<DIV><SPAN class=968082418-09102007><FONT face=Arial size=2>I am looking for 
some <SPAN 
class=937410020-09102007>un-official </SPAN>opinions <SPAN 
class=937410020-09102007>on an interpretation of </SPAN>Appendix <SPAN 
class=937410020-09102007> G </SPAN>.  </FONT></SPAN></DIV>
<DIV><SPAN class=968082418-09102007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=968082418-09102007><FONT face=Arial size=2>I am modeling a 
university stadium facility and the as-designed systems serving the locker 
room areas are constant volume reheat with heat recovery.  The 
intent is that these systems will run continuously for moisture and 
odor control.</FONT></SPAN></DIV>
<DIV><SPAN class=968082418-09102007><FONT size=+0></FONT></SPAN><FONT 
face=Arial><FONT size=2></FONT></FONT> </DIV>
<DIV><FONT size=2><FONT face=Arial>P<SPAN class=968082418-09102007>roblem #1 
</SPAN><SPAN class=968082418-09102007><FONT size=+0><FONT size=2>:  Based 
on the CFA, # of FLRs, and <SPAN class=937410020-09102007><FONT 
color=#0000ff><FONT color=#000000>HT Type</FONT></FONT></SPAN> the baseline 
system is System 7 VAV with Reheat.  However G3.1.2.5 states that 
the minimum ventilation would need to match the as-designed systems which 
in this case would be 100% design airflow.  Does the baseline in 
this case become constant volume because I have to maintain the same 
ventilation in both models?<SPAN class=937410020-09102007><FONT 
color=#0000ff>   </FONT>Or does minimum outside air ventilation 
refer to whatever is required by individual State code regardless of the 
as-designed case?  </SPAN><SPAN 
class=937410020-09102007> </SPAN></FONT> </FONT></SPAN></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN class=968082418-09102007><SPAN 
class=968082418-09102007></SPAN></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=968082418-09102007><SPAN 
class=968082418-09102007><SPAN class=968082418-09102007>My opinion is that<SPAN 
class=937410020-09102007> t</SPAN>he decision to use 100% constant volume 
outside air <SPAN class=937410020-09102007>is a</SPAN> design 
decision rather than a code/standard mandatory requirement.<SPAN 
class=937410020-09102007><FONT color=#0000ff><FONT color=#000000>   In 
this case minimum ventilation for locker rooms is 0.5 cfm/sq.ft dedicated 
exhaust.</FONT> </FONT></SPAN>  The additional energy associated 
with <SPAN class=937410020-09102007>providing constant 100% OA greater 
than 0.5 CFM/sq.ft. </SPAN>should not be included in the Appendix G 
baseline, <SPAN class=937410020-09102007><FONT color=#0000ff> <FONT 
color=#000000>but rather</FONT> </FONT></SPAN>the baseline should meet the 
minimum ventilation requirements of <SPAN 
class=937410020-09102007>the </SPAN>local state code.  
    </SPAN></SPAN></SPAN></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=968082418-09102007>Problem #2: How do I 
resolve the fact that the system will be operated continuously even though the 
space isn't occupied? Appendix G says systems shall run continuously during 
occupied periods and intermittently during unoccupied periods.  <SPAN 
class=937410020-09102007><FONT color=#0000ff> </FONT><FONT 
color=#000000>The locker rooms have low occupancy and therefore i</FONT></SPAN>f 
I only model the systems operating during occupied periods the annual building 
energy cost will be significantly lower than reality and the aggregate 
effect of other energy efficiency measures will be much greater (ie: the % cost 
savings for LEED will be much higher<FONT color=#0000ff><SPAN 
class=937410020-09102007> <FONT 
color=#000000>) </FONT></SPAN></FONT><FONT color=#000000><SPAN 
class=937410020-09102007>because the locker rooms only account for 20% of 
the total conditioned floor area but 40-50% of total energy 
cost</SPAN>).  </FONT></SPAN></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN class=968082418-09102007>Again I am 
going to argue that operating the systems continuously is a design 
decision and not a code/standard regulated requirement.  The 
additional energy associated with continuously operating the 
systems should be considered "process" energy and included in the 
baseline.  </SPAN></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN class=968082418-09102007>What does 
everyone think?  </SPAN></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN class=968082418-09102007>Thanks in 
advance for your comments.</SPAN></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT size=2><SPAN 
class=968082418-09102007></SPAN></FONT></FONT><SPAN 
class=968082418-09102007><FONT face="Arial Black"></FONT></SPAN> </DIV>
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=2>Tillou Engineering, 
LLC</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=1>Williamstown, MA 
01267</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=1>P: 
413-458-9870</FONT> <FONT face="Arial Black" size=1>C: 
413-652-1087</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>