Karen,<br>I just modeled a similar system in eQuest.  The central loop to loop heat pump worked out pretty well for me.  You have to set up the model (with all the necessary loops and pumps) in the detailed mode in eQuest.  I ran into a few quirks....I've been meaning to send them on to Jeff, but I'll just post them here instead.  They are only interface issues.
<br><br>

<ul style="margin-top: 0in;" type="square"><li class="MsoNormal" style="text-align: justify;"><font size="1">When creating a second HP type chiller by copying my
     first one, it asks me to create a new pump.<span style="">  </span>After I create that pump it never lets
     me out of the 'Required Chiller Data' dialogue box.<span style="">  </span>I ended up having to close eQuest with
     the task manager and couldn't save my file.</font></li></ul>



<ul style="margin-top: 0in;" type="square"><li class="MsoNormal" style="text-align: justify;"><font size="1">When creating a HP chiller from scratch, eQuest asks
     for a CHW loop, HW loop, and CW loop.<span style=""> 
     </span>The CW loop must be a lake/well loop but that isn't one of the
     options you're given to create.<span style=""> 
     </span>It's possible to get through this issue without things crashing,
     but it involved randomly clicking on cancel a half-dozen times.</font></li></ul>



<ul style="margin-top: 0in;" type="square"><li class="MsoNormal" style="text-align: justify;"><font size="1">When I try to change the pump 'motor class' and
     'capacity control' in the spreadsheet tab, I get errors.</font><br></li></ul>

The other thing that it sounds like you'll run into is that you can't put a boiler on the same loop as your heat pump.  I had to create a separate HW loop to model back-up energy use from a boiler for the building I was modeling.  I modeled the radiant system as induction units with fan power set to zero.
<br><br>Good luck,<br>Aleka<br><br><br>Hi All,<br><br>I have a question regarding eQuest:<br><br>I'm
modeling a house that will use a ground source heat pump with boiler
backup as a heat source.  The heat pumps will heat water that is
circulated through radiant tubing in the floor.  Is a loop-to-loop heat
pump a good way to model this?  I've done some research on it, but am
not sure whether this can be modeled in eQuest either in the wizards or
parametric runs without changing the BDL file directly.
<br><br>How are my options for
modeling cooling systems limited with the heating system described above?<br>
<br>Any help is appreciated.<br><br>Thank You,<br><br>~Karen~<br clear="all"><br>-- <br>Karen Walkerman<br>Second Law Consulting<br>802-238-0980<br><a href="mailto:kwalkerman@gmail.com">kwalkerman@gmail.com</a><br>