<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff size=2>It is
my understanding that what you state below is not actually correct.
demonstrating savings via Appendix G does not demonstrate compliance with the
standard. If you do not meet the mandatory provisions you do not meet the
prerequisite. If you do not meet the prescriptive requirements then officially
you need to demonstrate compliance via the ECB method (chapter 11) in a
pass/fail mode. </FONT></SPAN></DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff
size=2>provided you pass, then you use Appendix G to demonstrate
savings.</FONT></SPAN></DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff size=2>all -
correct me if I am wrong here.</FONT></SPAN></DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=270230622-12112007><FONT face=Arial color=#0000ff
size=2>Peter</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Vikram Sami<BR><B>Sent:</B>
Monday, November 12, 2007 12:28 PM<BR><B>To:</B>
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] LEED EA Prerequisite 1 and
eQUEST<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV dir=ltr align=left><SPAN class=484352520-12112007><FONT face=Arial
color=#0000ff size=2>Thanks to everyone for weighing in on this. It turns
out my question regarding LEED was a little premature - you can use your
Appendix G documentation for this.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=484352520-12112007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=484352520-12112007><FONT face=Arial
color=#0000ff size=2>Which brings up the question - given that LEED now requires
a minimum of 2 energy reduction credits to be earned, what's the point of the
prerequisite documentation? </FONT></SPAN></DIV>
<DIV> </DIV><!-- Converted from text/rtf format -->
<P><B><FONT face=Garamond color=#000000>Vikram Sami,</FONT></B> <FONT
face=Garamond color=#000000>LEED AP</FONT><B></B> <BR><FONT face=Garamond
color=#000000>Direct Phone 404-253-1466 | Direct Fax 404-253-1366</FONT> </P>
<P><B><FONT face=Garamond color=#800000>L</FONT><FONT face=Garamond
color=#800000 size=2>ORD</FONT><FONT face=Garamond color=#800000>, A</FONT><FONT
face=Garamond color=#800000 size=2>ECK</FONT><FONT face=Garamond color=#800000>
& S</FONT><FONT face=Garamond color=#800000 size=2>ARGENT</FONT><FONT
face=Garamond color=#800000> A</FONT><FONT face=Garamond color=#800000
size=2>RCHITECTURE</FONT><BR></B><FONT face=Garamond size=2>1201 Peachtree
Street NE, Suite 300, Atlanta, GA 30361</FONT> <BR><FONT face=Garamond
size=2>Responsive Design</FONT> <FONT face=Symbol size=1>·<FONT
face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Technological
Expertise</FONT> <FONT face=Symbol size=1>·<FONT
face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Exceptional
Service</FONT> <BR><FONT face=Garamond
color=#000000>www.lordaecksargent.com</FONT> </P>
<P><B><FONT face=Garamond color=#008000>Please don't print this email unless you
really have to</FONT></B><I><FONT face=Garamond color=#008000>.</FONT></I>
<BR><I><FONT face=Garamond color=#008000>In the United States, we use enough
office paper each year to build a 10-foot high wall that’s 6,815 miles long or
two and a half times the distance from New York to Los Angeles. </FONT></I></P>
<P><I><FONT face=Garamond color=#008000>~ Wisconsin Department of Natural
Resources, “Recycling Facts and Figures,” PUBL CE-163, 2002.</FONT></I> </P>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Aulbach, John<BR><B>Sent:</B>
Monday, November 12, 2007 2:55 PM<BR><B>To:</B>
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] LEED EA Prerequisite 1 and
eQUEST<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV dir=ltr align=left><SPAN class=550514419-12112007><FONT face=Arial
color=#0000ff size=2>Vik:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=550514419-12112007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=550514419-12112007><FONT face=Arial
color=#0000ff size=2>eQuest in its present form only can develop California
Title 24 forms. There IS a 90.1 Version in the works, but it is not yet
available. Stay tuned.</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Doug Gwaltney<BR><B>Sent:</B>
