color=#0000ff size=2>Mark,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2>The best way to test custom curve fits is to use the boiler 
hourly reports and check the efficiency/fuel consumption that is being 
calculated against what you are expecting to see.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2>Regards,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2>Peter</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=886021918-21122006>
<DIV align=left>
<DIV align=left><FONT face=Arial size=2>Peter Alspach, P.E.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Associate</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Arup</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>403 Columbia St., Suite 220</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Seattle, WA 98104</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>T: 206-493-2226</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>C: 206-<SPAN class=char id=TB><SPAN 
class=char id=VS><SPAN>816</SPAN>-</SPAN></SPAN><SPAN class=char 
id=VS><SPAN>4902</SPAN></SPAN></FONT></DIV>
<DIV align=left><FONT face=Arial size=2><SPAN class=char><SPAN>F: 
206-749-0665</SPAN></SPAN></FONT></DIV>
<DIV align=left><FONT face=Arial size=2>E: 
peter.alspach@arup.com</FONT></DIV></DIV></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> BLDG-SIM@GARD.COM 
[mailto:BLDG-SIM@GARD.COM] <B>On Behalf Of </B>Mark Nieman<BR><B>Sent:</B> 
Thursday, December 21, 2006 9:42 AM<BR><B>To:</B> 
BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM] eQUEST Condensing Boiler 
Curve<BR></FONT><BR></DIV>
<DIV></DIV><!-- Converted from text/rtf format -->
<P><FONT face=Courier size=2>Using eQUEST v.3.6, I've taken a stab at creating a 
performance curve for an Aerco KC1000 condensing boiler. I've defined 
BOILER:HIR-FT = "Aerco-KC1000-HIR-fEWT&LWT" as shown below. This boiler is 
being used for a water source heat pump condenser water loop with a CT/HX & 
two condensing boilers, piped in a primary loop configuration.</FONT></P>
<P><FONT face=Courier size=2>"Aerco-KC1000-HIR-fEWT&LWT" = 
CURVE-FIT       </FONT><BR><FONT face=Courier 
size=2>   
TYPE             = 
BI-QUADRATIC-T</FONT> <BR><FONT face=Courier size=2>   
INPUT-TYPE       = DATA</FONT> <BR><FONT 
face=Courier size=2>   INDEPENDENT-1    = ( 180, 180, 
180, 80, 80, 80, 100, 100, 100, 120, 120, </FONT><BR><FONT face=Courier 
size=2>         120, 140, 140, 140, 160, 
160, 160 )</FONT> <BR><FONT face=Courier size=2>   
INDEPENDENT-2    = ( 180, 90, 135, 90, 135, 180, 90, 135, 180, 
90, 135, </FONT><BR><FONT face=Courier 
size=2>         180, 90, 135, 180, 90, 
135, 180 )</FONT> <BR><FONT face=Courier size=2>   
DEPENDENT        = ( 1, 1.023, 1.019, 1.151, 
1.077, 1.065, 1.102, 1.047, </FONT><BR><FONT face=Courier 
size=2>         1.038, 1.053, 1.026, 
1.017, 1.033, 1.017, 1.012, 1.023, 1.017, </FONT><BR><FONT face=Courier 
size=2>         1.007 )</FONT> <BR><FONT 
face=Courier size=2>   ..</FONT> </P>
<P><FONT face=Courier size=2>Question: Is this a proper curve for this 
equipment? Any comments and critiques would be much appreciated. Part of my 
difficulty is that HIR-FT is a Bi-Quadratic-T or Bi-Linear-T curve that needs 
two temperatures (EWT & LWT) to define the HIR ratio modifier. When looking 
at the curves, it's stated as thermal efficiency vs. EWT (return water 
temperature) on several different curves based on fire rate of the boiler. 
Basically, I assumed a LWT based on firing rate (90F=25%, 135F=75% & 
180F=100%). I'm not sure if this is reasonable or not. Per the manual, the 
DEPENDENT variable is the ratio of the actual efficiency (based on the curves) / 
rated efficiency (at full fire, full load). INDEPENDENT-1 = EWT, INDEPENDENT-2 = 
LWT.</FONT></P>
<P><FONT face=Courier size=2>The link to the data sheet is here:</FONT> <BR><A 
href="http://www.aerco.com/cgi-bin/docsserv.cgi?idDocument=344"><U><FONT 
face=Arial color=#0000ff 
size=2>http://www.aerco.com/cgi-bin/docsserv.cgi?idDocument=344</FONT></U></A> 
</P>
<P><FONT face=Arial size=2>Mark Nieman, PE, CEM</FONT> <BR><FONT face=Arial 
size=2>Sr. Energy Engineer</FONT> <BR><FONT face=Arial size=2>McKinstry 
Essention</FONT> <BR><FONT face=Arial size=1>Direct: (206) 832-8152</FONT> 
<BR><FONT face=Arial size=1>Cell: (206) 510-4760</FONT> <BR><FONT face=Arial 
size=1>FAX: (206) 832-8552</FONT> <BR><A 
href="http://www.mckinstry.com"><U><FONT face=Arial color=#0000ff 
size=1>http://www.mckinstry.com</FONT></U></A> <BR><I><FONT face=Arial 
size=1>"For The Life Of Your Building"</FONT></I> </P><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><pre>____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
</pre><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>