face="Lucida Console" color=#0000ff size=2>Hello Tara,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2>See screen 23 of the eQuest
DD wizard. There is an input for exterior lighting in watts per square
foot for the selected shell. This unfortunately is not the way
exterior power is more generally characterized, namely as watts per linear foot
of perimeter. </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2>The input number is stored in
the pd2 file, and is multiplied by the shell square footage to obtain the
EXTERIOR-POWER value in kilowatts found in the inp file. The
EXT-USAGE keyword looks like it's used only to assign exterior power to a
particular electric meter.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=298350815-06072007><FONT
face="Lucida Console" color=#0000ff size=2>Generally I assign all the exterior
lighting load to the first floor Shell. You might try entering the data as
described above into the wizard, then saving the file and searching for the
keywords you're looking for in the inp file to see the syntax of
how they're used.</FONT></SPAN></DIV>
<DIV><FONT face="Lucida Console" color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face="Lucida Console"><FONT color=#0000ff><FONT size=2><SPAN
class=298350815-06072007>HTH</SPAN><SPAN
class=298350815-06072007>...</SPAN></FONT></FONT></FONT></DIV>
<DIV align=left>
<DIV align=left><FONT face=Arial size=2></FONT> </DIV><SPAN
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">
<DIV><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN
class=212011020-11052004><FONT color=#000000>Brandon Nichols,
PE</FONT></SPAN></SPAN></DIV>
<DIV><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN
class=212011020-11052004><FONT
color=#000000>Mechanical</FONT></SPAN></SPAN></DIV>
<DIV><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#000080><STRONG>HARGIS ENGINEERS</STRONG></FONT></DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#515151>600 Stewart Street</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#515151>Suite 1000</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#515151>Seattle, WA 98101<?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#515151>www.hargis.biz<o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><FONT
color=#515151> <o:p></o:p></FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">d
|</SPAN></B><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">
206.436.04<SPAN class=212011020-11052004>0</SPAN>0<SPAN
style="mso-spacerun: yes"> </SPAN><B>c | </B>206.<SPAN
class=212011020-11052004>228.8707</SPAN></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt"><SPAN
class=212011020-11052004></SPAN></SPAN><FONT color=#515151><B><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">o
|</SPAN></B><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
206.448.3376<SPAN style="mso-spacerun: yes"> </SPAN><B>f <SPAN
style="mso-spacerun: yes"> </SPAN>|</B>
206.448.4450</SPAN></FONT></P></SPAN></SPAN>
<DIV> </DIV></DIV>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@gard.com
[mailto:BLDG-SIM@gard.com] <B>On Behalf Of </B>Tara Streck<BR><B>Sent:</B>
Thursday, July 05, 2007 4:57 PM<BR><B>To:</B>
BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Exterior
Lighting<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><SPAN class=262235323-05072007><FONT face=Arial size=2>I am working on
adding exterior lighting loads to a building simulation and understand that
eQuest responds to EXTERIOR-POWER and EXT-USAGE as commands for this input.
However, I am unsure when to enter this information in the .inp file or what the
code might look like. Has anyone had experience with exterior
lighting?</FONT></SPAN></DIV>
<DIV><SPAN class=262235323-05072007><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=262235323-05072007><FONT face=Arial size=2>Thank
you,</FONT></SPAN></DIV>
<DIV> </DIV>
<DIV align=left>
<DIV align=left><FONT face=Arial>
<DIV align=left><FONT face="Palatino Linotype" size=2><STRONG>Tara
Streck</STRONG></FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>Mechanical
Engineer</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>LEED Accredited
Professional</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" color=#800000 size=2><STRONG>Wood
Harbinger, Inc.</STRONG></FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" color=#800000
size=2><STRONG>Mechanical/Electrical Engineers</STRONG></FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>3009 112th Ave NE, Ste
100</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>Bellevue, WA
98004-8008</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>(425)
822-9499</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2>(425) 822-4338
Fax</FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" size=2><A
title=mailto:tstreck@woodharbinger.com
href="blocked::mailto:tstreck@woodharbinger.com">tstreck@woodharbinger.com</A></FONT></DIV>
<DIV align=left><FONT face="Palatino Linotype" color=#0000ff
size=2><U>www.woodharbinger.com</U></FONT></DIV></FONT></DIV></DIV>
<DIV> </DIV><PRE>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>