size=2>Mike,</FONT></SPAN></DIV>
<DIV><SPAN class=937212818-17082006><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937212818-17082006><FONT face=Arial color=#0000ff size=2>What 
great timing you have. I was grappling with this exact issue this morning. You 
saved me some time. </FONT></SPAN></DIV>
<DIV><SPAN class=937212818-17082006><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV></DIV>
<DIV><SPAN class=937212818-17082006><FONT face=Arial><FONT size=2><FONT 
color=#0000ff>There seems to be a work around for the issue of the min CW temp 
at the chiller. <SPAN class=406454720-17082006>You say that "the chiller 
has a keyword MIN-COND-T that defualts to 70F and cannot be changed from within 
eQuest". </SPAN>I could not find how to change it within the main body of eQUEST 
either. However, it seems you CAN change it in a parametric run.<SPAN 
class=406454720-17082006> I did this and it seems to be reflected in the chiller 
condenser water temp in my hourly 
report.</SPAN></FONT></FONT></FONT></SPAN></DIV>
<DIV><FONT size=2></FONT> </DIV>
<DIV><FONT size=2>Kevin Warren, P.E., CEM, LEED AP<BR>Warren Energy Engineering, 
LLC<BR>(610) 255-3798 ph<BR>(610) 255-3406 f</FONT> </DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> BLDG-SIM@GARD.COM 
  [mailto:BLDG-SIM@GARD.COM]<B>On Behalf Of </B>Mike Tillou<BR><B>Sent:</B> 
  Thursday, August 17, 2006 1:58 PM<BR><B>To:</B> 
  BLDG-SIM@GARD.COM<BR><B>Subject:</B> [BLDG-SIM] Condenser Water Reset in 
  eQuest<BR><BR></FONT></DIV><!-- Converted from text/rtf format --><BR>
  <P><FONT face=Arial size=2>Hi all..I thought I would share a couple of tips on 
  using Condenser Water Reset Strategies in eQuest . Hopefully some of you will 
  find this useful.</FONT></P>
  <P><FONT face=Arial size=2>We just finished modeling a chiller plant where we 
  looked at using low condenser water temperatures ( below 60F ) as an energy 
  efficiency measure.  The project is in a climate with very low wetbulb 
  temperatures .  There are a couple of quirks I thought I would share 
  about trying to model a strategy like this.  </FONT></P>
  <P><FONT face=Arial size=2>The Condenser Loop Control tab has several options 
  for resetting the loop temperature.  If you notice MIN-RESET-T always 
  defaults to 70F. </FONT></P>
  <P><FONT face=Arial size=2>Issue  #1:  If you reset the Condenser 
  loop MIN-RESET-T lower than 70F (say 65F) and then run an hourly report to 
  check the loop temperature everything looks like it's working fine.  
  BUT..if you also check the chiller entering condenser temperature you will 
  find it never goes below 70F even though the condenser loop says it should be 
  lower.  This is because the chiller has a keyword MIN-COND-T that 
  defualts to 70F and cannot be changed from within eQuest.  You have to 
  change the keyword manually in the input file by adding the line, MIN-COND-T = 
  65 underneath the definition of your chiller.</FONT></P>
  <P><FONT face=Arial size=2>  </FONT><BR><FONT face=Arial size=2>The most 
  likely reason this defaults to 70F is because the default chiller performance 
  curves were not designed for condenser temperatures below 70F  ( someone 
  should correct me if this is wrong)  </FONT></P>
  <P><FONT face=Arial size=2>If you want to try and model condenser water 
  temperatures below 70F I highly recommend you create custom performance curves 
  that include data points that describe the operation of your chiller at the 
  appropriate condenser water conditions.</FONT></P>
  <P><FONT face=Arial size=2>That brings me to Issue #2.</FONT> </P>
  <P><FONT face=Arial size=2>The MIN-COND-T keyword has a lower limit of 
  60F.  In other words even if you create the appropriate performance 
  curves  and then try to set MIN-COND-T lower than 60F you will get a 
  simulation error.  </FONT></P>
  <P><FONT face=Arial size=2>You can work around this by using the DIAGNOSTIC 
  keyword "NO-LIMITS".  In effect this turns off both the Max and Min 
  keyword limits.  You can then simulate chiller operation with very low 
  condesner water temperatures.  </FONT></P>
  <P><FONT face=Arial size=2>If you use the "NO-LIMITS" keyword do so very 
  carefully.  This is a very important error checking function of DOE2.2 
  eQuest.</FONT></P>
  <P><B><FONT face=Arial size=2>Mike </FONT></B></P><BR>
  <P><B><FONT face=Arial size=2>Michael Tillou, PE<BR>etc Group, Inc.<BR>PO Box 
  7, Williamstown, MA 01267<BR>ph. (413) 458-9870 fx. (413) 
  458-9875<BR></FONT><BR></B></P><BR>
  <P><FONT face="Times New Roman"></FONT> </P><BR><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>