color=#0000ff size=2>Actually Kevin didn't get the boiler hourly energy equation 
quite right.  The actual equation is:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT 
face="Courier New"></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT 
face="Courier New">Hourly Boiler Energy = DesignCapacity * HIR * 
HIRf(plr)</FONT><BR></DIV></SPAN><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2>The part of this that Kevin didn't explain is that the 
boiler HIRf(PLR) curve includes the PLR which explains why the curve is nearly 
linear.  The value that the performance curve returns is actually  
</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2>(HIRadj) * PLR</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=828301914-05102007><FONT face=Arial 
color=#0000ff size=2>HIRadj  =  the </FONT></SPAN><FONT 
face=Arial><FONT color=#0000ff><FONT size=2><SPAN class=828301914-05102007><FONT 
face=Arial color=#0000ff size=2>multiplier that indicates how the full load 
HIR changes with respect to part load.   If the boiler efficiency 
at a given part load goes down, HIRadj > 1.  If the boiler efficiency 
goes up at a given part load HIRadj<1.  HIRadj is really the ratio 
HIR-partload over 
HIR-fullload. </FONT></SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=828301914-05102007> </SPAN></DIV>
<DIV>P<SPAN class=828301914-05102007>LR = hourly load on the boiler / total 
capacity of the boiler</SPAN></FONT></FONT></FONT></DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff size=2>To 
create a curve that describes boiler HIR at various part loads you will 
need to divide the performance curve output at each part load point by 
the part load value and then multiply by the full load 
HIR.</FONT></SPAN></DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff size=2>Taylor 
- You should double check your "custom" chiller curves I'm pretty sure from what 
you describe they are not correct.  The Vol6 -New Features user 
manual does a good job describing how the chiller curves work.  I suggest 
you review this.  You can use the Excel function "LINEST" to create the 
necessary coefficients for a bi-quadratic curve from manufacturers chiller 
data.  Typically you will need to request data for a specific chiller from 
the chiller rep.  The hardest data to get is the chiller capacity data 
at various CHW/CW temperatures.  Remember total chiller capacity is 
different than the rated 100% part load point, most chillers can provide 10-20% 
extra capacity.  </FONT></SPAN></DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff size=2>I have 
had good experience creating custom chiller curves for DOE2.2 and I think the 
default curves in eQuest are representative of the various chiller types.  
Obviously if you are evaluating a specific chiller you should try to create 
custom curves.</FONT></SPAN></DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=828301914-05102007> <FONT face=Arial color=#0000ff 
size=2>Mike</FONT></SPAN></DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=828301914-05102007><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com 
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Kevin Madison<BR><B>Sent:</B> 
Thursday, October 04, 2007 9:46 PM<BR><B>To:</B> 
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] eQuest Default f(PLR) 
Skepticism<BR></FONT><BR></DIV>
<DIV></DIV><TT>Perhaps it would help to clarify how DOE-2.2 (the simulation 
engine behind eQUEST) calculates hourly energy input for boilers and 
chillers.<BR><BR>For boilers, the hourly energy input is:<BR>  Hourly 
Energy = Cap(hour) * HIR * HIRf(plr)<BR><BR>So while the HIRf(plr) may increase 
as part load decreases, which is not uncommon for standard atmospheric boilers, 
the energy use will certainly decrease with plr because the required output of 
the boiler for the hour decreases.<BR><BR>For chillers, DOE-2 uses the following 
relationship to calculate the electricity input to the chiller each 
hour:<BR><BR>  Caphour  = Capacity * CAPf(t1,t2)<BR>  
PLR      = Load / Caphour<BR>  
dT       = t2 – t1<BR>  Elechour = Caphour * 
EIR * EIRf(t1,t2) * EIRf(PLR,dT) / 3413 Btu/kW<BR><BR>where<BR><BR>  
Caphour      hourly capacity, Btuh (this is dependent 
on condenser and evaporator conditions for that hour)<BR>  
Capacity     rated capacity, Btuh<BR>  
CAPf(t1,t2)  correction to capacity for temperatures, curve 
