color=#0000ff size=2>Steve:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=384231122-30012007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=384231122-30012007><FONT face=Arial
color=#0000ff size=2>What type of HVAC system are you running? A VAV system
Outside air will only see the mixing with return air upstream of the coil. The
cooling coil will adjust as required to maintain the 55 °F setpoint need as
outside conditions change. Downstream, the reheat coils will never see the
outside conditions.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=384231122-30012007><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=384231122-30012007><FONT face=Arial
color=#0000ff size=2>Correct me if I am wrong...</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Steve Barnell<BR><B>Sent:</B>
Tuesday, January 30, 2007 1:54 PM<BR><B>To:</B>
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Min Outdoor
Air<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>Hello,</DIV>
<DIV> </DIV>
<DIV>I am modelling a building in Canada with eQUEST and have several runs
varying the min OA rate. In comparing the runs I noticed that the cooling
comsumption varied as expected however the Space Heating comsumption
is not altered. This seems counter intuitive to me. Any ideas?</DIV>
<DIV> </DIV>
<DIV>-Steve</DIV><BR>-- <A
href="http://a8-asy.a8ww.net/a8-ads/adftrclick?redirectid=en-mail_a_01"
target=_blank><IMG alt=""
src="http://a8-asy.a8ww.net/a8-ads/adftrview?redirectid=en-mail_i_01" border=0
NOSEND="1"></A> <PRE>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>