color=#0000ff size=2>I have a question which might have been proposed to the 
Bldg. Sim. in the past but I'm not sure. Regarding underfloor air systems, 
since  DOE2 assumes a well mixed space and cannot model the 
destratification effect and since the supply air temperature for heating 
and cooling tends to be much lower/higher than typical conditions, the 
throttling range tends to be quite high. There is an exception in ASHRAE 90.1 
Appendix G that if you have a high throttling range you can try to argue an 
exception to this but I'm not sure if LEED would accept this. This might be 
similar to the natural ventilation issue. Would an underfloor air system which 
has typically 62 F to 64 F SAT with room thermostat settings of 72 to 75 
F fall under this exception for LEED since DOE2 cannot mode the 
distratification effect or do most people try to force the throttling range 
down to meet LEED/ASHRAE requirements which is what I have done in the 
past.  I did not see anything in the USGBC Credit Interpretation 
Rulings regarding this subject. I have heard the next version of eQuest 
should be able to model underfloor air systems and that Energy Plus does but 
until then.....</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=500553503-02012007><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=500553503-02012007><FONT face=Arial 
color=#0000ff size=2>Thank you,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-weight: bold"></SPAN></STRONG> </DIV>
<DIV dir=ltr align=left><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-weight: bold">Renée<?xml:namespace 
prefix = o ns = "urn:schemas-microsoft-com:office:office" 
/><o:p></o:p></SPAN></STRONG></DIV>
<DIV class=Section1>
<P class=MsoNormal><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: blue; FONT-FAMILY: Arial">Renée <SPAN 
class=SpellE>Azerbegi</SPAN>, CEM, LEED-AP<o:p></o:p></SPAN></STRONG></P>
<P class=MsoNormal><SPAN class=GramE><STRONG><SPAN 
style="COLOR: blue; FONT-FAMILY: Arial">ambient</SPAN></STRONG></SPAN><STRONG><SPAN 
style="COLOR: blue; FONT-FAMILY: Arial"> energy – solar & sustainable design 
solutions<o:p></o:p></SPAN></STRONG></P>
<P class=MsoNormal><SPAN class=GramE><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial">t</SPAN></STRONG></SPAN><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial"> 303.278.1532 | f 
303.278.8533 | c 303.885.2695 | </SPAN></STRONG><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial; mso-bidi-font-weight: normal">renee@ambient-e.com</SPAN></STRONG><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial"> 
</SPAN></STRONG><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial">|</SPAN></STRONG><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial; mso-bidi-font-weight: normal"> 
</SPAN></STRONG><STRONG><SPAN 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: Arial">ambient-e.com  
</SPAN></STRONG><SPAN style="COLOR: navy"><o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></P>
<P class=MsoNormal> </P></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Mike Tillou<BR><B>Sent:</B> 
Thursday, December 28, 2006 10:56 AM<BR><B>To:</B> 
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with natural 
ventilation for Appendix G<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><SPAN class=276444817-28122006><FONT face=Arial color=#0000ff size=2>There 
is no specific temperature range called out but Section G3.1.2.2 does limit the 
number of unmet heating and cooling hours your simulation can have.  The 
heating and cooling schedules you establish would be the required high / low 
temperatures you would need to meet.  </FONT></SPAN></DIV>
<DIV><SPAN class=276444817-28122006><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=276444817-28122006><FONT face=Arial color=#0000ff size=2>Again 
my interpretation of the Exception Calculation methodology is that if I feel the 
design I am modeling doesn't need to meet G3.1.2.2 then I need to argue the case 
why.</FONT></SPAN></DIV>
<DIV><SPAN class=276444817-28122006><FONT face=Arial color=#0000ff 
size=2>   </FONT></SPAN></DIV>
<DIV> </DIV><!-- Converted from text/rtf format -->
<P><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=2>Michael Tillou, 
PE</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=1>ETC 
Group, Inc - Energy Engineering for a Sustainable Future</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT face="Swis721 Blk BT" size=1>Ph:413-458-9870</FONT></SPAN> </P>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> 
  bldg-sim@gard.com [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Jon 
  McHugh<BR><B>Sent:</B> Thursday, December 21, 2006 2:44 PM<BR><B>To:</B> 
  bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with 
  natural ventilation for Appendix G<BR><BR></FONT></DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff>Mike,</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff>The prescribed range being what?  Is there a schedule of 
  high and low  temperatures that are called out in Appendix 
  G?</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff>Thanks,</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
  color=#0000ff>Jon</FONT></SPAN></DIV><BR>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
  <HR tabIndex=-1>
  <FONT face=Tahoma size=2><B>From:</B> Mike Tillou [mailto:miket@etcgrp.com] 
  <BR><B>Sent:</B> Thursday, December 21, 2006 11:12 AM<BR><B>To:</B> Jon 
  McHugh; bldg-sim@gard.com<BR><B>Subject:</B> RE: [bldg-sim] Modeling buildings 
  with natural ventilation for Appendix G<BR></FONT><BR></DIV>
  <DIV></DIV>
  <DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff size=2>I 
  have always gone under the assumption that my results have to meet the 
  criteria for zone temperatures being within the prescribed 
  range.</FONT></SPAN></DIV>
  <DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff 
  size=2>MMT</FONT></SPAN></DIV>
  <DIV> </DIV><!-- Converted from text/rtf format -->
  <P><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=2>Michael Tillou, 
  PE</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=1>ETC 
