The "air fired" surge gravel ( 2" to 6" ) rock bed storage is easily
beaten by an<br>
"over square Water fired" active / passive combo. Ours has been running
since<br>
January '87.  After accounting for an 85% reduction in DHW load from
active<br>
solar  AND 50% reduction in wall plug load via lighting and other
measures AND<br>
savings from a 2.5 / 4 ton 2 speed heat pump ;  we still beat Energy
10  V1.6 estimates of our energy use by 700+ kwhr /month. Our E-10
model has been refined over 28 iterations against weather data.  This
design won an  ASME region V design contest in 1980. General Tips
>>><br>
<br>
1) WALLS 2x6 stud 24" OC  1" blue styrofoam sheathing on outside,<br>
steel diagonal bracing. R-19 fiberglass. Tan brick veneer all walls
above<br>
grade.  57s gravel 4 ft deep below basement slab; 1" styro Tbreak
inside basement<br>
walls to footings, 2" Styro outside basement walls to footings. S side
basement is 100%<br>
height walk out.<br>
<br>
2) WINDOWS -- You have to use casement or awning windows because they<br>
seal air leakage better than anything else. Patio door only 1 allowed,
South side
only. <br>
N/E/W sides LoE2 glazing, S side LoE2 or double clear. All windows
& patio<br>
door have night insulation. Prefer fewer larger windows over more
numerous<br>
smaller windows for E/W/S.  ie  Andersen CW-24s  a  4640 Double
casement. <br>
N side gets  CW-14s a  2440? Single casement.<br>
Patio Door gets lightshelf daylight hours in heating season..<br>
<br>
3) SKYLIGHT  -- ONE only above freezer <font color="#cc0000">openable
. Freezer precharges skylight<br>
shaft with warm air !! <font color="#000000">Now you are ready for a
quick blow off to shed heat at sundown<br>
or to keep kitchen smoke contained ........... we have 10 ft ceilings
in  the Kitchen.<br>
</font></font><br>
4) OVERHANG  2ft on E W N sides, 4 ft on S --two story height. We are
at  38-45-00 N.<br>
<br>
5) Roof is 6/12 pitch  20 deg W of South, recommend 8/12 or 12/12   for
new install.<br>
Basement  slab w/ 900 ft + HDPE pipe, would use  REHAU  PEX for new
install. <br>
<br>
6) You will find a fan does not provide the flow pressure required to
spread out the heat<br>
in a really large rock bed ( ~ 2" water gauge ). You need a centrifugal
blower ( ~ 10" WG)<br>
it  will be louder than a fan.<br>
John R Ross  P.E.<br>
<br>
Renee J. Azerbegi wrote:<br>
<blockquote type="cite"
 cite="midMDAEMON-F200504061142.AA4241625pd80000651218@gard.com">
  <pre wrap="">I live in a passive (and active) solar home with rock bed storage in my
sunroom in Golden, Colorado. We did not design this house ourselves....
There is about 4 feet of rocks underneath wooden boards with about 1/2" of
space between the boards and the rocks start about 1 foot below the boards.
There is also brick on both walls. It gets really hot in this room in the
winter (and in the summer since it was not designed with proper overhangs so
we need to add some exterior overhangs as well). There used to be a duct and
fan to blow heat to the floor above, but it was removed by the previous
owners probably due to aesthetics since it was right in the middle of the
sunroom. Due to the airspace, there are a lot of bugs and dust that collect
on the rock bed. Frankly, I think the sunspace itself is quite sufficient
with the brick and glazing alone, and due to indoor air quality concerns, we
will likely take out the rock bed or seal it up. So if you do this rock bed,
make sure it is well sealed so bugs and dust cannot collect on it,
especially if you are going to blow air through it. And if it is already
going to be located in a sun room, it may not be necessary if you have brick
or another high mass feature in the space. It sounds like yours is going
over tile. You'd have to design it to make sure the rocks below the tile
heat up.

