<br>There's an advanced simulation guidebook for modeling chiller curves on the Energy Design Resources website. It addresses a number of questions regarding chiller curves in DOE-2.1 and DOE-2.2, particularly for chillers having variable speed drives.
<br><br><a href="http://www.energydesignresources.com/resource/202/">http://www.energydesignresources.com/resource/202/ </a><br><br>Best Regards,<br>Gail Stranske<br><br><div><span class="gmail_quote">On 12/19/06, <b class="gmail_sendername">
Aulbach, John</b> <<a href="mailto:jaulbach@nexant.com">jaulbach@nexant.com</a>> wrote:</span><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div>
<div dir="ltr" align="left">
<div align="left">
<div align="left"><font color="#0000ff" face="Arial" size="2"><span>Folks:</span></font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2"><span></span></font> </div>
<div align="left"><font color="#0000ff" face="Arial" size="2"><span>eQuest (as did its predecessor DOE-2.1) use three basic
curves to define chiller performance:</span></font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2"><span></span></font> </div>
<div align="left"><font color="#0000ff" face="Arial" size="2"><span><strong>1) EIR-FT</strong></span></font></div>
<div align="left">
<p>Takes the U-name of a curve that adjusts the electric input
ratio as a function of the leaving chilled water temperature and the condenser
temperature. This curve should be normalized to 1.0 at the ARI point
(RATED-CHW-T, RATED-COND-T, etc.). </p>
<h5>2) EIR-FPLR</h5>
<p>Takes the U-name of a curve that adjusts the electric input
ratio as a function of</p>
<p style="margin-left: 18pt;"> <u>The
part load ratio (PLR)</u> – The PLR is defined as the ratio of the hourly
load to the hourly capacity; Load / Cap<sub>hour</sub></p>
<p style="margin-left: 18pt;"> <u>The
evaporator/condenser dT</u> - The temperature differential between the
condenser and leaving chilled-water. The meaning of the condenser
temperature varies according to condenser type. </p></div>
<div align="left">
<h5><font face="Arial"><font color="#0000ff"><span>3)
</span>CAPACITY-FT</font></font></h5>
<p><font color="#0000ff" face="Arial" size="2">Takes the U-name of a
curve that adjusts the capacity of the chiller as a function of the leaving
evaporator water temperature and the condenser temperature. This curve should be
normalized to 1.0 at the rated conditions (RATED-CHW-T, RATED-COND-T,
etc.).</font></p>
<p><span><font color="#0000ff" face="Arial" size="2">MY understanding is the the EIR-FPLR was always to be the
part load curve based on a constant condenser water entering temperature (say
85°F) and that the program would use the other two curves to modify this based
on other chilled and condenser water conditions.</font></span></p>
<p><span><font color="#0000ff" face="Arial" size="2">NOW I see a new equation (new to me) in eQuest that I
can apparently put in the ARI curve of a chiller (based on ARI prescribed
condenser water relief) and the program will accept that.</font></span></p>
<p><span><font color="#0000ff" face="Arial" size="2">Is this anyone else's
understanding?</font></span></p></div>
<div align="left"><font color="#0000ff" face="Arial" size="2"></font> </div>
<div align="left"><font color="#0000ff" face="Arial" size="2"></font> </div>
<div align="left"><font color="#0000ff" face="Arial" size="2">John R. Aulbach, PE,
CEM</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2"><em>Project
Manager</em></font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">Nexant, Inc.</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">100 North Barranca, Suite
820</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">West Covina, CA 91791
USA</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">Phone:
626-430-9054</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">Fax:
626-430-9060</font></div>
<div align="left"><font color="#0000ff" face="Arial" size="2">email: </font><a title="mailto:jaulbach@nexant.com" href="mailto:jaulbach@nexant.com" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)"><font face="Arial" size="2">
jaulbach@nexant.com</font></a></div>
<div><font color="#0000ff" face="Arial" size="2"></font> </div></div></div><pre> </pre><pre>You received this e-mail because you are subscribed <br>to the <a href="mailto:BLDG-SIM@GARD.COM" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">
BLDG-SIM@GARD.COM</a> mailing list. To unsubscribe <br>from this mailing list send a blank message to <br><a href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM" target="_blank" onclick="return top.js.OpenExtLink(window,event,this)">
BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>
</pre></div>
</blockquote></div><br>