 
to simulate the<BR>> building in such a manner if it is existing. I am new 
energy modeling<BR>> for LEED credit and sincerely appreciate any 
assistance.<BR>> <BR>> Thank you,<BR>> <BR>> */Keith Lane, 
LEED AP/*<BR>> */Mechanical Engineer/*<BR>> Garcia.Galuska.DeSousa<BR>> 
/Consulting 
Engineers                     
Inc.                        
/<BR>> 370 Faunce Corner Road, Dartmouth, MA 02747<BR>> 
p.508.998.5700                          
f. 508.998.0883<BR>> <BR>> <BR>> <BR>> 
==================<BR>> You received this e-mail because you are subscribed 
to the<BR>> BLDG-SIM@GARD.COM mailing list.  To unsubscribe from this 
mailing list<BR>> send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>> <BR>> <BR>> 
==================<BR>> You received this e-mail because you are subscribed 
to the<BR>> BLDG-SIM@GARD.COM mailing list.  To unsubscribe from this 
mailing list<BR>> send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>><BR>> ==================<BR>> You 
received this e-mail because you are subscribed to the<BR>> BLDG-SIM@GARD.COM 
mailing list.  To unsubscribe from this mailing list<BR>> send a blank 
message to BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>><BR>><BR>><BR>> 
=====================================================You received this<BR>> 
e-mail because you are subscribed to the BLDG-SIM@GARD.COM mailing<BR>> 
list.  To unsubscribe from this mailing list send a blank message 
to<BR>> 
BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>><BR>> <BR>><BR>> <BR>><BR>> 
==================<BR>><BR>> You received this e-mail because you are 
subscribed<BR>><BR>> to the BLDG-SIM@GARD.COM mailing list.  To 
unsubscribe<BR>><BR>> from this mailing list send a blank message 
to<BR>><BR>> BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR>><BR>><BR>> 
======================================================<BR>> You received this 
e-mail because you are subscribed to the<BR>> BLDG-SIM@GARD.COM mailing 
list.  To unsubscribe from this mailing list<BR>> send a blank message 
to BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR><BR>--<BR>Jason Glazer, P.E., GARD 
Analytics, 90.1 ECB chair Admin of BLDG-SIM list for building simulation 
users<BR><BR></DIV></FONT><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>