color=#0000ff size=2>What do you mean by Horizontal Shading? Like fins (the 
device fin are vertical, but cut down light horizontally) ??</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=822485423-17012007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=822485423-17012007></SPAN><FONT 
face=Arial><FONT color=#0000ff><FONT size=2>I<SPAN class=822485423-17012007> 
just ran a typical office (250,000 sf) in Fresno, CA in eQuest.  When I put 
2.5 ft fins on all the windows, I got a slight decrease in heating as well (but 
not to your % level).</SPAN></FONT></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007></SPAN></FONT></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007>I traded the 2.5 ft fins with 2.5 overhangs. I got a 
15% decrease in cooling, and a 13% decrease in heating. This building is 
dominated by VAV/reheat. What I can surmise is that when the cooling load 
decreased, the need to reheat decreased as well. That the building is not skin 
dominated for energy.</SPAN></FONT></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007></SPAN></FONT></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007>Anyone else have a 
clue?</SPAN></FONT></FONT></FONT></DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007></SPAN></FONT></FONT></FONT> </DIV>
<DIV><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=822485423-17012007>
<DIV align=left>
<DIV align=left><FONT color=#0000ff>John R. Aulbach, PE, CEM</FONT></DIV>
<DIV align=left><FONT face=Arial size=2><EM>Project Manager</EM></FONT></DIV>
<DIV align=left><FONT face=Arial size=2><FONT color=#0000ff>Nexant, 
Inc</FONT>.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>100 North Barranca, Suite 
820</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>West Covina, CA 91791 USA</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Phone: 626-430-9054</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Fax: 626-430-9060</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>email: <A 
title=mailto:jaulbach@nexant.com 
href="mailto:jaulbach@nexant.com">jaulbach@nexant.com</A></FONT></DIV>
<DIV> </DIV></DIV></SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><BR></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Jaya Mukhopadhyay<BR><B>Sent:</B> 
Wednesday, January 17, 2007 3:25 PM<BR><B>To:</B> 
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Horizontal shading in 
EQUEST<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>I am examining several options for Horizontal shading for an office 
building using EQUEST.</DIV>
<DIV>A synopsis of the answers is as follows:</DIV>
<DIV>
<TABLE style="WIDTH: 362pt; BORDER-COLLAPSE: collapse" cellSpacing=0 
cellPadding=0 width=482 border=0 x:str>
  <COLGROUP>
  <COL style="WIDTH: 125pt; mso-width-source: userset; mso-width-alt: 6070" 
  width=166>
  <COL style="WIDTH: 92pt; mso-width-source: userset; mso-width-alt: 4498" 
  width=123>
  <COL style="WIDTH: 70pt; mso-width-source: userset; mso-width-alt: 3401" 
  width=93>
  <COL style="WIDTH: 75pt; mso-width-source: userset; mso-width-alt: 3657" 
  width=100>
  <TBODY>
  <TR style="HEIGHT: 27pt; mso-height-source: userset" height=36>
    <TD 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 125pt; BORDER-BOTTOM: #ece9d8; HEIGHT: 27pt; BACKGROUND-COLOR: transparent" 
    width=166 height=36></TD>
    <TD class=xl25 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 92pt; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    width=123><FONT size=2><STRONG>Total Annual Energy MBTU</STRONG></FONT></TD>
    <TD class=xl25 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 70pt; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    width=93><FONT size=2><STRONG>Space Cooling MBTU</STRONG></FONT></TD>
    <TD class=xl25 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 75pt; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    width=100><FONT size=2><STRONG>Space Heating MBTU</STRONG></FONT></TD></TR>
  <TR style="HEIGHT: 15pt; mso-height-source: userset" height=20>
    <TD class=xl26 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; HEIGHT: 15pt; BACKGROUND-COLOR: transparent" 
    height=20><STRONG><FONT size=2>Unshaded Option</FONT></STRONG></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>8380</FONT></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>2411.9</FONT></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>308.1</FONT></TD></TR>
  <TR style="HEIGHT: 25.5pt; mso-height-source: userset" height=34>
    <TD class=xl27 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 125pt; BORDER-BOTTOM: #ece9d8; HEIGHT: 25.5pt; BACKGROUND-COLOR: transparent" 
    width=166 height=34>
      <DIV><STRONG><FONT size=2>2.5 ft Horizontal shading on East West and 
      South</FONT></STRONG></DIV>
      <DIV><STRONG><FONT size=2></FONT></STRONG> </DIV></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>7936.8</FONT></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>2178.8</FONT></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num><FONT size=2>284.2</FONT></TD></TR>
  <TR style="HEIGHT: 25.5pt; mso-height-source: userset" height=34>
    <TD class=xl27 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; WIDTH: 125pt; BORDER-BOTTOM: #ece9d8; HEIGHT: 25.5pt; BACKGROUND-COLOR: transparent" 
    width=166 height=34><STRONG><FONT size=2>5 ft Horizontal shading on East 
      West and South</FONT></STRONG></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num>
      <DIV><FONT size=2></FONT> </DIV>
      <DIV><FONT size=2>7835</FONT></DIV></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num>
      <DIV><FONT size=2></FONT> </DIV>
      <DIV><FONT size=2>2158</FONT></DIV></TD>
    <TD class=xl24 
    style="BORDER-RIGHT: #ece9d8; BORDER-TOP: #ece9d8; BORDER-LEFT: #ece9d8; BORDER-BOTTOM: #ece9d8; BACKGROUND-COLOR: transparent" 
    x:num>
      <DIV><FONT size=2></FONT> </DIV>
      <DIV><FONT size=2>269.7</FONT></DIV></TD></TR></TBODY></TABLE></DIV>
<DIV> </DIV>
<DIV>The Questions:</DIV>
<DIV>1. Its very baffling to see the heating consumption go down too. I wanted 
to see an increase in heating on implementing the shading devices. How can I 
justify that decrease?</DIV>
<DIV> </DIV>
<DIV>2. The building has a total area of 210273 sqft. with 15 ft deep perimeter 
zones. The shading reduces the energy consumption by 5 to 6 %. Is that 
acceptable?</DIV>
<DIV> </DIV>
<DIV>Any help is greatly appreciated.</DIV>
<DIV>Thank you </DIV>
<DIV>Jaya Mukhopadhyay</DIV>
<P>
<HR SIZE=1>
<A 
href="http://us.rd.yahoo.com/evt=49678/*http://smallbusiness.yahoo.com/domains/?p=BESTDEAL">Get 
your own web address.</A><BR>Have a HUGE year through <A 
href="http://us.rd.yahoo.com/evt=49678/*http://smallbusiness.yahoo.com/domains/?p=BESTDEAL">Yahoo! 
Small Business.</A><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>