<HTML><HEAD>
<META http-equiv=Content-Type content="text/html; charset=utf-8">
<META content="MSHTML 6.00.6000.16414" name=GENERATOR></HEAD>
<BODY style="MARGIN: 4px 4px 1px; FONT: 10pt Tahoma">
<DIV>Neeraj,</DIV>
<DIV>I would agree that your interpretation and your proposed 'option 2' appear to be meeting the requirements of App G. The LEED NC V2.2 Reference Guide (refer to EA Credit 1 Calculations for 'Other Systems,' page 182) indicates that where specific energy efficiency requirements exist in A90.1, the lowest allowable efficiency shall be used for the Baseline. Garage ventilation is included in the sample listing of 'other' systems and the fan power allowance should apply to that system. Not sure whether LEED CS V2.0 has something equivalent.</DIV>
<DIV> </DIV>
<DIV>That said, I am not a LEED reviewer. It would be interesting to hear what others think on this as the fan power allowance is likely easy to beat for a ventilation only system where system pressure drop is minimal. I would expect that the intent of App G may not be to 'credit' these types of systems.</DIV>
<DIV>Bill Talbert, AEI<BR><BR>>>> neeraj <near_ej@yahoo.com> 4/20/2007 1:14 PM >>><BR></DIV>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: arial,helvetica,sans-serif">
<DIV>Hi all,<BR>
<UL>
<LI>LEED, Core and Shell V2.0<BR></LI>
<LI>A 300,000 sqft building, 12 stories above ground located in Washington DC. The baseline building is System # 8, i.e. VAV fan controlled, PIU, all electric heating and cooling.<BR></LI>
<LI><SPAN style="TEXT-DECORATION: underline">Problem Area -- To determine a correct Baseline</SPAN>: In the proposed design, 3 levels of underground parking garage are merely ventilated with constant volume fans and they are not equipped with CO/NOx sensors , i.e. they are merely constant volume, SA and EA fans.</LI>
<LI>We know that garage ventilation is not process energy, so it must be regulated somehow, right?! Plus, we cannot take credit for energy savings from OA ventilation air (according to Appendix G). Now, since this is a 'fans only' situation in both the models (no cooling or heating) I have assumed the CFM of OA ventilation air must be the same in both cases. Am I correct, so far?<BR></LI>
<LI>Using this as a premise, the following two contradicting scenarios for an appropriate baseline model can reasonably  be thought of:</LI>
<OL>
<LI>Model similar SA and EA CFM as in the "Proposed Building Model" with similar fan power kW/CFM, OR</LI>
<LI>Model similar SA and EA CFM as in the "Proposed Building Model" but calculating the fan power for the OA flow using Section G3.1.2.9 of the Informative Appendix G of ASHRAE 90.1-2004.</LI></OL></UL>
<DIV style="TEXT-ALIGN: center">
<DIV style="TEXT-ALIGN: left"><SPAN style="TEXT-DECORATION: underline">THE BIG QUESTION(s)</SPAN>: Is the second option a valid approach for determining fan power (kW/CFM) for the baseline? <BR></DIV>OR<BR></DIV>Is the method only meant for determining (and thus crediting/penalising) system supply air fans and not parking garage fans?<BR><BR>Thanks,<BR>Neeraj<BR><BR></DIV></DIV><BR>
<HR SIZE=1>
Ahhh...imagining that irresistible "new car" smell?<BR>Check out <A href="http://us.rd.yahoo.com/evt=48245/*http://autos.yahoo.com/new_cars.html;_ylc=X3oDMTE1YW1jcXJ2BF9TAzk3MTA3MDc2BHNlYwNtYWlsdGFncwRzbGsDbmV3LWNhcnM-">new cars at Yahoo! Autos.</A> <PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>