<div><div>Thanks to those who responded, I found a solution to the "Pump Head" and "CURINV" errors listed below.  I wanted to post the solution to the list, to add to our knowledge-base.<br><br>Best,<br>
Andy<br><br><br>

<p class="MsoNormal"><b style=""><span style="font-family: Courier;">Error:</span></b></p>

<p class="MsoNormal"><span style="font-family: Courier;"> **WARNING**********************************************************************<br>
             Pump:
DHW Loop
Pump                   
has a user-specified head <br>
            
of         1. feet, but the loop head
is       6. feet.<br>
CURINV: No real root for CURVE: <br>
 1  1.353483  0.015932 -0.369414  0.000000 
0.000000  0.000000<br>
CURINV: No real root for CURVE: <br>
 1  1.353483  0.015932 -0.369414  0.000000 
0.000000  0.000000<br>
CURINV: No real root for CURVE: <br>
 1  1.353483  0.015932 -0.369414  0.000000 
0.000000  0.000000</span></p>

<p class="MsoNormal"><span style="font-family: Courier;">…repeats for hundreds of
pages</span></p>

<p class="MsoNormal"><span style="font-family: Courier;"> </span></p>

<p class="MsoNormal"><b style=""><span style="font-family: Courier;">Solution:</span></b><span style="font-family: Courier;"></span></p>

<p class="MsoNormal"><span style="font-family: Courier;">Directly editing the INP
file:</span></p>

<p class="MsoNormal"><span style="font-family: Courier;">$
---------------------------------------------------------</span></p>

<p class="MsoNormal"><span style="font-family: Courier;">$<span style="">              </span>Pumps</span></p>

<p class="MsoNormal"><span style="font-family: Courier;">$
---------------------------------------------------------</span></p>

<p class="MsoNormal"><span style="font-family: Courier;"> </span></p>

<p class="MsoNormal"><span style="font-family: Courier;">"DHW </span><span style="font-family: Courier;">Loop</span><span style="font-family: Courier;"> Pump" = PUMP<span style="">            </span></span></p>


<p class="MsoNormal"><span style="font-family: Courier;"><span style="">   </span>HEAD<span style="">             </span>= 7</span></p>

<p class="MsoNormal"><span style="font-family: Courier;"><span style="">   </span>MOTOR-CLASS<span style="">      </span>= HI-EFF</span></p>

<p class="MsoNormal"><span style="font-family: Courier;"><span style="">   </span>..</span></p>

<p class="MsoNormal"><span style="font-family: Courier;"> </span></p>

<p class="MsoNormal"><b style=""><span style="font-family: Courier;">Comments:</span></b></p>

<p class="MsoNormal"><span style="font-family: Courier;">By increasing HEAD from "0.5" to "7", the error disappeared.  Impact on simulated energy consumption was
minimal, there was an increase in pump consumption of 0.4 kWh/yr.</span></p>

<br><br> </div><br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;"><div><blockquote style="margin-right: 0px;"><div dir="ltr" align="left" lang="en-us">
<font face="Tahoma" size="2">-----Original Message-----<br><b>From:</b> 
  <a href="mailto:BLDG-SIM@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">BLDG-SIM@gard.com</a> [mailto:<a href="mailto:BLDG-SIM@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">
BLDG-SIM@gard.com</a>] <b>On Behalf Of </b>Andy 
  McNamara<br><b>Sent:</b> Tuesday, July 17, 2007 12:18 PM<br><b>To:</b> 
  <a href="mailto:BLDG-SIM@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">BLDG-SIM@gard.com</a><br><b>Subject:</b> [BLDG-SIM] eQUEST warning messages: 
  HSUPPLY, DHW Loop Pump, CURINV<br><br></font></div><span class="gmail_quote"></span>I am modeling a building in eQUEST with the following 
  HVAC system types: PTAC, UVT, MZS, PMZS.  The building is situated in New 
  York City, where code ventilation requirements for the baseline model require 
  exhaust rates roughly triple ASHRAE 62 guidelines (those requirements will be 
  changing shortly).  It is a 15 story multifamily building comprised of 5 
  shells due to different floor shapes and zoning patterns.  I am having 
  difficulty understanding three of the warning messages and thought I would see 
  if other have experienced/solved these problems before.  Thanks in 
  advance!  <br><br>1)  I am pretty sure this warning message pertains 
  to the MZS or PMZS because they are the only two air-side systems with HSUPPLY 
  specified in the INP file.  
  <br><br>**WARNING********************************************************************** 
  <br>             
  User-specified HSUPPLY-CFM is larger 
  than<br>             
  available return air.  Heating capacity 
  may<br>             
  be inadequate.<br>I checked the BEPS report and it shows that 
                     
  <br>"PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE = 
  86.0<br>PERCENT OF HOURS ANY PLANT LOAD NOT 
  SATISFIED                
  =  0.0"<br><br>2)  I tried increasing the "Pump Head" under 
  "Domestic Water Heater/Attachments" in the DDI from the default of 1 to 
  several other values, but the warning message always spits back a number that 
  is 5 ft greater than whatever I enter under "Pump Head".  E.g., I enter 
  Pump Head = 100, it spits back a loop head of 105 in the warning 
  message.<br> **WARNING**********************************************************************<br>             
  Pump: DHW Loop 
  Pump                    
  has a user-specified head 
  <br>             
  of         1. feet, but the loop head 
  is       6. feet.<br><br>3)  Per a 
  recommendation from Mike Tillou on the BLDG-SIM archive, I tried changing all 
  curves in the model to "default", but that did not remove the following error 
  message (which repeats for literally hundreds of pages). <br>CURINV: No real 
  root for CURVE: <br> 1  1.353483  0.015932 -0.369414  
  0.000000  0.000000  0.000000<br>CURINV: No real root for CURVE: 
  <br> 1  1.353483  0.015932 -0.369414  0.000000  
  0.000000  0.000000<br>CURINV: No real root for CURVE: <br> 1  
  1.353483  0.015932 -0.369414  0.000000  0.000000  
  0.000000<br><br clear="all"><br>(Background):<br>Even though I think I've 
  figured out the source of this warning message, I thought I'd include it in 
  case it's relevant to understanding the warning messages above. <br><br>This 
  warning is coming from the exhaust rates being specified higher than outdoor 
  air intake rates.  
  <br>**WARNING**********************************************************************<br>             
  ZONE EL1 ESE Perim Zn ( G.ESE1)        in 
  SYSTEM EL1 Sys1 (PTAC) (G.ESE1)        
  <br>             
  has unused EXHAUST-CFM 
  specified.<br>             
  This has been converted to outside air.<br><br>Thank you so much!  
  Looking forward to hearing back from those with thoughts/insights/experiences 
  on this. <br><br>Best,<br>Andy<br><br></blockquote></div></blockquote></div>