<p class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman">We are modeling a group of six buildings for a university which will be served by the current campus CUP's steam and chilled water loops.<span style="mso-spacerun: yes">
</span>These buildings will all be submitted for<span style="mso-spacerun: yes"> </span>LEED certification as one project.<span style="mso-spacerun: yes"> </span>Does anyone know if we can model the baseline from ASHRAE
90.1-2004 Appendix G for <i style="mso-bidi-font-style: normal">each</i> building according to its individual square footage, or if we have to choose the baseline system based off of the <i style="mso-bidi-font-style: normal">
total</i> square footage for the entire group of buildings?<span style="mso-spacerun: yes"> </span>For our project this would mean the difference between 90.1's System 5 (DX cooling) and System 7 (chilled water).<span style="mso-spacerun: yes">
</span></font><a name="QuickMark"></a><font face="Times New Roman"> </font></p>
<p class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman">I found this little excerpt from the LEED Application Guide for multiple buildings and campuses, but feel it doesn't really directly tackle the question of choosing the baseline system but could potentially be interpretted to mean that each building is considered separately during the modeling process and therefor would have a baseline system based off of its own square footage:
</font></p>
<p class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman"> </font></p>
<p class="Default" style="MARGIN: 0in 0in 0pt"><b><span style="FONT-SIZE: 14pt">EA Credit 1: Optimize Energy Performance </span></b><span style="FONT-SIZE: 14pt"></span></p>
<p class="Default" style="MARGIN: 6pt 0in"><b>Application Guidance </b></p>
<p class="Default" style="MARGIN: 6pt 0in"><b>Requirements </b></p>
<p class="Default" style="MARGIN: 6pt 0in"><span style="FONT-SIZE: 11pt">This credit applies to each building within the project scope. To receive a single rating for a group of buildings, use a weighted average for the group of buildings based on their conditioned square footage, or aggregate the data into one PRM calculation, so that performance is achieved by buildings of varying sizes within a certifying group. Each building must still meet EA Prerequisite 1 and may receive its own rating if that is desired.
</span></p>
<p class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman"> </font></p>
<p class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman"> Any experience with this? <font face="Times New Roman">Any guidance would be greatly appreciated.<span style="mso-spacerun: yes"> </span></font>
</font></p>
<div class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman">Thanks!</font></div>
<div class="MsoNormal" style="MARGIN: 0in 0in 0pt"><font face="Times New Roman">Kathryn</font></div>