color=#0000ff size=2>Vikram,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=926370100-24012006><FONT face=Arial
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=926370100-24012006><FONT face=Arial><FONT
color=#0000ff><FONT size=2>If your base system<SPAN class=488580100-24012006>
already is dehumidifying enough to bring the space down to 50% RH under normal
operation then you would not expect to see any additional energy requirement.
Depending on your OA fraction in Atlanta you may not need any additional
dehumidification than what you get with your base DX system. Have you checked
the RH reports from your base model to determine if the base design is floating
up over 50% RH?</SPAN></FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=926370100-24012006><FONT face=Arial><FONT
color=#0000ff><FONT size=2><SPAN
class=488580100-24012006></SPAN></FONT></FONT></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=926370100-24012006><FONT face=Arial><FONT
color=#0000ff><FONT size=2><SPAN class=488580100-24012006>
<DIV align=left>
<DIV align=left><FONT face=Arial size=2>Peter Alspach, P.E.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Senior Mechanical Engineer</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Arup</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>901 Market Street, Suite
260</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>San Francisco, CA 94103</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>T: 415.957.9445</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>D: 415.946.0607</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>F: 415.957.9096</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>E:
peter.alspach@arup.com</FONT></DIV></DIV></SPAN></FONT></FONT></FONT></SPAN></DIV></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com
[mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Vikram Sami<BR><B>Sent:</B>
Monday, January 23, 2006 3:11 PM<BR><B>To:</B>
bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Humidity control in
eQUEST<BR></FONT><BR></DIV>
<DIV></DIV><!-- Converted from text/rtf format -->
<P><FONT face=Arial size=2>I am trying to model a humidistat in eQUEST using a
packaged single zone system (for a project in Atlanta), and for some reason, it
doesn’t seem to be adding energy for reducing max humidity from 100% to 50%. The
result is that there is a cooling penalty for using a liquid desiccant
dehumidifier. My question is:</FONT></P>
<P><FONT face=Arial size=2>A) Is it possible to have humidity controls for a PSZ
system type? If so - how do I do it?</FONT> <BR><FONT face=Arial size=2>B) If
not - what system type should I use, and how do I get it to dehumidify?</FONT>
</P>
<P><FONT face=Arial size=2>Thanks in advance.</FONT> </P>
<P><B><FONT face=Garamond>Vikram Sami,</FONT></B><FONT face=Garamond> LEED
AP</FONT><FONT face=Arial><BR></FONT><FONT face=Garamond>Direct Phone
404-253-1466 | Direct Fax 404-253-1366</FONT><FONT face=Arial> </FONT></P>
<P><B><FONT face=Garamond color=#800000>L</FONT><FONT face=Garamond
color=#800000 size=2>ORD</FONT><FONT face=Garamond color=#800000>, A</FONT><FONT
face=Garamond color=#800000 size=2>ECK</FONT><FONT face=Garamond color=#800000>
& S</FONT><FONT face=Garamond color=#800000 size=2>ARGENT</FONT><FONT
face=Garamond color=#800000> A</FONT><FONT face=Garamond color=#800000
size=2>RCHITECTURE</FONT><BR></B><FONT face=Garamond size=2>Responsive
Design</FONT><FONT face=Arial></FONT> <FONT face=Symbol size=1>·</FONT><FONT
face=Arial></FONT> <FONT face=Garamond size=2>Technological
Expertise</FONT><FONT face=Arial></FONT> <FONT face=Symbol size=1>·</FONT><FONT
face=Arial></FONT> <FONT face=Garamond size=2>Exceptional Service</FONT><FONT
face=Arial><BR></FONT><A href="file://www.lordaecksargent.com"><U></U><U><FONT
face=Garamond color=#0000ff>www.lordaecksargent.com</FONT></U></A><FONT
face=Arial> </FONT></P><BR><PRE>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE><pre>____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
</pre></BODY></HTML>