Renee Azerbegi

-----Original Message-----
From: <a
 class="moz-txt-link-abbreviated" href="mailto:postman@gard.com">postman@gard.com</a> [<a
 class="moz-txt-link-freetext" href="mailto:postman@gard.com">mailto:postman@gard.com</a>] On Behalf Of Graham & Megan
Sent: Tuesday, April 05, 2005 3:19 PM
To: <a
 class="moz-txt-link-abbreviated" href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</a>
Subject: [bldg-sim] suggestions other than eQuest

Lee,
I tend to agree with many of Steve's observations.  When I was at Berkeley
we visited the Village Homes site in Davis, California.  While this is a
more temperate climate, the feedback we got at the time was that the houses
performed quite well but the fan coupled rock stores in most cases were
providing very marginal benefit in winter as the houses already had a number
of other passive features.  If my memory servese me correctly, the controls
were two complicated for the simple home owner to manage to get the most out
of the system.  The summer benefits were likely greater.  I believe there is
some case study material on the Vital Signs website.  Cris Benton at
Berekeley I believe still runs the Vital Signs program if you can't find the
website.  A web search on Village Homes will turn up additional background
information.
Regards,
Graham
----- Original Message ----- 
From: "Steven Gates" <a
 class="moz-txt-link-rfc2396E" href="mailto:steve.gates@doe2.com"><steve.gates@doe2.com></a>
To: <a
 class="moz-txt-link-rfc2396E" href="mailto:bldg-sim@gard.com"><bldg-sim@gard.com></a>
Sent: Tuesday, April 05, 2005 12:41 PM
Subject: [bldg-sim] suggestions other than eQuest


  </pre>
  <blockquote type="cite">
    <pre wrap="">Lee,

OK, the rockbed is being charged with warm air from inside the house; not
from a solar air heater which could produce air at a considerably warmer
temperature.  If the maximum space temperature you are comfortable with is
80F, and the rock bed must be heated to at least 75F to later produce 70F
    </pre>
  </blockquote>
  <pre wrap=""><!---->in
  </pre>
  <blockquote type="cite">
    <pre wrap="">the space, then we are talking about a 5F MAXIMUM temperature differential
between the rock bed and the space.

While I make my living by writing energy simulation software (DOE-2), I
believe there are many times when a full-blown computer simulation is not
justified.  So, before getting bogged down in trying to model a rockbed
system in a detailed energy simulation program, it might be useful to
    </pre>
  </blockquote>
  <pre wrap=""><!---->first
  </pre>
  <blockquote type="cite">
    <pre wrap="">look at some rough numbers, and make a decision as to whether the rough
numbers justify a more detailed analysis.

So, for what it is worth, here is my 15 minutes of thinking:

To move 1000 cfm at 1" static will require about 0.25 kW of fan energy.
    </pre>
  </blockquote>
  <pre wrap=""><!---->But
  </pre>
  <blockquote type="cite">
    <pre wrap="">the air has to first be used to charge the rockbed, and then again to
discharge it.  So double the fan energy to 0.5 kW/1000cfm of heated air
delivered to the space.  At $0.10/kWh, this amounts to $0.05/1000cfm per
hour.

The amount of heat that can be delivered per 1000 cfm is:  1.08 * 1000cfm
    </pre>
  </blockquote>
  <pre wrap=""><!---->*
  </pre>
  <blockquote type="cite">
    <pre wrap="">5dT = 5400 Btuh.  Adding in the fan heat, the net heating effect is 5770
Btuh.  At an equivalent 80% furnace efficiency and $1.00 per therm of
natural gas, the gross savings in natural gas are $0.072/1000cfm of heated
air delivered to the space.  Assuming the system can provide 100% of the
annual heating loads, the savings on the heating bill are 1 - 0.05/0.072 =
~30%

The location described gets a lot of winter sun, which even in a
conventional design will act to significantly reduce heating loads.  What
would the house cost to heat if intelligently designed (well insulated,
reasonable south glass, some thermal mass), but without the rockbed? $1500
per year?  What does the rockbed cost, $20,000?  Does a potential ~$500
    </pre>
  </blockquote>
  <pre wrap=""><!---->per
  </pre>
  <blockquote type="cite">
    <pre wrap="">year savings justify the cost of the rockbed?

