<div><FONT face=arial>Hi Aulbach,</FONT></div>  <div><FONT face=arial></FONT> </div>  <div><FONT face=arial>Thanks for your reply. Yes, I inpu everything into the detail mode. Based on the system design in climate. The air system has three typies of heating: 1) preheating for preheating the incoming air to around 5 degree C; 2) main system heating coil to heat the incoming air (this heat coil is arranged after cooling coil); 3) reheat coil, this is the reheat coil in zone level to meet the zone temperature requirement.</FONT></div>  <div><FONT face=arial></FONT> </div>  <div><FONT face=arial>The one I found is the 2) main system heating coil never works. In the model, the preheating coil was ignored. Seems that all heating load goes to the zone level reheat coil.</FONT></div>  <div><FONT face=arial></FONT> </div>  <div><FONT face=arial>Any idea about this?</FONT></div>  <div><FONT
 face=arial></FONT> </div>  <div><FONT face=arial>Thanks.</FONT></div>  <div><FONT face=arial></FONT> </div>  <div><FONT face=arial>Regards,</FONT></div>  <div><FONT face=arial></FONT> </div>  <div><FONT face=arial>David  </FONT></div>  <div><BR><BR><B><EM>"Aulbach, John" <jaulbach@nexant.com></EM></B> wrote:</div>  <BLOCKQUOTE class=replbq style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #1010ff 2px solid">  <META content="MSHTML 6.00.2900.2963" name=GENERATOR>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2>I am going to take a stab at this one. In eQuest, a VAV system is a Terminal System. Therefore, in the Wizard, the zone level is where all heating and/or reheating is done (and developed). You have to force a primary heating source to occur, but this doesn't appear in the Wizard mode, apparently..</FONT></SPAN></DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT
 face=Arial color=#0000ff size=2></FONT></SPAN> </DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2>Have you input a Reheat-Delta-T? The temperature of 55 DegF + 40 DegF = 95 DegF heating supply temp.</FONT></SPAN></DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2></FONT></SPAN> </DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2>I also do NOT find the ability to create a pre heat coil in the Wizard. I have done it, but am quite sure this was input in the Detailed Interface Mode. There are MANY eQuest features that become available (like more SYSTEM-TYPES) in the Detailed Mode.</FONT></SPAN></DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2></FONT></SPAN> </DIV>  <DIV dir=ltr align=left><SPAN class=281030818-22082007><FONT face=Arial color=#0000ff size=2>Once
 you have "cookie cuttered" your building in the Wizards, switch to the Detailed Mode. There you will find your preheat coil.</FONT></SPAN></DIV><BR>  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>  <HR tabIndex=-1>  <FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com [mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Zhen Tian<BR><B>Sent:</B> Wednesday, August 22, 2007 9:49 AM<BR><B>To:</B> BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] eQUEST-System no heating<BR></FONT><BR></DIV>  <DIV></DIV>  <DIV>Dear All,</DIV>  <DIV> </DIV>  <DIV>I experienced an issue when I use eQUEST. I model a building in cold climate with VAV system. In the wizard mode, I found the system heat source is "not installed". But when I change to electricity, I found the heating enery use for system heating is zero. I also tried other options, always found that the system heat source is useless. I found that all the heating goes the zone level. Based on my understanding, this
 should not be the real case.</DIV>  <DIV> </DIV>  <DIV>I set the air supply temperature as constant as 55F (around 13 degree C), zone entering max air tem as 95F. Enen I set the zone entering max air tem as 86 (30 C). The system heating coil still has no load.</DIV>  <DIV> </DIV>  <DIV>Has anyone experience the same problem before and know to to solve this problem?</DIV>  <DIV> </DIV>  <DIV>Thanks a lot.</DIV>  <DIV> </DIV>  <DIV>Regards,</DIV>  <DIV> </DIV>  <DIV>David</DIV>  <div>  <HR SIZE=1>  Ready for the edge of your seat? <A href="http://us.rd.yahoo.com/evt=48220/*http://tv.yahoo.com/">Check out tonight's top picks</A> on Yahoo! TV. </BLOCKQUOTE><BR><p>
      <hr size=1>Moody friends. Drama queens. Your life? Nope! - their life, your story.<br> <a href="http://us.rd.yahoo.com/evt=48224/*http://sims.yahoo.com/">Play Sims Stories at Yahoo! Games. </a>