<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff 
size=2>G,</FONT></SPAN></DIV>
<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff size=2>I have 
tried both with and w/o the night cycle cooling controls (for all 4 types, i.e 
stay-off, cycle on any, etc) before posting this question. But it didn't 
work. One good suggestion is to create a schedule 
to simulate natural ventilation. I am going to try that idea. Thank you for 
the hints. I appreciate it.   </FONT></SPAN></DIV>
<DIV><SPAN class=286082919-15112005></SPAN> </DIV>
<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff size=2>Albert 
Sitorus. </FONT></SPAN></DIV>
<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=286082919-15112005><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=286082919-15112005> </SPAN><FONT face=Tahoma></DIV>
<DIV><FONT size=2><SPAN class=286082919-15112005> </SPAN>-----Original 
Message-----<BR><B>From:</B> Graham & Megan 
[mailto:hamnmegs@ozemail.com.au]<BR><B>Sent:</B> Tuesday, November 15, 2005 
11:06 AM<BR><B>To:</B> bldg-sim@gard.com<BR><B>Subject:</B> [bldg-sim] Out of 
Throttle Range.<BR><BR></DIV></FONT></FONT>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV><FONT face=Arial size=2>Also run with and without the night cycle cooling 
  controls.  Equest includes any night ventilative cooling hours as run 
  hours and thus is likely biasing your hours under-cooled ...</FONT></DIV>
  <DIV><FONT face=Arial size=2>G</FONT></DIV>
  <DIV>----- Original Message ----- </DIV>
  <BLOCKQUOTE dir=ltr 
  style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
    <DIV 
    style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
    <A title=keirh@bluestoneenergy.com 
    href="mailto:keirh@bluestoneenergy.com">Keir Howell</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>To:</B> <A title=bldg-sim@gard.com 
    href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, November 16, 2005 5:39 
    AM</DIV>
    <DIV style="FONT: 10pt arial"><B>Subject:</B> [bldg-sim] Out of Throttle 
    Range.</DIV>
    <DIV><BR></DIV>
    <DIV><FONT face=Arial size=2>If the apartment units have no cooling, then 
    you shouldn't experience any hours outside of the throttling range because 
    there will be no cooling setpoint.  Make sure that the cooling 
    temperature schedule (COOL-TEMP-SCH) for all zones on the second and third 
    floors are undefined.</FONT></DIV>
    <DIV><FONT face=Arial size=2></FONT> </DIV>
    <DIV><FONT face=Arial size=2>Keir Howell<BR>Bluestone Energy Services, 
    Ltd.<BR>phone:    781-356-8865<BR>fax:    
    781-356-8864</FONT></DIV>
    <BLOCKQUOTE dir=ltr 
    style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
      <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
      <DIV 
      style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
      <A title=asitorus@glumac.com href="mailto:asitorus@glumac.com">Albert 
      Sitorus</A> </DIV>
      <DIV style="FONT: 10pt arial"><B>To:</B> <A title=bldg-sim@gard.com 
      href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</A> </DIV>
      <DIV style="FONT: 10pt arial"><B>Sent:</B> Tuesday, November 15, 2005 
      11:51 AM</DIV>
      <DIV style="FONT: 10pt arial"><B>Subject:</B> [bldg-sim] Out of Throttle 
      Range.</DIV>
      <DIV><BR></DIV>
      <DIV><FONT face=Arial size=2><SPAN class=598395115-15112005>Hello 
      everybody,</SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN class=598395115-15112005>I 
      am modeling a 3-story building mixed-used LEED building. The first 
      floor is used as classrooms and retails. The 2nd and 3rd floors are 
      used for residential units. Most of the systems on the 
      first floor are air-cooled condensing unit with electric 
      heat-pump heating, and the rest are exhaust fan systems. For the 
      2nd and 3rd floors, the apartment units use unit heaters  
      without any cooling. Corridors on these floors are served by 
      make-up air units with gas-fired heating. There is not any warning or 
      error when I simulate the model. </SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN class=598395115-15112005>The problem is 
      that I can't reduce the "percent of hours any system zone outside of 
      throttling range" to an acceptable value. I have 
      tried adjusting air flow, throttling range, etc w/o achieving the 
      desired results. I looked at SS-O report and the problem is there are 
      too many hours when the cooling isn't satisfied for 2nd and 3rd 
      floor. In other words, for all zones on 2nd and 3rd floors there 
      are many hours when the units are over 80 - 85F or 
      even above 85F. I also tweaked the fans night control cycle, infiltration 
      schedule, set-point temperature, and zone entering max supple temp but the 
      out of throttling range is still exceptionally 
      high. </SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN class=598395115-15112005>I have no 
      idea how to fix this error. Without cooling in these units, should I 
      not expect such large out of throttling range issues? Has anyone 
      encountered this kind of problem before? Can anyone share their 
      experience or solution? Has anyone done LEED model w/o 
      cooling? I would appreciate any response, idea or hints that 
      would help solve this problem. I have described the problem as 
      clear as I can but I am sure there are things that I may have 
      left out, please don't hesitate to ask me. Again, I am trying to get some 
      ideas, hints or methods so I will provide as much info as anyone want 
      in order to help me solve this.</SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN class=598395115-15112005>Thank you very 
      much in advance for your help. I appreciate any 
      help, hints or suggestions. Thank you 
      again. </SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005>Sincerely, </SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005>Albert Sitorus. </SPAN></FONT></DIV>
      <DIV><FONT face=Arial size=2><SPAN 
      class=598395115-15112005></SPAN></FONT> </DIV><FONT face=Arial 
      size=2></FONT><FONT face=Arial size=2></FONT><FONT face=Arial 
      size=2></FONT>
      <DIV><FONT face=Arial size=2></FONT><FONT face=Arial size=2></FONT><FONT 
      face=Arial size=2></FONT><BR><BR><SPAN 
      style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN><STRONG>Albert T. 
      Sitorus</STRONG><BR><SPAN 
      style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><FONT face="Times New Roman" 
      size=3>Energy Analyst</FONT></SPAN></DIV>
      <DIV><FONT face=Arial size=2></FONT> </DIV>
      <DIV><FONT face=Arial size=2></FONT><BR><A 
      href="http://www.glumac.com/"><IMG 
      src="http://www.glumac.com/glumacsig.gif" border=0 NOSEND="1"></A> </DIV>
      <DIV>
      <HR style="WIDTH: 330px; HEIGHT: 2px" align=left width=330 color=#9acb33 
      noShade SIZE=2>
      </DIV>
      <DIV></DIV><SPAN 
      style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">320 
      SW Washington, Suite 200</SPAN><BR><SPAN 
      style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">Portland, 
      OR 97204-2640</SPAN><BR><SPAN 
      style="FONT-SIZE: 9pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt">T.  
      503.227.5280<SPAN style="mso-spacerun: yes">  </SPAN>F. 
      503.274.7674<BR><BR><STRONG><SPAN 
      style="FONT-SIZE: 10pt; COLOR: #333333; FONT-FAMILY: Arial">Thinking. 
      Inside the building.</SPAN></STRONG><BR><STRONG><SPAN 
      style="FONT-WEIGHT: normal; FONT-SIZE: 10pt; COLOR: #333333; FONT-FAMILY: Arial"><A 
      href="http://www.glumac.com/">www.glumac.com</A></SPAN></STRONG></SPAN> 
      <DIV> </DIV><PRE>======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>
=====================================================You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>