color=#0000ff>Mike,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff>The prescribed range being what?  Is there a schedule of high 
and low  temperatures that are called out in Appendix 
G?</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff>Thanks,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=609024419-21122006><FONT face=Arial 
color=#0000ff>Jon</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> Mike Tillou [mailto:miket@etcgrp.com] 
<BR><B>Sent:</B> Thursday, December 21, 2006 11:12 AM<BR><B>To:</B> Jon McHugh; 
bldg-sim@gard.com<BR><B>Subject:</B> RE: [bldg-sim] Modeling buildings with 
natural ventilation for Appendix G<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff size=2>I have 
always gone under the assumption that my results have to meet the criteria for 
zone temperatures being within the prescribed range.</FONT></SPAN></DIV>
<DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=329500519-21122006><FONT face=Arial color=#0000ff 
size=2>MMT</FONT></SPAN></DIV>
<DIV> </DIV><!-- Converted from text/rtf format -->
<P><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=2>Michael Tillou, 
PE</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=1>ETC 
Group, Inc - Energy Engineering for a Sustainable Future</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT face="Swis721 Blk BT" size=1>Ph:413-458-9870</FONT></SPAN> </P>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> Jon McHugh 
  [mailto:Jon.McHugh@h-m-g.com] <BR><B>Sent:</B> Tuesday, December 19, 2006 1:25 
  PM<BR><B>To:</B> Mike Tillou; bldg-sim@gard.com<BR><B>Subject:</B> RE: 
  [bldg-sim] Modeling buildings with natural ventilation for Appendix 
  G<BR><BR></FONT></DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff>Mike,</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff>Does this proposed methodology place limits on the number 
  of occupied hours above or below a given temperature/RH?</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff>Thanks,</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=187512418-19122006><FONT face=Arial 
  color=#0000ff>Jon McHugh</FONT></SPAN></DIV><BR>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
  <HR tabIndex=-1>
  <FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
  [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Mike Tillou<BR><B>Sent:</B> 
  Tuesday, December 19, 2006 7:18 AM<BR><B>To:</B> 
  bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with 
  natural ventilation for Appendix G<BR></FONT><BR></DIV>
  <DIV></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2>Ramana,</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>The 
  ASHRAE 90.1 ECB sub-committee is working on a methodology for simulating 
  natural ventilation within the framework of Appendix G but I don't think its 
  finished yet.  In the meantime here is what I would 
  recommend.</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2>Appendix G / 90.1 ECB allows you to use 
  an exception calculation method to simulate hybrid systems or 
  unique efficiency measures to demonstrate above-standard performance.  I 
  think this would certainly apply in your case.   
</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=479163814-19122006></SPAN><SPAN 
  class=479163814-19122006><FONT face=Arial color=#0000ff size=2>Here's what I 
  have done on projects requiring an exception calculation method.  
  </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>1. 
  Establish your energy cost budget and your design energy case 
  following the Appendix G guidelines.  </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>2. 
  Create a second model using the Design Energy Case as the baseline and make 
  the necessary modifications to simulate radiant heating / no cooling via 
  natural ventilation.  </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>3. 
  Report the energy savings from your exception calculation as a line item at 
  the end of your LEED EA-1 summary table (similar to how renewable energy is 
  reported). </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>4. 
   Include a seperate summary table  for the exception 
  calculation showing the energy end-use breakdown and how you arrived at 
  the cost savings.  Show both the baseline and proposed energy use.  
  </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>5. 
  Make sure the savings are reasonable and prudent for the system you are 
  proposing.  </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>6. 
  Document any changes to the model especially changes to schedules that were 
  necessary to properly simulate your system. </FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>7. 
  Make it easy for someone to review your assumptions and the methodology 
  you used to estimate the savings</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff size=2>I 
  hope this helps.  Good luck.</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2>Mike</FONT></SPAN></DIV>
  <DIV><SPAN class=479163814-19122006><FONT face=Arial color=#0000ff 
  size=2></FONT></SPAN> </DIV><!-- Converted from text/rtf format -->
  <P><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=2>Michael Tillou, 
  PE</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" size=1>ETC 
  Group, Inc - Energy Engineering for a Sustainable Future</FONT></SPAN> 
  <BR><SPAN lang=en-us><FONT face="Swis721 Blk BT" 
  size=1>Ph:413-458-9870</FONT></SPAN> </P>
  <BLOCKQUOTE style="MARGIN-RIGHT: 0px">
    <DIV></DIV>
    <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
    face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> 
    bldg-sim@gard.com [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Ramana 
    Koti<BR><B>Sent:</B> Monday, December 18, 2006 4:53 PM<BR><B>To:</B> 
    bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Modeling buildings with 
    natural ventilation for Appendix G<BR><BR></FONT></DIV>Dear all,<BR><BR>Is 
    ignoring natural ventilation in both proposed and baseline designs an 
    accepted/fair way of modeling based on Appendix G (ASHRAE 
    90.1-2004)?<BR><BR>Part of the proposed design has (radiant heating + 
    natural ventilation) with no cooling which was modeled as a radiant slab, no 
    cooling, natural ventilation ignored. <BR><BR>But the Baseline HVAC system 
    based on Appendix G is System 5: Packaged VAV w/Reheat. (Natural ventilation 
    can be modeled based on Air Change method or Sherman Grimsrud method though 
    I do not know how to do it).<BR><BR>I cannot decide how to make the baseline 
    and proposed comparable with respect to Natural Ventilation (in a manner 
    acceptable to LEED review), suggestions will be 
    appreciated.<BR><BR>Thanks,<BR><BR>Ramana Koti, Sustainable Building Analyst 
    <BR>LEED AP<BR><BR>ELEMENTS | a division of berkebile nelson immenschuh 
    mcdowell architects<BR>106 W. 14th Street Suite 200<BR>Kansas City, Missouri 
    64105<BR><BR>p 816.783.1635 f 816.783.1501<BR>www.bnim.com| <A 
    href="http://elements.bnim.com">elements.bnim.com</A><BR><BR></BLOCKQUOTE><PRE>==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>