District steam is not always waste energy from a power plant.  In
the case that district steam is just for heating and cooling, then the
ASHRAE 90.1 states correctly that the heating and/or cooling should be
modelled as purchased using the applicable rate.  For situations
were the building uses steam that can't be used by the power plant I
would suggest that the proposed would only get credit if the overall
steam efficiency (work out/ fuel in) is greater than 75% AFUE.  This
is the budget building perscriptive requirement for steam boilers. 
LEED should not give credit for using a convenient heat/cool source if
that source is inefficient overall.<br><br>
<br>
At 15:24 12/11/2004, Varkie Thomas wrote:<br>
<blockquote type=cite class=cite cite=""><font face="Times New Roman, Times"> <br>
At the end of this message is the part load performance of steam turbine
chillers.  As you can see from the response from Rob Firnstein of
</font>York, energy software developers can incorporate this data into
their programs. <br>
<font face="Times New Roman, Times"> <br>
Steam turbine chillers have recently been specified for buildings in
NYC.  ConEd has low summer rates for steam.  Cities like
</font>Boston, Minneapolis and Philadelphia also provide district
steam.  Since district steam is waste energy from a power plant
perhaps there should be LEED credits for using this waste energy although
the ECB method might show higher costs over electric centrifugal.<br>
<font face="Times New Roman, Times"> <br>
Varkie Thomas<br>
 <br>
 <br>
-----Original Message-----<br>
From: Robert Firnstein
[<a href="mailto:robert.firnstein@york.com" eudora="autourl">mailto:robert.firnstein@york.com</a>]
<br>
Sent: </font>Thursday, November 11, 2004 3:20 PM<br>
<font face="Times New Roman, Times">To: </font>Varkie Thomas<br>
<font face="Times New Roman, Times">Subject: RE: </font>Steam Turbine YK
rating<br>
<font face="Times New Roman, Times"> <br>
Varkie,<br>
 <br>
Feel free to forward on the information. Recently, </font>York
re-designed the<br>
<font face="Times New Roman, Times">software for selecting our steam
turbine chillers so that we now have<br>
greater capability to pair compressors and steam turbines for
optimum<br>
performance. If you are interested in seeing any generic selections
for<br>
additional chillers please let me know.<br>
 <br>
Regards,<br>
 <br>
Rob Firnstein<br>
Sales Engineer<br>
York</font> International - Chicago<br>
<font face="Times New Roman, Times">PH:(847)493-6124
FX:(847)759-0676<br>
 <br>
<b>Part Load Performance at Condenser Water Temperatures (CWT)<br>
</b></font><font face="Times New Roman, Times" size=2>Constant Speed
Operation at 4500 RPM, 125 PSIG D&S Steam Supply, Producing
41<sup>o</sup>F Chilled Water<br>
     RCLWT = Refrigerant Condenser Leaving Water
Temperature  <br>
<b>CWT</b></font>     <font size=2><b>%
Load</b></font>       
<font size=2><b>100%</b></font>    
<font size=2><b>90%</b></font>      
<font size=2><b>80%</b></font>     
<font size=2><b>70%</b></font>     
<font size=2><b>60%</b></font>     
<font size=2><b>50%</b></font>   
<font size=2><b>40%</b></font>   
<font size=2><b>30%</b></font>   
<font size=2><b>20%</b></font>    
<font size=2><b>15%<br>
</font><font face="Times New Roman, Times" size=2> </b></font>          
<font size=2><b>Tons</b></font>           
<font size=2>1800</font>       
<font size=2>1620</font>       
<font size=2>1440</font>       
<font size=2>1260</font>      
<font size=2>1080</font>      
<font size=2>900</font>      
<font size=2>720</font>      
<font size=2>540</font>      
<font size=2>360</font>      
<font size=2>270<br>
</font><font face="Times New Roman, Times" size=2><b>85<sup>o</sup>F</b></font>     
<font size=2><b>BHP</b></font>           
<font size=2>1,378.0</font>    
<font size=2>1,210.6</font>    
<font size=2>1,058.2</font>    
<font size=2>923.6</font>     
<font size=2>802.4</font>     
<font size=2>690.4</font>    
<font size=2>583.9</font>     <font size=2>- -
-</font>       <font size=2>- -
-</font>       <font size=2>- - -<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/Hr</b></font>        
<font size=2>17,873</font>    
<font size=2>15,919</font>     
<font size=2>13,884</font>    
<font size=2>12,210</font>    
<font size=2>10,744</font>    
<font size=2>9,383</font>    
<font size=2>8,029</font>     <font size=2>- -
-</font>       <font size=2>- -
-</font>       <font size=2>- - -<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/TR-Hr</b></font>   
<font size=2>9.93</font>       
<font size=2>9.83</font>        
<font size=2>9.64</font>       
<font size=2>9.69</font>       
<font size=2>9.95</font>       
<font size=2>10.43</font>    
<font size=2>11.15</font>     <font size=2>- -
-</font>       <font size=2>- -
-</font>       <font size=2>- - -<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>RCLWT <sup>o</sup>F</b></font>   
<font size=2>94.33</font>      
<font size=2>93.38</font>      
<font size=2>92.43</font>      
<font size=2>91.50</font>     
<font size=2>90.57</font>     
<font size=2>89.67</font>    
<font size=2>88.76</font>     <font size=2>- -
-</font>       <font size=2>- -
