color=#0000ff size=2>Andy:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2>For chiller and boilers, go into the Water Side Tab (I 
assume you are in the Detailed Edit Mode by this time), click on either chiller 
of boiler, go to the far right side to Capacity Ratio, and input 1.15 for 
chiller, and 1.25 for boilers.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2>For TWO identically sized machines,  use the logic 
shown below from the DOE2 help tab in eQuest.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial 
color=#0000ff size=2>
<DIV class=d2h_main_topic 
style="PADDING-RIGHT: 0pt; PADDING-LEFT: 0pt; PADDING-BOTTOM: 10pt; MARGIN: 0pt; PADDING-TOP: 0pt">
<H5>CAPACITY-RATIO</H5>
<P class=MsoBodyText>The fraction of the design loop capacity that the chiller 
will be sized to meet. This keyword is allowed only if CAPACITY is not 
specified. If you are defining two chillers of identical size that exactly meet 
the design loop load, set each chiller's CAPACITY-RATIO to 0.5. To include a 20% 
safety factor, set each chiller's CAPACITY-RATIO to 0.6. If neither CAPACITY nor 
CAPACITY-RATIO is specified, the chiller capacity will default to the loop 
capacity divided by the number of chillers attached to the 
loop.</P></DIV></FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Andy McNamara<BR><B>Sent:</B> 
Thursday, February 15, 2007 12:48 PM<BR><B>To:</B> 
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] eQUEST HVAC sizing 
runs<BR></FONT><BR></DIV>
<DIV></DIV>Hello,<BR><BR>As I mentioned previously, I am creating an energy 
model for a LEED project.  In "baselining" the building, one of the 
stipulations of ASHRAE 90.1 2004 is:<BR>"G3.1.2.2 Equipment Capacities.  
The equipment capacities for the baseline building design shall be based on 
sizing runs for each orientation and shall be oversized by 15% for cooling and 
25% for heating" <BR><BR>I think that means I use "auto-size", but then how do I 
capture what that size is and oversize it accordingly?  I am guessing that 
the results may be in the SIM file.  Can anyone provide tips for executing 
this?  Is there a better way to do that auto-sizing for each orientation? 