<DIV>Gerald, <BR><BR>I am not sure I understand your question, but I will take a 
shot at answering. Appendix G is different from the body of the standard. 
Chapter 5 prescribes maximum fenestration areas as a % of gross wall area which 
includes below grade walls. Appendix G, in describing the hypothetical baseline 
building prescribes a maximum fenestration area as a percentage of above grade 
wall area. These two sections are clearly different.</DIV>
<DIV> </DIV>
<DIV>Mike</DIV>
<DIV> </DIV>
<DIV>Michael Rosenberg<BR>Oregon Department of Energy<BR>625 Marion St. 
N.E.<BR>Salem, OR 97301-3742<BR>Phone : (503) 373-7809<BR>Fax: (503) 
373-7806<BR><BR>>>> Gerald Pde <GERALDPDE@YAHOO.COM>04/25/06 02:51PM 
>>> <BR>Michael, <BR>Appendix-g states that use 40% glazing if glazing 
% is <BR>above 40%, otherwise use whatever is smaller. From all <BR>the 
discussions regarding this above-grade/below-grade <BR>issue, we now learn that, 
as an update to the code, <BR>below grade walls(if the adjecent space is 
<BR>conditioned) are now included in the WWR calculations. <BR>Appendix-g should 
not change anything apart from the <BR>fact that glazing will need to be equally 
distributed <BR>through-out the above-grade facade, am I correct? 
<BR><BR><BR>Gerald <BR><BR>--- Michael Rosenberg 
<MICHAEL.ROSENBERG@STATE.OR.US><BR>wrote: <BR><BR>> Since many of you readers 
are using Appendix G of <BR>> Standard 90.1 for modeling LEED rated buildings 
you <BR>> should be aware that Table G.3.1.5 states in the <BR>> 
description of the baseline building for WWR; <BR>> <BR>> " Vertical 
fenestration areas for new buildings and <BR>> additions shall equal that in 
the proposed design or <BR>> 40% of gross above grade wall area, whichever is 
<BR>> smaller, and shall be distributed uniformly in <BR>> horizontal 
bands across the four orientations." <BR>> <BR>> As for the last part of 
that requirement, <BR>> distributing fenestration uniformly in horizontal 
<BR>> bands across the four orientations, that has been <BR>> removed in 
Addendum A to the 2004 Standard, but will <BR>> not be updated in the 
published version until 2007. <BR>> <BR>> Mike <BR>> <BR>> <BR>> 
<BR>> Michael Rosenberg <BR>> Oregon Department of Energy <BR>> 625 
Marion St. N.E. <BR>> Salem, OR 97301-3742 <BR>> Phone : (503) 373-7809 
<BR>> Fax: (503) 373-7806 <BR>> <BR>> >>> "Larry Degelman" 
<LDEGELMAN@COX.NET>04/24/06 <BR>> 05:07PM >>> <BR>> Possibly the 
interpretation of what is gross wall <BR>> area depends on what <BR>> 
version of 90.1 you are looking at. As for <BR>> 90.1-2004, the official 
<BR>> interpretation on the ASHRAE web site leaves no <BR>> doubt that 
"gross wall area" <BR>> include both above- and below-ground walls. See the 
<BR>> following item verbatim <BR>> from the ASHRAE web site. <BR>> 
<BR>> <BR>> <BR>> INTERPRETATION IC 90.1-2004-1 OF ANSI/ASHRAE/IESNA 
<BR>> STANDARD 90.1-2004 <BR>> <BR>> Energy Standard for Buildings 
Except Low-Rise <BR>> Residential Buildings <BR>> <BR>> <BR>> 
<BR>> <BR>> <BR>> Date Approved June 25, 2005 <BR>> <BR>> 
<BR>> <BR>> Request from: Roger Chang (E-mail: <BR>> <U><A 
href="mailto:roger.chang@arup.com">roger.chang@arup.com</A></U> ), Associate 
Member, <BR>> 155 Avenue of the Americas, New York, NY 10013. <BR>> 
<BR>> <BR>> <BR>> Reference: This request for interpretation refers 
<BR>> to the requirements <BR>> presented in ANSI/ASHRAE/IESNA Standard 
90.1-2004, <BR>> Section 5.2.1 Compliance, <BR>> relating to gross wall 
area. <BR>> <BR>> <BR>> <BR>> Background: Standard 90.1-2004 does 
not appear to be <BR>> clear as to what gross <BR>> wall area means. 
