color=#0000ff size=2>Lynn,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=271562922-12072007><FONT face="Courier New" 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=271562922-12072007><FONT face="Courier New" 
color=#0000ff size=2>Do you really need the plenums?  Personally I find 
them non-value-added for most of our energy study work.  Suggest specifying 
ceiling height equal to floor-to-floor height in the DD wizard to make them 
disappear.  </FONT></SPAN></DIV>
<DIV><FONT face="Courier New" color=#0000ff size=2></FONT> </DIV>
<DIV><SPAN class=271562922-12072007><FONT face="Courier New" color=#0000ff 
size=2>Regards</FONT></SPAN></DIV>
<DIV align=left>
<DIV align=left><FONT face=Arial size=2></FONT> </DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">
<DIV><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN 
class=212011020-11052004><FONT color=#000000>Brandon Nichols, 
PE</FONT></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN 
class=212011020-11052004><FONT 
color=#000000>Mechanical</FONT></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#000080><STRONG>HARGIS ENGINEERS</STRONG></FONT></DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#515151>600 Stewart Street</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#515151>Suite 1000</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#515151>Seattle, WA 98101<?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#515151>www.hargis.biz<o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT 
color=#515151> <o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">d 
|</SPAN></B><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"> 
206.436.04<SPAN class=212011020-11052004>0</SPAN>0<SPAN 
style="mso-spacerun: yes">  </SPAN><B>c | </B>206.<SPAN 
class=212011020-11052004>228.8707</SPAN></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN 
class=212011020-11052004></SPAN></SPAN><FONT color=#515151><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">o 
|</SPAN></B><SPAN 
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"> 
206.448.3376<SPAN style="mso-spacerun: yes">  </SPAN><B>f <SPAN 
style="mso-spacerun: yes"> </SPAN>|</B> 
206.448.4450</SPAN></FONT></P></SPAN></SPAN>
<DIV> </DIV></DIV>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com 
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Lynn Qualmann<BR><B>Sent:</B> 
Thursday, July 12, 2007 3:03 PM<BR><B>To:</B> 
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Oh, what a tangled web we 
weave...<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT face=Arial size=2><SPAN class=356491421-12072007>I am using eQuest to 
model an office building with 3 unique floors, many spaces (with diff't use 
types) per floor and plenums between floors. I have already defined the 
appropriate footprints for each floor and imported them into a single model. 
NBD. Because there are many spaces per floor and plenums assume the shape of the 
space they sit over, it seemed like a good idea to import the plenums as 
separate, floor-shaped spaces. This was to allow internal floors and 
ceilings of the non-plenum spaces to be specified as NEXT-TO the appropriate 
plenum without any concern for the shape of the plenum. If each space on, say, 
Floor1 had an associated plenum reflecting the space shape, the 
spaces on Floor2 would not line up with those plenums. I defined neither a floor 
or ceiling for the plenums so that interior floors and ceilings would be part of 
the occupied spaces. As I'm sure many of you are thinking, DOE2 doesn't like 
that arrangement and requires at least two TILTs among the 
interior surfaces, i.e. walls + floor, walls + ceiling or floor + ceiling. 
If I put a floor in the 1st-floor plenum, I need to specify which space it is 
NEXT-TO and the approach falls apart. Obviously, the same deal applies to plenum 
ceilings. Has anyone got any ideas of how to work around this? Is it better to 
just associate the plenums with the spaces below them and let the chips fall 
where they may when the separate floors are imported (i.e. can heat transfer 
from/to plenums be ignored?)? Am I missing something really 
obvious?</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN 
class=356491421-12072007></SPAN></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=356491421-12072007>Thanks in 
advance.</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN 
class=356491421-12072007></SPAN></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=356491421-12072007>
<DIV align=left><FONT size=2><FONT face=Arial><STRONG>R. Lynn Qualmann, 
P.E</STRONG>.</FONT></FONT></DIV>
<DIV align=left><FONT face=Arial size=2>SBW Consulting, Inc.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>2820 Northup Way  #230</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Bellevue, WA  98004</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Phone:  (425) 827-0330</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>FAX:     (425) 
822-8119</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>e-mail:  <A 
href="mailto:rlq@sbwconsulting.com">rlq@sbwconsulting.com</A></FONT></DIV></SPAN></FONT></DIV><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>
****E-Mail Disclaimer****  This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to whom they are addressed. If you have received this email in error please notify the sender at once.  Any disclosure, copying, distribution or any action taken in reliance on it, is prohibited and may be unlawful.  Finally, the recipient should check this email and any attachments for the presence of viruses. The company accepts no liability for any damage caused by any virus transmitted by this email. SBW Consulting.</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>