<DIV><FONT face=Arial size=2><SPAN class=865104716-07072006>I would appreciate 
any clarifications that can be shared on the underlined sentences in these 
two excerpts from Appendix G of ASHRAE 90.1-2004.  They seem 
contradictory so I must be missing the author's intent.</SPAN></FONT></DIV>
<DIV><FONT face=Arial><FONT face=TT12B7o00>
<P align=left><FONT size=2>G3.1.2.8 </FONT></FONT><FONT size=2><B><FONT 
face="Times New Roman">Design Air Flow Rates. </FONT></B><U><FONT 
face="Times New Roman">System design supply<SPAN class=865104716-07072006> 
</SPAN></FONT><FONT face="Times New Roman">air flow rates for the <I>baseline 
building design </I>shall be based<SPAN class=865104716-07072006> 
</SPAN></FONT></U><FONT face="Times New Roman"><U>on a supply-air-to-room-air 
temperature difference of 20°F</U>. If<SPAN class=865104716-07072006> 
</SPAN></FONT><FONT face="Times New Roman">return or relief fans are specified 
in the <I>proposed design</I>, the<SPAN class=865104716-07072006> 
</SPAN><I>baseline building design </I>shall also be modeled with fans 
serving<SPAN class=865104716-07072006> </SPAN>the same functions and sized for 
the <I>baseline </I>system supply<SPAN class=865104716-07072006> </SPAN>fan air 
quantity less the minimum <I>outdoor air</I>, or 90% of<SPAN 
class=865104716-07072006> </SPAN></FONT></FONT><FONT face="Times New Roman" 
size=2>the supply fan air quantity, whichever is larger.</FONT></P>
<P align=left><FONT face="Times New Roman"><FONT size=2>G3.1.3.12 <B>Supply Air 
Temperature Reset (Systems 5<SPAN class=865104716-07072006> </SPAN>through 8). 
</B>Supply air temperature shall be reset based on<SPAN 
class=865104716-07072006> </SPAN>zone demand from the design temperature 
difference to a<SPAN class=865104716-07072006> </SPAN>10°F temperature 
difference under minimum load conditions.<SPAN class=865104716-07072006> 
</SPAN><U>Design air flow rates shall be sized for the reset supply air<SPAN 
class=865104716-07072006> </SPAN></U></FONT></FONT><FONT face="Times New Roman" 
size=2><U>temperature, i.e., a 10°F temperature difference.</U></FONT></P>
<P align=left><SPAN class=865104716-07072006><FONT size=2>Thank 
you,</FONT></SPAN></P></FONT></DIV>
<DIV><SPAN class=141333114-30122005><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-family: 'Times New Roman'">Paul 
<SPAN class=SpellE>Riemer</SPAN><BR></SPAN><SPAN 
style="FONT-FAMILY: 'BankGothic Md BT'">THE WEIDT GROUP</SPAN><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-bidi-font-family: 'Times New Roman'"><BR>952.938.1588<BR><A 
title=mailto:PaulR@twgi.com 
href="mailto:PaulR@twgi.com">PaulR@twgi.com</A><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></DIV></SPAN>
<DIV> </DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>