-</font>       <font size=2>- - -<br>
</font><font face="Times New Roman, Times" size=2><b>75<sup>o</sup>F</b></font>     
<font size=2><b>BHP</b></font>           
<font size=2>1,182.8</font>    
<font size=2>1,043.2</font>    
<font size=2>918.6</font>      
<font size=2>808.1</font>     
<font size=2>706.6</font>     
<font size=2>611.3</font>    
<font size=2>519.1</font>    
<font size=2>427.5</font>    
<font size=2>335.3</font>     
<font size=2>307.1<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/Hr</b></font>        
<font size=2>15,069</font>    
<font size=2>13,395</font>     
<font size=2>11,832</font>    
<font size=2>10,497</font>    
<font size=2>9,264</font>     
<font size=2>8,106</font>    
<font size=2>6,982</font>    
<font size=2>5,912</font>    
<font size=2>4,781</font>     
<font size=2>4,453<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/TR-Hr</b></font>   
<font size=2>8.37</font>       
<font size=2>8.27</font>        
<font size=2>8.22</font>       
<font size=2>8.33</font>       
<font size=2>8.58</font>       
<font size=2>9.01</font>     
<font size=2>9.70</font>     
<font size=2>10.95</font>    
<font size=2>13.28</font>     
<font size=2>16.49<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>RCLWT <sup>o</sup>F</b></font>   
<font size=2>84.14</font>      
<font size=2>83.20</font>      
<font size=2>82.28</font>      
<font size=2>81.37</font>     
<font size=2>80.47</font>     
<font size=2>79.58</font>    
<font size=2>78.69</font>    
<font size=2>77.80</font>    
<font size=2>76.92</font>     
<font size=2>76.34<br>
</font><font face="Times New Roman, Times" size=2><b>65<sup>o</sup>F</b></font>     
<font size=2><b>BHP</b></font>           
<font size=2>1,035.7</font>    
<font size=2>921.1</font>      
<font size=2>817.9</font>      
<font size=2>723.4</font>     
<font size=2>634.6</font>     
<font size=2>550.3</font>    
<font size=2>467.6</font>    
<font size=2>384.3</font>    
<font size=2>299.7</font>     
<font size=2>264.8<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/Hr</b></font>        
<font size=2>13,008</font>    
<font size=2>11,633</font>     
<font size=2>10,412</font>    
<font size=2>9,332</font>     
<font size=2>8,180</font>     
<font size=2>7,215</font>    
<font size=2>6,256</font>    
<font size=2>5,292</font>    
<font size=2>4,307</font>     
<font size=2>3,901<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/TR-Hr</b></font>   
<font size=2>7.23</font>       
<font size=2>7.18</font>        
<font size=2>7.23</font>       
<font size=2>7.41</font>       
<font size=2>7.57</font>       
<font size=2>8.02</font>     
<font size=2>8.69</font>     
<font size=2>9.80</font>     
<font size=2>11.96</font>     
<font size=2>14.45<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>RCLWT <sup>o</sup>F</b></font>   
<font size=2>73.99</font>      
<font size=2>73.08</font>      
<font size=2>72.18</font>      
<font size=2>71.28</font>     
<font size=2>70.40</font>     
<font size=2>69.52</font>    
<font size=2>68.64</font>    
<font size=2>67.76</font>    
<font size=2>66.88</font>     
<font size=2>66.42<br>
</font><font face="Times New Roman, Times" size=2><b>55<sup>o</sup>F</b></font>     
<font size=2><b>BHP</b></font>           
<font size=2>926.6</font>      
<font size=2>828.4</font>      
<font size=2>738.3</font>      
<font size=2>654.3</font>     
<font size=2>574.3</font>     
<font size=2>496.1</font>    
<font size=2>418.8</font>    
<font size=2>339.9</font>    
<font size=2>259.5</font>     
<font size=2>220.2<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/Hr</b></font>        
<font size=2>11,527</font>    
<font size=2>10,405</font>     
<font size=2>9,369</font>      
<font size=2>8,408</font>     
<font size=2>7,485</font>     
<font size=2>6,588</font>    
<font size=2>5,691</font>    
<font size=2>4,776</font>    
<font size=2>3,834</font>     
<font size=2>3,365<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>Lbs/TR-Hr</b></font>   
<font size=2>6.40</font>       
<font size=2>6.42</font>        
<font size=2>6.51</font>       
<font size=2>6.67</font>       
<font size=2>6.93</font>       
<font size=2>7.32</font>     
<font size=2>7.90</font>     
<font size=2>8.84</font>     
<font size=2>10.65</font>     
<font size=2>12.46<br>
</font><font face="Times New Roman, Times" size=2><b> </b></font>          
<font size=2><b>RCLWT <sup>o</sup>F</b></font>   
<font size=2>63.87</font>      
<font size=2>62.98</font>      
<font size=2>62.09</font>      
<font size=2>61.21</font>     
<font size=2>60.34</font>     
<font size=2>59.46</font>    
<font size=2>58.59</font>    
<font size=2>57.72</font>    
<font size=2>56.84</font>     
<font size=2>56.43<br>
</font><font face="Times New Roman, Times"> <br>
</font><br>
<pre>


You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</pre><font face="Courier New, Courier"></blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones, P.Eng.<br>
14 Oneida Avenue<br>
Toronto, ON M5J2E3<br>
Tel. 416 203-7465<br>
Fax. 416 946-1005</font><PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></body>

</html>