<DIV><SPAN class=937325917-26072006><FONT size=2>Hello,</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>I am having trouble 
understanding the behaviour of an air source heat pump in DOE2.1E and would 
appreciate any helpful insights. The system has ample supplementary electric 
resistance heating capacity, but is still unable to maintain heating sepoint 
conditions during cold spells (typically starting just above the freezing mark) 
in the early morning occupied periods (yes, there is a thermostat setback). I 
have created hourly reports (all in SYSTEMS), which show:</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>1. System variable 78 (total 
heating capacity) is always large - in this particular case, about 200,000 
Btu/h</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>2. System variable 43 (adjusted 
capacity of heat pump in this hour) changes moderately with changes in outdoor 
air dry bulb - about 40,000 Btu/h when OA temp=32F</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>3. System variable 166 (output 
of unit) is the same as variable 43 sometimes, typically when OA temp is about 
36 or 37F - if OA temps are lower, variable 166 values are much lower than 
variable 43 (down to about 26,000 Btu/h)</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>4. System variable 5 (total 
central coil heating energy input) typically matches variable 166 in more 
moderate OA temps, but greatly exceeds this variable when OA temps are lower 
than about 38F (reaching a peak of about 75,000 Btu/h)</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>5. Zone variable 48 
(supplemental heat load for zone's heat pump this hour) is always 
zero.</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>Some questions that come to 
mind:</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>1. Does the adjusted capacity 
of the heat pump (var. 43) not include the effect of the defrost cycle? Is this 
why the output of the unit (var. 166) is lower?</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>2. What does variable 5 
represent? Does it include supplemental electric resistance heating? Defrost 
energy? (in this case, defrost type is resistive, the 
default)</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>3. Can zone variable 48 be 
trusted? Is supplemental heat being delivered? If not, why?</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>For completeness, some 
pertinent system inputs are shown below.</FONT></SPAN></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2></FONT></SPAN> </DIV>
<DIV><FONT 
size=2> MAX-SUPPLY-T          
=  
110<BR> HEAT-SOURCE           
=  HEAT-PUMP<BR> HEATING-CAPACITY      
=  
-54589<BR> HEAT-SET-T            
=  
110<BR> HEATING-EIR           
=  0.2762<BR> HP-SUPP-SOURCE        
=  
ELECTRIC<BR> HEAT-CAP-FT           
=  
SDL-C52<BR> HEAT-EIR-FT           
=  
SDL-C57<BR> HEAT-EIR-FPLR         
=  
SDL-C62<BR> MAX-HP-SUPP-T         
=  40<BR> HP-SUPP-HT-CAP        
=  
-170650<BR> MIN-HP-T              
=  
23<BR> DEFROST-T             
=  35<BR></FONT></DIV>
<DIV><SPAN class=937325917-26072006><FONT size=2>I have tried increasing the 
airflow, but the number of underheated hours increased. Increasing supplemental 
capacity has no effect. My apologies for the length of this 
email.</FONT></SPAN></DIV>
<DIV><FONT size=2> </DIV></FONT>
<DIV align=left><FONT size=2>
<DIV align=left><SPAN class=005282818-24052006><SPAN lang=en-us><FONT 
face=Arial>Stantec's North <SPAN class=453122720-24052006>Vancouver</SPAN> 
office relocates as of May 29, 2006, please note the new address, telephone 
and fax. The email address remains the same<SPAN 
class=453122720-24052006>:</SPAN></FONT></SPAN></SPAN></DIV>
<DIV><SPAN class=005282818-24052006><SPAN lang=en-us><FONT size=+0><FONT 
size=+0><SPAN class=453122720-24052006><FONT face=Arial><FONT 
size=2></FONT></FONT></SPAN></FONT></FONT></SPAN></SPAN> </DIV>
<DIV><SPAN class=005282818-24052006><SPAN lang=en-us><SPAN 
class=453122720-24052006><FONT color=#0000ff><FONT face=Arial><STRONG><FONT 
color=#000000>Derek Whitehead</FONT></STRONG><BR><SPAN 
class=453122720-24052006></SPAN><FONT color=#000000>Sustainable Building 
Analyst</FONT><BR></FONT><FONT face=Arial><FONT color=#000000>Stantec <SPAN 
class=453122720-24052006>Consulting Ltd.</SPAN><BR>1100 - 111 Dunsmuir Street 
<BR>Vancouver, BC, V6B 6A3 <BR>Ph: <SPAN 
class=453122720-24052006>604-696-8383</SPAN></FONT></FONT></FONT></SPAN></SPAN></SPAN></DIV>
<DIV><SPAN class=005282818-24052006><SPAN lang=en-us><SPAN 
class=453122720-24052006><FONT color=#0000ff><FONT face=Arial><FONT 
color=#000000><SPAN class=453122720-24052006></SPAN>Fx: 
604-696-8100</FONT> <BR><SPAN class=453122720-24052006><A 
href="mailto:dewhitehead@stantec.com">dewhitehead@stantec.com</A></SPAN></FONT></FONT><BR><A 
title=http://www.stantec.com/ href="blocked::http://www.stantec.com"><FONT 
face=Arial>www.stantec.com</FONT></A><FONT face=Arial color=#0000ff> 
</FONT></SPAN></SPAN></SPAN></DIV></FONT></DIV>
<DIV> </DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>