<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff size=2>Make 
two separate chillers, and have them scheduled for availability such that the 
one with the performance curves for ice is available during your ice-build 
times, and the "standard" performance machine is available during other 
times.</FONT></SPAN></DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff size=2>I 
haven't looked at an ice-building performance curve yet, but even if the curves 
are similar, the EIR and capacity for the two cases will be 
different.</FONT></SPAN></DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff size=2>Hope 
this helps!</FONT></SPAN></DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial color=#0000ff 
size=2>David</FONT></SPAN></DIV>
<DIV><SPAN class=586481515-05122005><FONT face=Arial size=2></FONT> </DIV>
<DIV>
<DIV align=left><FONT face=Arial 
size=2>--------------------------------------------------------------</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>David S. Eldridge, Jr.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Project Engineer</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>LEED v2.0 Accredited 
Professional</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Grumman/Butkus Associates</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>820 Davis St., Suite 300</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Evanston, IL  60201</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>847.328.3555  ext. 224</FONT></DIV>
<DIV align=left><FONT face=Arial size=2><A 
href="mailto:dse@grummanbutkus.com">dse@grummanbutkus.com</A></FONT></DIV>
<DIV align=left><FONT face=Arial 
size=2>-------------------------------------------------------------</FONT></DIV></SPAN></DIV><BR>
<BLOCKQUOTE 
style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #0000ff 2px solid; MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
  <HR tabIndex=-1>
  <FONT face=Tahoma size=2><B>From:</B> bldg-sim@gard.com 
  [mailto:bldg-sim@gard.com] <B>On Behalf Of </B>Gang Wu<BR><B>Sent:</B> Sunday, 
  December 04, 2005 8:33 PM<BR><B>To:</B> bldg-sim@gard.com<BR><B>Subject:</B> 
  [bldg-sim] Simulation of Ice Storage in Equest<BR></FONT><BR></DIV>
  <DIV></DIV>
  <DIV id=RTEContent>Hi folks,<BR>   <BR>  I am simulating a 
  partial ice-storage system using Equest. One of the <BR>chillers in the plant 
  has to operate under low temperature to make ice <BR>during off-peak hours, 
  while during on-peak hours it runs under high <BR>temperature to supply 
  chilled water to coils. To my knowledge it shoulf <BR>be a dual-condition 
  chiller, screw or centrifugal type. <BR>   <BR>  I am wondering 
  how I can model this dual-condition chiller in Equest. <BR>Can one performance 
  curve represent the chiller's performance of making <BR>both ice and chilled 
  water?  If my understanding is correct, each <BR>chiller in Equest can 
  only be assigned with one performance curve.<BR>   <BR>  I 
  highly appreciate if any expert provide some successful examples of <BR>both 
  ice-storage simulation and that dual-condition chiller curve.<BR>   
  <BR>  Best,<BR>  Glenn Wu</DIV>
  <P>
  <HR SIZE=1>
  <B>Yahoo! Personals</B><BR>Skip the bars and set-ups and <A 
  href="http://us.rd.yahoo.com/evt=36107/*http://personals.yahoo.com/us/reg/free7days ">start 
  using Yahoo! Personals for free</A></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>