class=728103223-31102006>Chris,</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=728103223-31102006>We ran 
into a similar question on a LEED C&S project in Seattle. We submitted a CIR 
to USGBC to allow for energy savings, after the construction, for a TI 
build-out to code. In our case, the lighting power density would, by Seattle 
code, be less than the LPD for ASHRAE code. Because the maximum LPD would 
be code-required, and because this LPD is less than the ASHRAE standard, the 
savings was allowed.  Here is the text of the CIR and subsequent 
ruling.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006></SPAN></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=728103223-31102006><STRONG>CIR 
submission:</STRONG></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006></SPAN></FONT><FONT face=Arial color=#0000ff 
size=2><SPAN class=728103223-31102006><FONT face="Times New Roman" color=#ff0000 
size=1><FONT face=Arial><FONT color=#000000><FONT size=2>We are performing 
energy modeling for <SPAN 
class=728103223-31102006>[Seattle] </SPAN>Core & Shell <SPAN 
class=728103223-31102006>...</SPAN>projects<SPAN class=728103223-31102006> 
</SPAN>according to the requirements for version 2.1 of the LEED-CS Rating 
System. Our question pertains to<SPAN class=728103223-31102006> </SPAN>future 
tenant improvements for the lighting systems.<SPAN class=728103223-31102006> 
</SPAN></FONT></FONT></FONT></FONT></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=728103223-31102006><FONT 
face="Times New Roman" color=#ff0000 size=1><FONT face=Arial><FONT 
color=#000000><FONT size=2><SPAN 
class=728103223-31102006></SPAN></FONT></FONT></FONT></FONT></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=728103223-31102006><FONT 
face="Times New Roman" color=#ff0000 size=1><FONT face=Arial><FONT 
color=#000000><FONT size=2><SPAN class=728103223-31102006></SPAN>Since it is a 
tenant improvement, the future lighting system is not currently being designed. 
However, we<SPAN class=728103223-31102006> </SPAN>propose that the lighting 
power densities in the Design Energy Cost model be set to Washington State<SPAN 
class=728103223-31102006> </SPAN>Energy Code (WSEC) maximum allowable values. 
The tenants will have to meet the WSEC for the<SPAN class=728103223-31102006> 
</SPAN>lighting design. Since these lighting levels are lower than those in 
ASHRAE 90.1-99, the building will see<SPAN class=728103223-31102006> 
</SPAN></FONT></FONT></FONT><FONT face=Arial color=#000000 size=2>additional 
energy savings over the ASHRAE code.</FONT></FONT></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=728103223-31102006><FONT 
color=#000000><SPAN class=728103223-31102006>T</SPAN>he Energy Cost Budget will 
be modeled to ASHRAE 90.1-1999 following the space-by-space method.<SPAN 
class=728103223-31102006> </SPAN>This approach will also keep from mixing and 
matching between ASHRAE and state code for the<SPAN class=728103223-31102006> 
</SPAN>baseline model.<SPAN class=728103223-31102006> 
</SPAN></FONT></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=728103223-31102006><FONT 
color=#000000><SPAN 
class=728103223-31102006></SPAN></FONT></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff><SPAN class=728103223-31102006><FONT 
color=#000000><SPAN class=728103223-31102006></SPAN><FONT size=2>We believe that 
using the WSEC for the lighting design would be a reasonable approach. If the 
lighting<SPAN class=728103223-31102006> </SPAN>design had been completed by the 
design group, the lighting levels would be less than or equal to the<SPAN 
class=728103223-31102006> </SPAN>WSEC in order to be compliant. Therefore, the 
WSEC maximum lighting power density would represent<SPAN 
class=728103223-31102006> </SPAN>the most conservative design to be installed 
after the tenant improvements are complete.<SPAN class=728103223-31102006> 
</SPAN></FONT></FONT></DIV>
<DIV>
<P align=left><FONT color=#000000><SPAN 
class=728103223-31102006></SPAN></FONT><FONT color=#000000 size=2>If our 
proposal is accepted, the following lighting power density values would be 
used:</FONT></P><B>
<P align=left><FONT face="Lucida Console" color=#000000 
size=2>Space Type <SPAN 
class=728103223-31102006>          </SPAN>ECB <SPAN 