Monday, November 12, 2007 11:15 AM<BR><B>To:</B>
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] LEED EA Prerequisite 1 and
eQUEST<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV dir=ltr align=left><FONT face=Arial size=2><SPAN
class=158191319-12112007>Vik,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial size=2><SPAN
class=158191319-12112007></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial size=2><SPAN class=158191319-12112007>I
believe eQUEST will only produce overall performance for Title 24 not the
prescriptive forms.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial size=2><SPAN
class=158191319-12112007></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial size=2><SPAN class=158191319-12112007>
<DIV align=left><FONT face=Arial size=2>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt" align=left><st1:PersonName><B
style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">Doug
Gwaltney</SPAN></B></st1:PersonName><B
style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 8pt"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B
style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">Barrett, Woodyard &
Associates</SPAN></B><B style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 8pt"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><st1:phone o_x003a_ls="trans"
phonenumber="$6810$$$"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">770.810.8800</SPAN></st1:phone><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"> Office<SPAN
style="mso-spacerun: yes"> </SPAN></SPAN><st1:phone
o_x003a_ls="trans" phonenumber="$6301$$$"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">678.301.2235</SPAN></st1:phone><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"> Direct</SPAN><SPAN
style="FONT-SIZE: 8pt"><o:p></o:p></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><st1:phone o_x003a_ls="trans"
phonenumber="$6810$$$"><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">770.810.8808</SPAN></st1:phone><SPAN
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial">
Fax</SPAN></P></FONT></DIV></SPAN></FONT></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Vikram Sami<BR><B>Sent:</B>
Monday, November 12, 2007 11:31 AM<BR><B>To:</B>
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] LEED EA Prerequisite 1 and
eQUEST<BR></FONT><BR></DIV>
<DIV></DIV><!-- Converted from text/rtf format -->
<P><FONT face=Arial size=2>Has anyone used eQUEST to document the EA
prerequisite (compliance with 90.1 or other codes)? I suspect eQUEST does not do
that for anything other than Title 24 - am I correct? </FONT></P>
<P><B><FONT face=Garamond>Vikram Sami,</FONT></B> <FONT face=Garamond>LEED
AP</FONT><B></B> <BR><FONT face=Garamond>Direct Phone 404-253-1466 | Direct Fax
404-253-1366</FONT> </P>
<P><B><FONT face=Garamond color=#800000>L</FONT><FONT face=Garamond
color=#800000 size=2>ORD</FONT><FONT face=Garamond color=#800000>, A</FONT><FONT
face=Garamond color=#800000 size=2>ECK</FONT><FONT face=Garamond color=#800000>
& S</FONT><FONT face=Garamond color=#800000 size=2>ARGENT</FONT><FONT
face=Garamond color=#800000> A</FONT><FONT face=Garamond color=#800000
size=2>RCHITECTURE</FONT><BR></B><FONT face=Garamond size=2>1201 Peachtree
Street NE, Suite 300, Atlanta, GA 30361</FONT> <BR><FONT face=Garamond
size=2>Responsive Design</FONT> <FONT face=Symbol size=1>·<FONT
face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Technological
Expertise</FONT> <FONT face=Symbol size=1>·<FONT
face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Exceptional
Service</FONT> <BR><A href="file://www.lordaecksargent.com"><U></U><U><FONT
face=Garamond color=#0000ff>www.lordaecksargent.com</FONT></U></A> </P>
<P><B><FONT face=Garamond color=#008000>Please don't print this email unless you
really have to</FONT></B><I><FONT face=Garamond color=#008000>.</FONT></I>
<BR><I><FONT face=Garamond color=#008000>One tree makes 16.67 reams of copy
paper or 8,333.3 sheets<BR>~Conservatree, September
2002</FONT></I><BR></P><BR><BR><PRE>==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><pre>____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
</pre><PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>