Of course, these numbers are very approximate, and the actual savings may
vary due to a variety of factors:
1)  If natural gas is not available, then the system may be more
    </pre>
  </blockquote>
  <pre wrap=""><!---->attractive.
  </pre>
  <blockquote type="cite">
    <pre wrap="">2)  The 5F delta T may be too large.  80F space temperature in a cold,
    </pre>
  </blockquote>
  <pre wrap=""><!---->dry,
  </pre>
  <blockquote type="cite">
    <pre wrap="">5000 ft desert climate may result in extremely low humidity in the space.
This may tend to desiccate the occupant's skin and sinuses, and they may
    </pre>
  </blockquote>
  <pre wrap=""><!---->not
  </pre>
  <blockquote type="cite">
    <pre wrap="">find it comfortable.
3)  Many hours, the fan will be charging the rockbed with the house being
cooler than 80F.  So effectiveness during those hours is reduced.
4)  Rockbeds tend to be dusty, and may become moldy.  You may need to use
    </pre>
  </blockquote>
  <pre wrap=""><!---->a
  </pre>
  <blockquote type="cite">
    <pre wrap="">high efficiency filter, which may raise the required fan static to do the
job.
5)  This quickie analysis assumes that the solar system can provide 100%
    </pre>
  </blockquote>
  <pre wrap=""><!---->of
  </pre>
  <blockquote type="cite">
    <pre wrap="">the annual heating; some auxiliary heat will almost certainly be required.
6)  All losses from the rockbed to the ground are neglected.
7)  The bright sun will act to fade the furniture more rapidly than in a
conventional house.  What is impact on the furniture replacement budget?
The sun may also degrade the finish on cabinetry more rapidly, especially
    </pre>
  </blockquote>
  <pre wrap=""><!---->if
  </pre>
  <blockquote type="cite">
    <pre wrap="">varnished.  Deduct maintenance costs from the energy savings.

For many experienced people using this listing, the above may come across
    </pre>
  </blockquote>
  <pre wrap=""><!---->as
  </pre>
  <blockquote type="cite">
    <pre wrap="">too preachy.  To those people, I apologize.  But I understand that a lot
    </pre>
  </blockquote>
  <pre wrap=""><!---->of
  </pre>
  <blockquote type="cite">
    <pre wrap="">graduate students also subscribe to this listing, and I want to emphasize
that considering too many details when first approaching a problem can get
in the way of the answer.  It is often useful to first look at the forest
before focusing on the trees........

Lee, I would be interested in knowing what your ultimate conclusions are.

Steve

-----Original Message-----
From: <a
 class="moz-txt-link-abbreviated" href="mailto:postman@gard.com">postman@gard.com</a> [<a
 class="moz-txt-link-freetext" href="mailto:postman@gard.com">mailto:postman@gard.com</a>] On Behalf Of Lee Elson
Sent: Monday, April 04, 2005 4:18 PM
To: <a
 class="moz-txt-link-abbreviated" href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</a>
Cc: <a
 class="moz-txt-link-abbreviated" href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</a>
Subject: [bldg-sim] suggestions other than eQuest

First, let me say that I've been a bit overwhelmed with the quality (and
quantity) of responses. I appreciate all the discourse and am struggling
to check out all the suggestions.

It is a good idea for me to address some of the issues I described
originally. "ICF" stands for insulated concrete forms which consist of a
foam form (about 2" thick) into which concrete (9-12" thick) is poured.
These will be used for exterior walls for the single story structure.
Although the insulating (sound and heat) properties are great, and the
costs are reasonable, there is little heat storage by the concrete
because of the interior foam.

