<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>Hello 
all,</FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial color=#0000ff size=2><FONT 
color=#000000>We have recently performed an analysis on</FONT> <FONT 
color=#000000>a building that is potentially going to incorporate the City Multi 
system. After many hours of going through eQUEST, I devised a method of modeling 
it that I would like to run past you all for any thoughts/ideas. 
</FONT></FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial color=#0000ff size=2><FONT 
color=#000000></FONT></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial color=#0000ff size=2><FONT 
color=#000000>First, for those not aware of the problems, here is a 
<STRONG>background of the systems</STRONG>:</FONT></FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>The City Multi 
system consists of essentially three parts: the condenser, the BC controller, 
and the heat exchanger unit at each zone. Refrigerant is the only property used 
for heat exchange, i.e. there is no water running from the condenser to the 
controller to the zone units. Each zone unit is essentially a fan coil, in that 
there is no compressor work at the zone, only fan energy. The BC controller is 
essentially a heat exchanger which gives the City Multi system a large advantage 
by being able to transfer heat, say from the south face of a building, to the 
north face, which is in the shade. All of the individual zone units connect to 
the BC controller and the BC controller distributes the refrigerant accordingly. 
If there is not enough free energy being generated by the system, the compressor 
kicks in and supplies or rejects heat from the loop to meet the demand. 
</FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>To model this in 
eQUEST, which has been suggested before, the water source heat pump system 
should be selected in order to account for the free transfer of heat from zone 
to zone. There are, however, several problems with this. One is that pumping 
energy is required to pump the water throughout the building. The second problem 
is that at each zone, each heat pump runs a compression cycle in order to supply 
or reject heat to or from the zone to the water loop. The third is that a boiler 
and cooling tower take the place for the condenser in the City Multi system. 
Each system requires a make-up air unit which can be modeled the same in each 
simulation.</FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2><STRONG>Now here is 
what I would like you all to review</STRONG>: </FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007></SPAN><SPAN class=149124914-22082007><FONT 
face=Arial size=2>These are some of the steps I went to in order to make the 
water source heat pump as much like the City Multi as 
possible.</FONT></SPAN></DIV>
<UL>
  <LI><SPAN class=149124914-22082007><FONT face=Arial size=2>Made the boiler and 
  electric boiler (to simulate the electric compressor) and gave it the 
  appropriate heating EIR that was specified in the Citi Multi specification 
  manual. <SPAN class=149124914-22082007><FONT face=Arial size=2>I gave the fan 
  the same EIR as the cooling side of the compressor in the same 
  manual.</FONT></SPAN></FONT></SPAN> 
  <LI><SPAN class=149124914-22082007><FONT face=Arial size=2>I made a 
  spreadsheet to subtract out the pumping energy (only from the water loop! Not 
  the DHW loop!) to simulate the suction of the refrigerant through the building 
  in the City Multi system. I had to do this in the BEPS and the BEPU report 
  which made it kind of a hassle to find the energy cost savings.</FONT></SPAN> 
  <LI><SPAN class=149124914-22082007><FONT face=Arial size=2>For each heat pump, 
  I set the EIR equal to 0.0001 to simulate the fan coil in the City Multi 
  system. Therefore, whatever heat is transferred to or from the water loop is 
  only shown with the fan energy from blowing the air over the coils. IF this is 
  not a proper way to do it, then what should the EIR be? It cannot be the EIR 
  from the condenser, because that has nothing to do with the free heat transfer 
  energy at the zones. </FONT></SPAN></LI></UL>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>What do you guys 
think about this approach? I figure that since this is a tough problem that 
other people have encountered as well, I might as well use this huge resource 
that has many great minds to come to a solution. </FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>Please, any feedback 
would be greatly appreciated. </FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007></SPAN> </DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial size=2>Regards,<FONT 
face=Arial size=2></FONT><FONT face=Arial size=2></FONT><FONT face=Arial 
size=2></FONT>
<DIV><BR><STRONG><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Dana 
Troy</SPAN></STRONG></DIV>
<DIV><STRONG><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN></STRONG><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN><FONT face=Arial 
size=2>Energy Analyst </FONT><BR><BR><A href="http://www.glumac.com/"><IMG 
src="http://www.glumac.com/glumacsig.gif" border=0></A> </DIV>
<DIV>
<HR style="WIDTH: 330px; HEIGHT: 2px" align=left width=330 color=#9acb33 noShade 
SIZE=2>
</DIV>
<DIV></DIV>
<DIV><SPAN 
style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">320 SW 
Washington, Suite 200</SPAN><BR><SPAN 
style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">Portland, 
OR 97204-2640</SPAN><BR><SPAN 
style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">T.  
503.227.5280<SPAN style="mso-spacerun: yes">  </SPAN>F. 
503.274.7674</SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">D. 
503.345.6286<BR><BR><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: #333333; FONT-FAMILY: Arial">Thinking. Inside the 
building.</SPAN></STRONG><BR><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 10pt; COLOR: #333333; FONT-FAMILY: Arial"><A 
href="http://www.glumac.com/">www.glumac.com</A></SPAN></STRONG></SPAN> 
</DIV></FONT></SPAN></DIV>
<DIV><SPAN class=149124914-22082007><FONT face=Arial 
size=2></FONT></SPAN> </DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>