<P><FONT size=2>Dan,<BR>Not sure if this is relevant, but have you factored in 
the reheat load associated with dehumidifying using a cooling coil? That might 
be where your getting the additional load. Also - if you are cooling sensibly 
separately, you might want to dehumidify using a liquid desiccant system. This 
could end up saving you a lot.<BR><BR><BR><!-- Converted from text/rtf format --></P>
<P><B><FONT face=Garamond color=#000000>Vikram Sami,</FONT></B> <FONT 
face=Garamond color=#000000>LEED AP</FONT><B></B> <BR><FONT face=Garamond 
color=#000000>Direct Phone 404-253-1466 | Direct Fax 404-253-1366</FONT> </P>
<P><B><FONT face=Garamond color=#800000>L</FONT><FONT face=Garamond 
color=#800000 size=2>ORD</FONT><FONT face=Garamond color=#800000>, A</FONT><FONT 
face=Garamond color=#800000 size=2>ECK</FONT><FONT face=Garamond color=#800000> 
& S</FONT><FONT face=Garamond color=#800000 size=2>ARGENT</FONT><FONT 
face=Garamond color=#800000> A</FONT><FONT face=Garamond color=#800000 
size=2>RCHITECTURE</FONT><BR></B><FONT face=Garamond size=2>Responsive 
Design</FONT> <FONT face=Symbol size=1>·<FONT face="Courier New"></FONT></FONT> 
<FONT face=Garamond size=2>Technological Expertise</FONT> <FONT face=Symbol 
size=1>·<FONT face="Courier New"></FONT></FONT> <FONT face=Garamond 
size=2>Exceptional Service</FONT> <BR><FONT face=Garamond 
color=#000000>www.lordaecksargent.com</FONT> </P>
<P><FONT face=Arial color=#0000ff></FONT><BR>-----Original Message-----<BR>From: 
bldg-sim@gard.com [<A 
href="mailto:bldg-sim@gard.com">mailto:bldg-sim@gard.com</A>] On Behalf Of Dan 
Johnson<BR>Sent: Monday, August 07, 2006 5:21 PM<BR>To: 
bldg-sim@gard.com<BR>Subject: [bldg-sim] People load: BTUs vs 
moisture<BR><BR>Hi,<BR>I'm designing an expensive residential dining room in 
Shanghai that will be dehumidified using the required outside air through a 
chilled-water coil and the room's sensible loads will be met using radiant 
cooling from an exposed, chilled slab.<BR><BR>When I calculate the 
cooling/dehumidifying load based on moisture output per person (using 0.235 
lb/hr/person), I come up with a cooling capacity that is 245% of what I need if 
I size the system to meet the heat output per person (250 latent + 250 
sensible).<BR><BR>Why do the two approaches yield such different system 
sizes?  (Or:<BR>why<BR>do the BTU/hr/person numbers not correspond to the 
pounds-of-moisture/hr/person numbers?)<BR><BR>Is my moisture load (0.235 
lb/hr/person) a good assumption for sedentary dining in comfortable 
conditions?<BR><BR>Does ASHRAE Fundamentals list a table of moisture 
output/person in different conditions?<BR><BR>Thanks in advance.<BR><BR>--Dan 
Johnson<BR><BR>Berkeley 
CA<BR><BR><BR><BR>__________________________________________________<BR>Do You 
Yahoo!?<BR>Tired of spam?  Yahoo! Mail has the best spam protection around 
<A 
href="http://mail.yahoo.com">http://mail.yahoo.com</A><BR><BR>======================================================<BR>You 
received this e-mail because you are subscribed to the BLDG-SIM@GARD.COM mailing 
list.  To unsubscribe from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM<BR><BR></FONT></P><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>