Some details on the rock floor. It will be a layer of 2" rocks, about 4
feet deep. There will be insulation underneath and a concrete and tile
floor above. Part (about 1/3) of the tile floor will be in direct sun
when conditions allow. There will be a couple of plenums (consisting of
stacked concrete blocks with spacers near the bottom) running the length
of the rock floor and there will be an air barrier of some sort that
will channel warm air from the plenum to the outer portion of the rock
floor. Other plenums near the ceiling will allow warm air to be forced
(with fans) down to the rock floor where it will circulate back into the
house through floor registers (after having given up heat to the rocks).
This rock floor will be used over the entire structure (about 3500 sq
ft). The builder/designer says that he's used this approach and it works
pretty well. There is sufficient heat transferred to the rocks to make
them a reasonable thermal mass. This system also redistributes air from
the warm (south/high) side of the structure to the cold (north/low) side.

I realize that this type of thermal mass may be difficult to model in
detail and that it is important to look at the energy cost of the fan(s)
in all of this.

I hope this description helps.

Regards,
Lee Elson

Steven Gates wrote:

    </pre>
    <blockquote type="cite">
      <pre wrap="">Is there a more fundamental issue that is being missed here?  Lee Elson's
description includes the phrase "insulated rock floor with active air
recirculation".  It also includes "ICF", which I am not familiar with.

The description of the system appears to be a floor/rock-bed that uses a
      </pre>
    </blockquote>
    <pre wrap="">fan
    </pre>
    <blockquote type="cite">
      <pre wrap="">to recirculate air between the rockbed and the space.  So solar falls
directly on the floor surface, but the floor also captures/releases heat
convectively using a fan.

If that is the case, it is critical that the convective leg be simulated.
Assuming the space will not be allowed to be uncomfortably warm, and that
the rockbed temperature must be at least 70F to have any heating
effectiveness at all, this implies a very low delta-T between the rockbed
and the space when convectively charging or discharging the rockbed -
corresponding to a large, potentially drafty, airflow.  It also suggests
that the convective thermal capacity of the rockbed may be quite limited,
corresponding to a temperature swing on the order of 5F or less.

It is essential that the fan energy of this system be modeled; with such
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->a
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">small delta T between the rockbed and the space, the cost to run the fan
      </pre>
    </blockquote>
    <pre wrap="">may
    </pre>
    <blockquote type="cite">
      <pre wrap="">exceed the cost of the heating energy saved by the convective component
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->of
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">this system.

It would be helpful if Lee described the system in more detail.
eQUEST/DOE-2 does not simulate either convective rockbeds or the combined
radiant/convective rockbed floor that this building appears to use.  Do
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->any
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">programs have this capability?


-----Original Message-----
From: <a
 class="moz-txt-link-abbreviated" href="mailto:postman@gard.com">postman@gard.com</a> [<a
 class="moz-txt-link-freetext" href="mailto:postman@gard.com">mailto:postman@gard.com</a>] On Behalf Of Blake, Jeff
Sent: Sunday, April 03, 2005 8:03 AM
To: <a
 class="moz-txt-link-abbreviated" href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</a>
Subject: [bldg-sim] suggestions other than eQuest

Lee,

Doe2 (2.1 or 2.2) is not the right program for looking at heavy thermal
      </pre>
    </blockquote>
    <pre wrap="">mass
    </pre>
    <blockquote type="cite">
      <pre wrap="">buildings.  The limitation is a function of the thermal response factors
used to represent time-delayed heat transfer through opaque surfaces.
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->This
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">method is a legacy of the original DOE2 design requirements which were
somewhat hindered by slow computers.

You should use a simulation program that uses a more fundamental heat
balance approach.  There are several but I believe that ESP-r (ESRU,
University of Strathclyde) is one of the best.