International Energy Conservation <BR>> Code is clear that <BR>> 
prescriptive requirements are based on window to <BR>> above-grade wall area. 
This <BR>> impacts all sections of the code where the <BR>> window-to- 
wall area ratio is <BR>> taken into consideration. <BR>> <BR>> <BR>> 
<BR>> <BR>> <BR>> Interpretation: Gross wall area refers to <BR>> 
above-grade wall only. <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> 
Question: Is this interpretation correct? <BR>> <BR>> <BR>> <BR>> 
<BR>> <BR>> Answer: No. <BR>> <BR>> <BR>> <BR>> <BR>> 
<BR>> Comments: <BR>> <BR>> <BR>> <BR>> Section 3.2 defines 
"building envelope" to include <BR>> "the elements of a <BR>> 
building*that enclose...spaces through which thermal <BR>> energy may be 
<BR>> transferred to or from the exterior". <BR>> <BR>> <BR>> 
<BR>> Section 3.2, in the definition of "wall" states <BR>> "this includes 
above- and <BR>> below-grade walls, between floor spandrels, <BR>> 
peripheral edges of floors, and <BR>> foundation walls". <BR>> <BR>> 
<BR>> <BR>> Section 3.2 defines "gross wall area" as "the area <BR>> of 
the wall measured on <BR>> the exterior face from the top of the floor to the 
<BR>> bottom of the roof". <BR>> <BR>> <BR>> <BR>> Therefore, for 
buildings with conditioned space <BR>> below-grade, the gross wall <BR>> 
area extends from the top of the surface of the <BR>> floor of the lowest 
<BR>> conditioned space to the bottom of the roof of the <BR>> highest 
conditioned <BR>> space. <BR>> <BR>> <BR>> <BR>> (Note that the 
use of a similar term in a document <BR>> from another organization <BR>> 
is irrelevant to an interpretation of Standard <BR>> 90.1.) <BR>> <BR>> 
<BR>> <BR>> Page 1 of 1 <BR>> �2005 ASHRAE. All Rights reserved. 
<BR>> <BR>> <BR>> <BR>> <BR>> <BR>> 
===================================== <BR>> <BR>> Larry O. Degelman, P.E. 
<BR>> <U><A href="mailto:ldegelman@cox.net">ldegelman@cox.net</A></U> 
<BR>> <BR>> Prof. Emeritus of Architecture Ph./Fax: <BR>> 
1-979-696-2506 <BR>> <BR>> Texas A&M University <BR>> <BR>> 
===================================== <BR>> <BR>> <BR>> <BR>> 
-----Original Message----- <BR>> From: <U><A 
href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A></U> [<U> <A 
href="mailto:BLDG-SIM@gard.com]">mailto:BLDG-SIM@gard.com]</A></U> <BR>> On 
Behalf Of Jon McHugh <BR>> Sent: Sunday, April 23, 2006 8:40 PM <BR>> To: 
<U><A href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A></U> <BR>> 
Subject: [BLDG-SIM] WWR definition <BR>> <BR>> <BR>> <BR>> Rene, 
Larry and Gerald, <BR>> <BR>> <BR>> <BR>> I think that the the 
underground wall area should be <BR>> included for each floor <BR>> that 
has windows. These windows in partially below <BR>> ground stories are 
<BR>> providing light and views that are no less important <BR>> than 
similar functions <BR>> provided on upper floors. However, if I have a 
<BR>> skyscraper with 4 stories of <BR>> underground garage of basement 
areas, I don't think <BR>> these fully underground <BR>> wall areas should 
be included. Rene, in evaluating <BR>> the energy and cost <BR>> impacts 
of windows in buildings, it is important to <BR>> look at the potential 
<BR>> for daylighting or the value of view, otherwise an <BR>> engineering 
analysis <BR>> might conclude that we don't need any windows at <BR>> all. 