CAP-FT<BR>  t1           leaving 
chilled-water temperature, °F<BR>  
t2           condenser 
temperature, °F<BR>  
PLR          Part load 
ratio<BR>  Load         Hourly 
load, Btuh<BR>  
dT           Temperature 
differential across chiller, °F<BR>  Elechour     
electric input to the chiller, kW<BR>  
EIR          rated electric input 
ratio<BR>  EIRf(t1,t2)  correction to EIR for temperatures, curve 
EIR-FT<BR>  EIRf(PLR,dT) correction to EIR for part-load ratio and dT, 
curve EIR-FPLR<BR><BR>Again, the primary factor affecting chiller energy use is 
the cooling capacity needed for that hour. Just because you don't have access to 
the dual function information doesn't mean you shouldn't be accounting for it in 
the simulation. Chiller performance is dependent on all operating conditions 
including load, condenser conditions and evaporator conditions.<BR><BR>For a 
more complete discussion on these simulation concepts, refer to the DOE-2 
documentation included with the eQUEST installation. Look in Dictionary:HVAC 
Components:Boiler:Boiler Energy Consumption and Dictionary:HVAC 
Components:Chiller:Chiller Energy Consumption.<BR><BR>Kevin Madison<BR>Madison 
Engineering PS<BR>Seattle WA<BR>USA<BR></TT><BR>Taylor Keep wrote: 
<BLOCKQUOTE cite=mid:MDAEMON-F200710041858.AA5833843pd80003835671@gard.com 
type="cite">
  <META content="MS Exchange Server version 6.5.7651.59" name=Generator><!-- Converted from text/rtf format -->
  <P><FONT face=Arial size=2>eQuest models boiler and chiller plants with 
  default part load curves that I think may be incorrect. As I understand it, 
  the f(PLR) curves are used as a direct multiplier on the HIR for boilers and 
  EIR for chillers, with full load (1.0 PLR) corresponding to a 1.0 multiplier. 
  If this is true, the f(PLR) curve should increase at part load for atmospheric 
  boilers (atmospheric boilers become somewhat less efficient at part load). The 
  default atmospheric boiler curve decreases almost linearly down to zero! I am 
  having a tough time wrapping my head around this.</FONT></P>
  <P><FONT face=Arial size=2>On the chiller side, the default f(PLR) is a 
  bi-quadratic function using both dT and PLR as variables, so it is f(PLR,dT). 
  Since I never have this dual function information in my general chiller 
  selections, I have been using a standard f(PLR) function quoted at a fixed dT 
  from the manufacturer. The curve I get from a McQuay 400-ton chiller selection 
  is quadratic, with decreasing EIR down to 50% load and increasing EIR below 
  50% load. I seriously doubt that the eQuest default corresponds with this 
  entry because changing the function produces a huge change in 
  performance.</FONT></P>
  <P><FONT face=Arial size=2>Do any of you have any thoughts or suggestions 
  about the accuracy of default f(PLR) curves? Should I scrap my "improved," 
  real curves - they are drastically changing the model 
  performance?!?!</FONT></P>
  <P><FONT face=Arial size=2>Taylor</FONT> </P><BR>
  <P><FONT face=Arial 
  size=2>________________________________________________________</FONT> 
  <BR><FONT face=Arial size=2>Taylor Keep</FONT> <BR><FONT face=Arial 
  size=2>Mechanical, LEED® AP</FONT> <BR><FONT face=Arial 
  size=2><U>                          
  </U></FONT><BR><FONT face=Arial size=2>Arup </FONT><BR><FONT face=Arial 
  size=2>901 Market Street Suite 260</FONT> <BR><FONT face=Arial size=2>San 
  Francisco, CA 94103</FONT> <BR><FONT face=Arial size=2>tel: 415 946 
  0279</FONT> <BR><FONT face=Arial size=2>fax: 415 957 9096</FONT> <BR><FONT 
  face=Arial size=2><A class=moz-txt-link-abbreviated 
  href="mailto:taylor.keep@arup.com">taylor.keep@arup.com</A></FONT> <BR><A 
  href="file://www.arup.com" moz-do-not-send="true"><U><FONT face=Arial 
  color=#0000ff size=2>www.arup.com</FONT></U></A> </P><BR><PRE>____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
  </PRE><PRE>======================================================
You received this e-mail because you are subscribed 
to the <A class=moz-txt-link-abbreviated href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A> mailing list.  To unsubscribe 
from this mailing list send a blank message to 
<A class=moz-txt-link-abbreviated href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A>
  </PRE></BLOCKQUOTE><PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>