  Group, Inc - Energy Engineering for a Sustainable Future</FONT></SPAN> 
  <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" 
  size=1>Ph:413-458-9870</FONT></SPAN> </P>
  <BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
    <DIV></DIV>
    <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
    face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> Jon McHugh 
    [mailto:Jon.McHugh@h-m-g.com] <BR><B>Sent:</B> Tuesday, December 19, 2006 
    1:25 PM<BR><B>To:</B> Mike Tillou; bldg-sim@gard.com<BR><B>Subject:</B> RE: 
    [bldg-sim] Modeling buildings with natural ventilation for Appendix 
    G<BR><BR></FONT></DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff>Mike,</FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff>Does this proposed methodology place limits on the number 
    of occupied hours above or below a given temperature/RH?</FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff>Thanks,</FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
    color=#0000ff>Jon McHugh</FONT></SPAN></DIV><BR>
    <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
    <HR tabIndex=-1>
    <FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
    [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Mike Tillou<BR><B>Sent:</B> 
    Tuesday, December 19, 2006 7:18 AM<BR><B>To:</B> 
    bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with 
    natural ventilation for Appendix G<BR></FONT><BR></DIV>
    <DIV></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2>Ramana,</FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2>The ASHRAE 90.1 ECB sub-committee is working on a methodology for 
    simulating natural ventilation within the framework of Appendix G but I 
    don't think its finished yet.  In the meantime here is what I would 
    recommend.</FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2>Appendix G / 90.1 ECB allows you to use 
    an exception calculation method to simulate hybrid systems or 
    unique efficiency measures to demonstrate above-standard performance.  
    I think this would certainly apply in your case.   
    </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV><SPAN class=479163814-19122006></SPAN><SPAN 
    class=479163814-19122006><FONT face=Arial color=#0000ff size=2>Here's what I 
    have done on projects requiring an exception calculation method.  
    </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>1. 
    Establish your energy cost budget and your design energy case 
    following the Appendix G guidelines.  </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>2. 
    Create a second model using the Design Energy Case as the baseline and make 
    the necessary modifications to simulate radiant heating / no cooling via 
    natural ventilation.  </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>3. 
    Report the energy savings from your exception calculation as a line item at 
    the end of your LEED EA-1 summary table (similar to how renewable energy is 
    reported). </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>4. 
     Include a seperate summary table  for the exception 
    calculation showing the energy end-use breakdown and how you arrived at 
    the cost savings.  Show both the baseline and proposed energy 
    use.  </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>5. 
    Make sure the savings are reasonable and prudent for the system you are 
    proposing.  </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>6. 
    Document any changes to the model especially changes to schedules that were 
    necessary to properly simulate your system. </FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>7. 
    Make it easy for someone to review your assumptions and the methodology 
    you used to estimate the savings</FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>I 
    hope this helps.  Good luck.</FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2>Mike</FONT></SPAN></DIV>
    <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV><!-- Converted from text/rtf format -->
    <P><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=2>Michael Tillou, 
    PE</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=1>ETC 
    Group, Inc - Energy Engineering for a Sustainable Future</FONT></SPAN> 
    <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" 
    size=1>Ph:413-458-9870</FONT></SPAN> </P>
    <BLOCKQUOTE style="MARGIN-RIGHT: 0px">
      <DIV></DIV>
      <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
      face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> 
      bldg-sim@gard.com [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Ramana 
      Koti<BR><B>Sent:</B> Monday, December 18, 2006 4:53 PM<BR><B>To:</B> 
      bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with 
      natural ventilation for Appendix G<BR><BR></FONT></DIV>Dear all,<BR><BR>Is 
      ignoring natural ventilation in both proposed and baseline designs an 
      accepted/fair way of modeling based on Appendix G (ASHRAE 
      90.1-2004)?<BR><BR>Part of the proposed design has (radiant heating + 
      natural ventilation) with no cooling which was modeled as a radiant slab, 
      no cooling, natural ventilation ignored. <BR><BR>But the Baseline HVAC 
      system based on Appendix G is System 5: Packaged VAV w/Reheat. (Natural 
      ventilation can be modeled based on Air Change method or Sherman Grimsrud 
      method though I do not know how to do it).<BR><BR>I cannot decide how to 
      make the baseline and proposed comparable with respect to Natural 
      Ventilation (in a manner acceptable to LEED review), suggestions will be 
      appreciated.<BR><BR>Thanks,<BR><BR>Ramana Koti, Sustainable Building 
      Analyst <BR>LEED AP<BR><BR>ELEMENTS | a division of berkebile nelson 
      immenschuh mcdowell architects<BR>106 W. 14th Street Suite 200<BR>Kansas 
      City, Missouri 64105<BR><BR>p 816.783.1635 f 816.783.1501<BR>www.bnim.com| 
      <A 
href="http://elements.bnim.com">elements.bnim.com</A><BR><BR></BLOCKQUOTE><PRE>==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>