<span class="gmail_quote"></span>Andrew makes a good point. Set either system or plant sizing factors to 1.15 & 1.25 respectively, but not both.<br><br>Gail Stranske<br><div><span class="e" id="q_110c7ba571f14c03_1"><br>
<br><div><span class="gmail_quote">On 2/15/07, <b class="gmail_sendername">Andrew Craig</b>
<<a href="mailto:andrew_c@ieice.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">andrew_c@ieice.com</a>> wrote:</span><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p><font color="navy" face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial; color: navy;">Assuming you are using eQUEST, in the
Detailed Edit mode, you can specify the ratio of equipment sizing that you want
for both heating and cooling. So to specify the Appendix G baseline model, you
would oversize cooling by a factor of 1.15 and heating by a factor of 1.25.
Take care to check what the system sizing ratio is set at as well so you don't
add safety factor upon safety factor. Good luck.</span></font></p>
<p><font color="navy" face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p><font color="navy" face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<div>
<div style="text-align: center;" align="center"><font face="Times New Roman" size="3"><span style="font-size: 12pt;">
<hr align="center" size="2" width="100%">
</span></font></div>
<p><b><font face="Tahoma" size="2"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font face="Tahoma" size="2"><span style="font-size: 10pt; font-family: Tahoma;">
<a href="mailto:bldg-sim@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">bldg-sim@gard.com</a> [mailto:<a href="mailto:bldg-sim@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">
bldg-sim@gard.com</a>] <b><span style="font-weight: bold;">On
Behalf Of </span></b>Andy McNamara<br>
<b><span style="font-weight: bold;">Sent:</span></b> Thursday, February 15, 2007
12:48 PM<br>
<b><span style="font-weight: bold;">To:</span></b> <a href="mailto:bldg-sim@gard.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">bldg-sim@gard.com</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> [bldg-sim] eQUEST HVAC
sizing runs</span></font></p>
</div>
<p><font face="Times New Roman" size="3"><span style="font-size: 12pt;"> </span></font></p>
<p><font face="Times New Roman" size="3"><span style="font-size: 12pt;">Hello,<br>
<br>
As I mentioned previously, I am creating an energy model for a LEED
project. In "baselining" the building, one of the stipulations
of ASHRAE 90.1 2004 is:<br>
"G3.1.2.2 Equipment Capacities. The equipment capacities for the
baseline building design shall be based on sizing runs for each orientation and
shall be oversized by 15% for cooling and 25% for heating" <br>
<br>
I think that means I use "auto-size", but then how do I capture what
that size is and oversize it accordingly? I am guessing that the results
may be in the SIM file. Can anyone provide tips for executing this?
Is there a better way to do that auto-sizing for each orientation? <br>
<br>
Thanks,<br>
Andrew McNamara</span></font></p>