<html xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns="http://www.w3.org/TR/REC-html40">

<head>

<meta name=Generator content="Microsoft Word 11 (filtered medium)">
<style>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman";}
a:link, span.MsoHyperlink
        {color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;
        text-decoration:underline;}
p
        {mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman";}
span.highlight
        {font-family:Arial;
        font-weight:bold;
        font-style:italic;}
p.tabletext, li.tabletext, div.tabletext
        {margin-top:3.0pt;
        margin-right:0in;
        margin-bottom:3.0pt;
        margin-left:0in;
        line-height:11.0pt;
        font-size:8.0pt;
        font-family:Arial;}
span.EmailStyle20
        {mso-style-type:personal-compose;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
        {page:Section1;}
-->
</style>

</head>

<body lang=EN-US link=blue vlink=purple>

<div class=Section1>

<p style='margin-bottom:12.0pt'><font size=3 face="Times New Roman"><span
style='font-size:12.0pt'>All;<br>

When simulating (eQ v3-61, DOE-2.2 v44e4) a building with a "plenum"
(unconditioned or plenum), and changing the roof absorptance greatly, the auto-sized
design air flow does NOT seem to change in the zone below, even though the ZONE
SIZING-OPTION = ADJUST-LOADS. After observing this in a big model, I tested
this in a simple single zone model (eQ Wiz). I made sure airflow sizing was
driven by cooling loads, and created a parametric run that changed the
ABSORPTANCE of the roof construction between 90% and 10%. Hourly cooling loads
vary as expected, but design airflow remains the same between both models.<o:p></o:p></span></font>

</p>

<p style='margin-bottom:12.0pt'><font size=3 face="Times New Roman"><span
style='font-size:12.0pt'>Raising the DESIGN-COOL-T (from the default 75F, same
for all zones) in the "plenum" increases the design airflow in the
zone below (for both absorptances), but I thought ADJUST-LOADS did more than just
recognize this input. The problem seems to persist whether I have a cooling
design day or not, and whatever I do with the LOADS SPACE "TEMPERATUREs"
and ZONE DESIGN-COOL-Ts. <br>

<br>

Any insights out there? Anyone else notice this behavior? Is this a bug, or did
I expect too much of the program? Unless the DESIGN-COOL-T is raised (to a
value one must estimate or find by inspection of hourly reports), it appears the
program under-sizes airflow to zones where a significant fraction of the heat
gain is through a ceiling cavity/plenum/attic, or I suppose any
"un-conditioned" buffer space.<br>

<br>

Fred Porter<o:p></o:p></span></font>