<html xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta name=Generator content="Microsoft Word 11 (filtered medium)">
<style>
<!--
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman";}
a:link, span.MsoHyperlink
{color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{color:purple;
text-decoration:underline;}
p
{mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman";}
span.highlight
{font-family:Arial;
font-weight:bold;
font-style:italic;}
p.tabletext, li.tabletext, div.tabletext
{margin-top:3.0pt;
margin-right:0in;
margin-bottom:3.0pt;
margin-left:0in;
line-height:11.0pt;
font-size:8.0pt;
font-family:Arial;}
span.EmailStyle20
{mso-style-type:personal-compose;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
{page:Section1;}
-->
</style>
</head>
<body lang=EN-US link=blue vlink=purple>
<div class=Section1>
<p style='margin-bottom:12.0pt'><font size=3 face="Times New Roman"><span
style='font-size:12.0pt'>All;<br>
When simulating (eQ v3-61, DOE-2.2 v44e4) a building with a "plenum"
(unconditioned or plenum), and changing the roof absorptance greatly, the auto-sized
design air flow does NOT seem to change in the zone below, even though the ZONE
SIZING-OPTION = ADJUST-LOADS. After observing this in a big model, I tested
this in a simple single zone model (eQ Wiz). I made sure airflow sizing was
driven by cooling loads, and created a parametric run that changed the
ABSORPTANCE of the roof construction between 90% and 10%. Hourly cooling loads
vary as expected, but design airflow remains the same between both models.<o:p></o:p></span></font>
</p>
<p style='margin-bottom:12.0pt'><font size=3 face="Times New Roman"><span
style='font-size:12.0pt'>Raising the DESIGN-COOL-T (from the default 75F, same
for all zones) in the "plenum" increases the design airflow in the
zone below (for both absorptances), but I thought ADJUST-LOADS did more than just
recognize this input. The problem seems to persist whether I have a cooling
design day or not, and whatever I do with the LOADS SPACE "TEMPERATUREs"
and ZONE DESIGN-COOL-Ts. <br>
<br>
Any insights out there? Anyone else notice this behavior? Is this a bug, or did
I expect too much of the program? Unless the DESIGN-COOL-T is raised (to a
value one must estimate or find by inspection of hourly reports), it appears the
program under-sizes airflow to zones where a significant fraction of the heat
gain is through a ceiling cavity/plenum/attic, or I suppose any
"un-conditioned" buffer space.<br>
<br>
Fred Porter<o:p></o:p></span></font>