Jeff Blake

-----Original Message-----
From: <a
 class="moz-txt-link-abbreviated" href="mailto:postman@gard.com">postman@gard.com</a> [<a
 class="moz-txt-link-freetext" href="mailto:postman@gard.com">mailto:postman@gard.com</a>]On Behalf Of Lee Elson
Sent: Friday, April 01, 2005 3:55 PM
To: <a
 class="moz-txt-link-abbreviated" href="mailto:bldg-sim@gard.com">bldg-sim@gard.com</a>
Subject: [bldg-sim] suggestions other than eQuest


I'm designing a 3500 sq foot residence at a 5000' desert-like elevation
(Nevada).
The site has good sun exposure and the climate is generally dry. Typical
temperatures in Feb are 20-40 F. The building is mostly oriented
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->east-west
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">and has
a 2' deep insulated rock floor (for thermal mass) with active air
recirculation.
ICF's will be used as well as tile over concrete (above rock floor) in
      </pre>
    </blockquote>
    <pre wrap="">south
    </pre>
    <blockquote type="cite">
      <pre wrap="">facing rooms.

I'm trying to get a realistic estimate of temperature swings and
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->auxiliary
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">heating
requirements. I've used eQuest, which seems pretty impressive and easy to
use.
I've entered the floor plan layout, specified the glazing (clear glass on
the
south side) and the building materials. The calculations are a bit
disappointing:
with 12% of the total floor space in south facing glass, the aux heating
required
is not too different (~20%) from a house with standard insulation and no
added
south facing glass. Another oddity: when I change the south facing glass
area from
5% of the available south wall to 90% of the south wall, I get an
      </pre>
    </blockquote>
    <pre wrap="">*increase*
    </pre>
    <blockquote type="cite">
      <pre wrap="">in
aux heating requirements. The eQuest developer thinks this is due to
inadequate
thermal mass/heat recirculation modeling.

I suspect that eQuest is not doing accurate modeling since other houses
      </pre>
    </blockquote>
    <pre wrap="">with
    </pre>
    <blockquote type="cite">
      <pre wrap="">a
similar design in this area get much better thermal performance. Can
      </pre>
    </blockquote>
  </blockquote>
  <pre wrap=""><!---->anyone
  </pre>
  <blockquote type="cite">
    <blockquote type="cite">
      <pre wrap="">suggest either software or a service provider that might be able to do a
more
accurate calculation?

TIA

Lee Elson




======================================================
You received this e-mail because you are subscribed
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe
      </pre>
    </blockquote>
    <pre wrap="">>from this mailing list send a blank message to
    </pre>
    <blockquote type="cite">
      <pre wrap=""><a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>

======================================================
You received this e-mail because you are subscribed
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe
      </pre>
    </blockquote>
    <pre wrap="">>from this mailing list send a blank message to
    </pre>
    <blockquote type="cite">
      <pre wrap=""><a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>




======================================================
You received this e-mail because you are subscribed
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe
      </pre>
    </blockquote>
    <pre wrap="">>from this mailing list send a blank message to
    </pre>
    <blockquote type="cite">
      <pre wrap=""><a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>


      </pre>
    </blockquote>
    <pre wrap="">======================================================
You received this e-mail because you are subscribed
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe
from this mailing list send a blank message to
<a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>




======================================================
You received this e-mail because you are subscribed
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe
from this mailing list send a blank message to
<a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>

    </pre>
  </blockquote>
  <pre wrap=""><!---->

======================================================
You received this e-mail because you are subscribed 
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe 
from this mailing list send a blank message to 
<a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>




======================================================
You received this e-mail because you are subscribed 
to the <a
 class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM@GARD.COM">BLDG-SIM@GARD.COM</a> mailing list.  To unsubscribe 
from this mailing list send a blank message to 
<a class="moz-txt-link-abbreviated"
 href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>


  </pre>
</blockquote>
<PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></body>

</html>