<BR>> <BR>> <BR>> <BR>> Perhaps this should be brought up with the 
90.1 <BR>> envelope committee. <BR>> <BR>> <BR>> <BR>> Sincerely, 
<BR>> <BR>> <BR>> <BR>> Jon McHugh, PE, LC <BR>> Technical 
Director <BR>> Heschong Mahone Group Inc. <BR>> 11626 Fair Oaks Blvd #302 
<BR>> Fair Oaks, CA 95628 (Sacramento) <BR>> (916)962-7001 ext 38 <BR>> 
(916)962-0101 FAX <BR>> e-mail: <U><A 
href="mailto:mchugh@h-m-g.com">mchugh@h-m-g.com</A></U> <BR>> URL: <U><A 
href="http://www.h-m-g.com/">www.h-m-g.com</A></U> <BR>> <BR>> <BR>> 
<BR>> _____ <BR>> <BR>> From: <U><A 
href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> [<U> <A 
href="mailto:BLDG-SIM@GARD.COM]">mailto:BLDG-SIM@GARD.COM]</A></U> <BR>> On 
Behalf Of Renee J. <BR>> Azerbegi <BR>> Sent: Sunday, April 23, 2006 11:11 
AM <BR>> To: <U><A href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> 
<BR>> Subject: [BLDG-SIM] WWR definition <BR>> <BR>> It depends on the 
code in use. <BR>> <BR>> <BR>> <BR>> I submitted an official request 
(CM proposal) to the <BR>> ASHRAE 90.1 Envelope <BR>> committee to change 
the definition to only include <BR>> the above grade walls but <BR>> they 
declined it so it is still the above and below <BR>> grade walls. The reason 
<BR>> I sent the request is that architects tend to add <BR>> more glazing 
to the above <BR>> grade walls because they can include the below grade 
<BR>> walls in the <BR>> definition. I showed some modeling results of the 
<BR>> difference between a two <BR>> story building with one above and 
below grade wall <BR>> in a few difference <BR>> cities in the US and 
there was a significant energy <BR>> impact. <BR>> <BR>> <BR>> 
<BR>> However, I believe the IECC includes only the above <BR>> grade 
walls. <BR>> <BR>> <BR>> <BR>> Ren�e <BR>> <BR>> <BR>> 
<BR>> <BR>> <BR>> Ren�e Azerbegi, CEM, LEED-AP <BR>> <BR>> 
President/Sustainable Design Engineer <BR>> <BR>> ambient energy * solar 
& sustainable design <BR>> solutions <BR>> <BR>> t 303.278.1532 | f 
303.278.8533 | c 303.885.2695 <BR>> <BR>> <U><A 
href="mailto:renee@ambient-e.com">renee@ambient-e.com</A></U> <BR>> <BR>> 
ambient-e.com <BR>> <BR>> _____ <BR>> <BR>> From: <U><A 
href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> [<U> <A 
href="mailto:BLDG-SIM@GARD.COM]">mailto:BLDG-SIM@GARD.COM]</A></U> <BR>> On 
Behalf Of Larry <BR>> Degelman <BR>> Sent: Sunday, April 23, 2006 10:26 AM 
<BR>> To: <U><A href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> 
<BR>> Subject: [BLDG-SIM] <BR>> <BR>> <BR>> <BR>> Gerald et al, 
<BR>> <BR>> <BR>> <BR>> The conventional definition of 
window-wall-ratio is <BR>> the window area divided <BR>> by the "gross" 
wall area, though the term <BR>> "window-wall-ratio" is no longer <BR>> 
among the Definitions section of 90.1-2004. For <BR>> that matter, WWR is not 
<BR>> defined in the Abbreviations section. <BR>> <BR>> <BR>> 
<BR>> Notwithstanding all that, the definition for "Gross <BR>> Wall Area" 
is clearly <BR>> defined in the 90.1-2004 User's Manual. <BR>> <BR>> 
<BR>> <BR>> On page 5-30, example 5-G addresses "Determining <BR>> 
Gross Wall Area", stating <BR>> that this is very significant since the 
window area <BR>> requirements are based <BR>> on Window-Wall-Ratio (WWR). 
