<span class="gmail_quote"></span>I am modeling a building in eQUEST with the following HVAC system types: PTAC, UVT, MZS, PMZS. The building is situated in New York City, where code ventilation requirements for the baseline model require exhaust rates roughly triple ASHRAE 62 guidelines (those requirements will be changing shortly). It is a 15 story multifamily building comprised of 5 shells due to different floor shapes and zoning patterns. I am having difficulty understanding three of the warning messages and thought I would see if other have experienced/solved these problems before. Thanks in advance!
<br><br>1) I am pretty sure this warning message pertains to the MZS or PMZS because they are the only two air-side systems with HSUPPLY specified in the INP file. <br><br>**WARNING**********************************************************************
<br> User-specified HSUPPLY-CFM is larger than<br> available return air. Heating capacity may<br> be inadequate.<br>I checked the BEPS report and it shows that <br>
"PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE = 86.0<br>
PERCENT OF HOURS ANY PLANT LOAD NOT SATISFIED = 0.0"<br><br>2) I tried increasing the "Pump Head" under "Domestic Water Heater/Attachments" in the DDI from the default of 1 to several other values, but the warning message always spits back a number that is 5 ft greater than whatever I enter under "Pump Head".
E.g., I enter Pump Head = 100, it spits back a loop head of 105 in the warning message.<br> **WARNING**********************************************************************<br> Pump: DHW Loop Pump has a user-specified head
<br> of 1. feet, but the loop head is 6. feet.<br><br>3) Per a recommendation from Mike Tillou on the BLDG-SIM archive, I tried changing all curves in the model to "default", but that did not remove the following error message (which repeats for literally hundreds of pages).
<br>CURINV: No real root for CURVE: <br> 1 1.353483 0.015932 -0.369414 0.000000 0.000000 0.000000<br>CURINV: No real root for CURVE: <br> 1 1.353483 0.015932 -0.369414 0.000000 0.000000 0.000000<br>CURINV: No real root for CURVE:
<br> 1 1.353483 0.015932 -0.369414 0.000000 0.000000 0.000000<br><br clear="all"><br>(Background):<br>Even though I think I've figured out the source of this warning message, I thought I'd include it in case it's relevant to understanding the warning messages above.
<br><br>This warning is coming from the exhaust rates being specified higher than outdoor air intake rates. <br>**WARNING**********************************************************************<br> ZONE EL1 ESE Perim Zn (
G.ESE1) in SYSTEM EL1 Sys1 (PTAC) (G.ESE1) <br> has unused EXHAUST-CFM specified.<br> This has been converted to outside air.<br><br>Thank you so much! Looking forward to hearing back from those with thoughts/insights/experiences on this.
<br><br>Best,<br>Andy<br><br>-- <br>****************************************************<br>Andrew McNamara, LEED AP<br>Bright Power, Inc.<br>43 W. 33rd St.<br>Suite 302<br>New York, NY 10001<br>p. 212.803.5868<br>f. 866.379.8026
<br>c. 917.974.4499<br><a href="mailto:amcnamara@brightpower.biz" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">amcnamara@brightpower.biz</a><br><a href="http://www.brightpower.biz" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">
www.brightpower.biz</a>
<br>