class=728103223-31102006>       
</SPAN>DEC</FONT></P></B>
<P align=left><FONT face="Lucida Console" color=#000000 size=2>Retail <SPAN 
class=728103223-31102006>                 
</SPAN>1.9 W/sf <SPAN class=728103223-31102006>   </SPAN>1.5 
W/sf</FONT></P>
<P align=left><FONT face="Lucida Console" color=#000000 size=2>Office-open 
plan <SPAN class=728103223-31102006>       
</SPAN>1.3 W/sf <SPAN class=728103223-31102006>   </SPAN>1.0 
W/sf</FONT></P>
<P align=left><FONT face="Lucida Console" color=#000000 size=2>Main Floor 
Lobby <SPAN class=728103223-31102006>       
</SPAN>1.8 W/sf <SPAN class=728103223-31102006>   </SPAN>1.2 
W/sf</FONT></P>
<P align=left><FONT face="Lucida Console" color=#000000 size=2>Other Elevator 
Lobbies <SPAN class=728103223-31102006> </SPAN>1.8 W/sf <SPAN 
class=728103223-31102006>   </SPAN>0.8 W/sf</FONT></P><B>
<P align=left><FONT color=#000000 size=2>Draft RULING:</FONT></P></B>
<P align=left><FONT color=#000000><FONT size=2>This is acceptable. The Core and 
Shell Energy Modeling Guidelines are developed with<SPAN 
class=728103223-31102006> </SPAN>ASHRAE 90.1 as the referenced standard for both 
the Energy Cost Budget (ECB) and the Design<SPAN class=728103223-31102006> 
</SPAN>Energy Cost (DEC) to ensure a minimum standard for the lighting power 
density in spaces that<SPAN class=728103223-31102006> </SPAN>are outside of the 
control of the owner/developer. Because tenant buildout (not in the control 
of<SPAN class=728103223-31102006> </SPAN></FONT></FONT><FONT color=#000000 
size=2>the owner/developer) will be <U>required</U> by local or regional 
regulations</FONT></P>
<P align=left><FONT color=#000000 size=2><SPAN 
class=728103223-31102006>..Tom</SPAN></FONT></P>
<DIV><FONT size=2>Thomas J. White, P.E.</FONT></DIV>
<DIV><FONT size=2>Associate</FONT></DIV>
<DIV><FONT size=2>Lead Engineer, Energy Services</FONT></DIV>
<DIV><SPAN><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">LEED<SUP>(R)</SUP> Accredited 
Professional</SPAN></SPAN></SPAN></DIV>
<DIV><FONT size=2>503.345.6246  |  <A 
href="mailto:twhite@glumac.com">twhite@glumac.com</A></FONT></DIV>
<DIV><FONT size=2></FONT> </DIV>
<DIV><FONT size=2>Glumac</FONT></DIV>
<DIV><FONT size=2>320 SW Washington, Suite 200</FONT></DIV>
<DIV><FONT size=2>Portland, OR 97204-2640</FONT></DIV>
<DIV><FONT size=2>T. 503.227.5280   
F. 503.274.7674 </FONT></DIV>
<DIV><FONT size=2><A 
href="http://www.glumac.com/">http://www.glumac.com</A></FONT></DIV>
<DIV><FONT size=2></FONT> </DIV><FONT color=#000000 
size=2></FONT></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=728103223-31102006> </SPAN></FONT></DIV>
<DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
size=2>-----Original Message-----<BR><B>From:</B> BLDG-SIM@GARD.COM 
[mailto:BLDG-SIM@GARD.COM]<B>On Behalf Of </B>Chris Jones<BR><B>Sent:</B> 
Tuesday, October 31, 2006 2:41 AM<BR><B>To:</B> 
BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM] LEED Core&Shell simulation 
and lighting<BR><BR></FONT></DIV>I am a bit fuzzy on how to define the design 
and budget building lighting loads for LEED C&S.  With most core and 
shell projects, the lighting is minimal - waiting for the TI to design the 
lighting.  If that is the case with a specific C&S project, then I 
assume the lighting is not fully designed then I assume that table 11.3.1 1(c) 
applies:<BR><FONT face="Times New Roman, Times" size=2>(c) When the <I>energy 
cost budget </I>method is applied to buildings in which<BR>energy-related 
features have not yet been designed (e.g., a lighting system),<BR>those 
yet-to-be-designed features shall be described in the <I>proposed design 
</I>so<BR>that they minimally comply with applicable mandatory and 
prescriptive<BR>requirements from Sections 5 through 10. Where the space 
classification for a<BR>building is not known, the building shall be categorized 
as an office building.<BR><BR></FONT>In this case, then it would seem that there 
is no advantage to trying to design an efficient Core and Shell lighting 
design?  Any thoughts greatly appreciated.<BR><BR><BR><BR><BR><X-SIGSEP>
<P></X-SIGSEP>Chris Jones<BR>14 Oneida Avenue<BR>Toronto, ON M5J 
2E3.<BR>Tel.  416-203-7465<BR>Fax. 416-946-1005<BR><BR><PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>