<DIV><FONT color=#800000 size=2>One has to be careful about defining the shading 
factor. The shaded portion of the window in PREBID is treated as the opaque part 
of the window which may have a very different U-value than that of the 
glass (glazing). The heat conducted across the window will be affected if a 
glazing forms significantly large portion of the wall.</FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT color=#800000 size=2>Let me explain by the following example (a 
single glazed window with wooden frame).</FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT color=#800000 size=2>If the shading coefficient is 0.5, beam and 
diffuse radiation will pass through 50% of the area of the glass. The 
remaining 50% of glass area would be treated as wood.</FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT color=#800000 size=2>In reality, heat conduction will take place 
through the remaining 50% of the glass area (it should not be treated as 
wood).  (Imagine the difference when the c<FONT color=#800000 
size=2>onductivity of glass = 2.88 kJ/m-K</FONT> and the c<FONT color=#800000 
size=2>onductivity of wood = 0.54 kJ/m-K).</FONT></FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT color=#800000 size=2>A better method to model shading would be to 
treat the beam and diffuse radiation with the shading coefficients in IISiBat 
before it is given as input to Type 56.</FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT size=2><FONT color=#800000><FONT>Caution: The modified radiation to 
be given separately for windows, it should not affect the radiation incident on 
the walls. This would require creating a separate surface to contain the windows 
only. Same c</FONT>aution is required also when Types 34 and 68 are used as 
suggested by David.</FONT></FONT></DIV>
<DIV><FONT size=2><FONT color=#800000></FONT></FONT> </DIV>
<DIV><FONT size=2><FONT color=#800000>David: pl confirm the above 
statement.</FONT></FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<DIV><FONT color=#800000 size=2>Anil Misra</FONT></DIV>
<DIV><FONT color=#800000 size=2></FONT> </DIV>
<BLOCKQUOTE dir=ltr 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #800000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=bradley@tess-inc.com href="mailto:bradley@tess-inc.com">David 
  Bradley</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, November 15, 2004 9:38 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] Windows Shading 
  Coefficient</DIV>
  <DIV><BR></DIV><FONT face=arial size=2>Dear </FONT>Maurizio,<BR><BR>
  <BLOCKQUOTE class=cite cite="" type="cite"><FONT face=arial size=2>1) I'm 
    currently modelling in PREBID a residential building for which the montly 
    Shading Coefficients on the windows have been calculated with the software 
    ECOTECT. I insert the SC in the appropriate field ("external shading 
    coefficient") as an input and set the "view factor" to 0,5 (vertical 
    surfaces). It's the exact way? My doubt is that the solar incident radiation 
    is halved (view factor = 0,5) and then reduced of the 
  SC...</FONT></BLOCKQUOTE><BR>It is correct, provided that the shading 
  coefficient from Ecotect is the opaque fraction of the window (i.e. 1 = 
  completely shaded).<BR>The view factor to the sky (FSky) is only used for 
  longwave radiation so it will not interfere with shading.<BR><BR>The one thing 
  to bear in mind about PREBID's external and internal shading coefficient is 
  that the entered fraction effects both beam and diffuse radiation equally. 
  Thus if you enter a value of 0.5 for the external shading factor, half of the 
  incident diffuse radiation and half of the incident beam radiation will enter 
  the space. If you want to treat beam and diffuse radiation separately, you can 
  use one of the external shading models (Type34, or Type68).<BR><BR>
  <BLOCKQUOTE class=cite cite="" type="cite"><FONT face=arial size=2>2) It's 
    possible to use old TESS libraries with TRNSYS 16 or are they already 
    comprised in the new version?</FONT></BLOCKQUOTE><BR>Because of the change in 
  coding standards for components between version 15 and 16, the TESS Libraries 
  <I>v. </I>1.x are not directly useable with TRNSYS <I>v</I> 16. We have, 
  however, expanded the libraries and released version 2.0, which are not only 
  compatible with TRNSYS 16 but are also backwards compatible with TRNSYS 15. If 
  you are interested in upgrading, you will be credited the full amount that you 
  paid for your version 1.x libraries toward the purchase of version 2.x 
  libraries. If you do not wish to upgrade then you can follow the steps laid 
  out in the TRNSYS 16 documentation that show you how to modify a TRNSYS 15 
  Type to make it accessible from TRNSYS 16. I will send along a second email 
  containing a document that lists the contents of the 12 version 2.0 libraries 
  as well as an order form that contains the pricing information. I would be 
  happy to answer any questions that you might have about them.<BR><BR>Kind 
  regards,<BR>  David<BR><BR><BR><X-SIGSEP>
  <P></X-SIGSEP><FONT 
  face="Courier New, Courier">****************************************************************************************<BR>Thermal 
  Energy System Specialists (TESS), LLC <BR>David 
  BRADLEY                           
  2916 Marketplace Drive - Suite 104 
  <BR>Partner                                        
  Madison, WI 53719 <BR>Phone: (608) 274-2577 USA <BR>Fax: (608) 278-1475 
  <BR>E-mail: bradley@tess-inc.com <BR>Web Pages:  <A 
  href="http://www.tess-inc.com/" 
  eudora="autourl">http://www.tess-inc.com</A>     
  and      <A href="http://www.trnsys.com/" 
  eudora="autourl">http://www.trnsys.com<BR><BR></A>"Providing software 
  solutions for today's energy engineering projects" 
  <BR>****************************************************************************************<BR></FONT><PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>