<BR>> <BR>> <BR>> <BR>> Answer (as shown on the same page): "The 
gross wall <BR>> area includes both <BR>> above-grade walls and 
below-grade walls so that <BR>> gross wall area is simply <BR>> the 
perimeter of the building * times the height*" <BR>> <BR>> <BR>> 
<BR>> Larry D. <BR>> <BR>> ===================================== 
<BR>> <BR>> Larry O. Degelman, P.E. <BR>> <U><A 
href="mailto:ldegelman@cox.net">ldegelman@cox.net</A></U> <BR>> <BR>> 
Prof. Emeritus of Architecture Ph./Fax: <BR>> 1-979-696-2506 <BR>> 
<BR>> Texas A&M University <BR>> <BR>> 
===================================== <BR>> <BR>> <BR>> <BR>> 
-----Original Message----- <BR>> <BR>> From: <U><A 
href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A></U> <BR>> <BR>> To: 
<U><A href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A></U> <BR>> 
<BR>> Sent: Fri Apr 21 09:06:56 2006 <BR>> <BR>> Subject: [BLDG-SIM] 
ASHRAE 90.1 window-wall ratio <BR>> <BR>> <BR>> <BR>> I recently 
came across a paper from "Building Energy <BR>> <BR>> Codes Program" 
called "Setting the Standard" and <BR>> lists <BR>> <BR>> out various 
new code updates. It seems that <BR>> currently <BR>> <BR>> we are 
allowed to count below-grade walls as part of <BR>> <BR>> the window-wall 
ratio calculations. Does anyone <BR>> have <BR>> <BR>> an update on 
this or point me to the right resource <BR>> to <BR>> <BR>> confirm 
this information? <BR>> <BR>> <BR>> <BR>> Thanks. <BR>> <BR>> 
Gerald <BR>> <BR>> <BR>> <BR>> 
__________________________________________________ <BR>> <BR>> Do You 
Yahoo!? <BR>> <BR>> Tired of spam? Yahoo! Mail has the best spam <BR>> 
protection around <BR>> <BR>> <U><A 
href="http://mail.yahoo.com/">http://mail.yahoo.com</A></U> <HTTP: 
mail.yahoo.com /><BR>> <BR>> <BR>> <BR>> 
<BR>====================================================== <BR>> <BR>> 
<BR>> <BR>> <BR>> <BR>> 
<BR>=====================================================You <BR>> received 
this e-mail because you are subscribed <BR>> to the <U><A 
href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> mailing list. To 
<BR>> unsubscribe <BR>> from this mailing list send a blank message to 
<BR>> <U><A 
href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A></U> 
<BR>> <BR>> <BR>=====================================================You 
<BR>> received this e-mail because you are subscribed <BR>> to the <U><A 
href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> mailing list. To 
<BR>> unsubscribe <BR>> from this mailing list send a blank message to 
<BR>> <U><A 
href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A></U> 
<BR>> <BR>> <BR><BR><BR>__________________________________________________ 
<BR>Do You Yahoo!? <BR>Tired of spam? Yahoo! Mail has the best spam protection 
around <BR><U><A href="http://mail.yahoo.com/">http://mail.yahoo.com</A></U> 
<BR><BR>====================================================== <BR>You received 
this e-mail because you are subscribed <BR>to the <U><A 
href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</A></U> mailing list. To 
unsubscribe <BR>from this mailing list send a blank message to <BR><U><A 
href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</A></U> 
<BR><BR></DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>