color=#0000ff size=2>Andy:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2>For chiller and boilers, go into the Water Side Tab (I
assume you are in the Detailed Edit Mode by this time), click on either chiller
of boiler, go to the far right side to Capacity Ratio, and input 1.15 for
chiller, and 1.25 for boilers.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2>For TWO identically sized machines, use the logic
shown below from the DOE2 help tab in eQuest.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=613132721-15022007><FONT face=Arial
color=#0000ff size=2>
<DIV class=d2h_main_topic
style="PADDING-RIGHT: 0pt; PADDING-LEFT: 0pt; PADDING-BOTTOM: 10pt; MARGIN: 0pt; PADDING-TOP: 0pt">
<H5>CAPACITY-RATIO</H5>
<P class=MsoBodyText>The fraction of the design loop capacity that the chiller
will be sized to meet. This keyword is allowed only if CAPACITY is not
specified. If you are defining two chillers of identical size that exactly meet
the design loop load, set each chiller's CAPACITY-RATIO to 0.5. To include a 20%
safety factor, set each chiller's CAPACITY-RATIO to 0.6. If neither CAPACITY nor
CAPACITY-RATIO is specified, the chiller capacity will default to the loop
capacity divided by the number of chillers attached to the
loop.</P></DIV></FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Andy McNamara<BR><B>Sent:</B>
Thursday, February 15, 2007 12:48 PM<BR><B>To:</B>
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] eQUEST HVAC sizing
runs<BR></FONT><BR></DIV>
<DIV></DIV>Hello,<BR><BR>As I mentioned previously, I am creating an energy
model for a LEED project. In "baselining" the building, one of the
stipulations of ASHRAE 90.1 2004 is:<BR>"G3.1.2.2 Equipment Capacities.
The equipment capacities for the baseline building design shall be based on
sizing runs for each orientation and shall be oversized by 15% for cooling and
25% for heating" <BR><BR>I think that means I use "auto-size", but then how do I
capture what that size is and oversize it accordingly? I am guessing that
the results may be in the SIM file. Can anyone provide tips for executing
this? Is there a better way to do that auto-sizing for each orientation?
<BR><BR>Thanks,<BR>Andrew McNamara<BR><PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>