<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML xmlns:o = 
"urn:schemas-microsoft-com:office:office"><HEAD>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=us-ascii">
<TITLE>Message</TITLE>
<META content="MSHTML 6.00.2800.1458" name=GENERATOR>
<STYLE></STYLE>
</HEAD>
<BODY bgColor=#ffffff>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>We are 
building a small two story dormitory in Albuquerque, NM with packaged 
rooftop units for each floor and exposure.</FONT></SPAN></DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>I am 
simulating per the ECB methodology and the baseline system is a PTAC 
system.  However, I went ahead and created two ECB models; 
one with PTAC and the other with packaged rooftops.  
</FONT></SPAN></DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>The 
PTAC is modeled with hydronic heating with a natural gas fired 
boiler.</FONT></SPAN></DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2>The rooftops have gas fired furnaces.</FONT></SPAN></DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>The 
PTAC's space heating energy is 5 to 6 times that of the rooftops.  
Even when simulating the PTAC with gas furnace heating, the space heating energy 
is still 5 to 6 times that of the rooftops.  Space cooling usage amongst 
all three models is very similar.</FONT></SPAN></DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>The 
peak heating loads are all the same for the various 
zones.</FONT></SPAN></DIV><SPAN class=808421917-01092004><FONT face=Arial 
color=#0000ff size=2></FONT><FONT face=Arial color=#0000ff size=2></FONT>
<DIV><FONT face=Arial color=#0000ff size=2></FONT><BR><FONT face=Arial><FONT 
color=#0000ff><FONT size=2>Has anyone had any issues modeling <SPAN 
class=808421917-01092004>space </SPAN>heating <SPAN 
class=808421917-01092004>with a </SPAN>gas furnaces in <SPAN 
class=808421917-01092004>a </SPAN>rooftops?<SPAN class=808421917-01092004>  
Basically, the space heating component is coming back consistently with the 
rooftops at less than 3kbtu/sf/yr.  I believe this to be too 
low.</SPAN></FONT></FONT></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><SPAN class=808421917-01092004><FONT face=Arial color=#0000ff size=2>Also, 
I can't seem to find any reports which show the Heating Input Ratio for the gas 
furnaces in the rooftops...I look at the SV-A report and I see Heating EIR which 
comes back as Zero all the time.  When I vary the HIR for the rooftops, the 
space heating load varies slightly.</FONT></SPAN></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV></SPAN> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="PostalCode"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="State"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="City"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="place"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="Street"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="address"></o:SmartTagType>
<STYLE>st1\:* {
        BEHAVIOR: url(#ieooui)
}
</STYLE>
<STYLE>@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.25in 1.0in 1.25in; mso-header-margin: .5in; mso-footer-margin: .5in; mso-paper-source: 0; }
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
SPAN.SpellE {
        mso-style-name: ""; mso-spl-e: yes
}
DIV.Section1 {
        page: Section1
}
</STYLE>
<DIV class=Section1>
<P class=MsoNormal align=left><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Louis Molinini</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Energy 
Engineer</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">LEED<SUP>TM</SUP></SPAN><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial"> </SPAN><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Accredited Professional</SPAN></P>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN class=SpellE><SPAN 
style="FONT-SIZE: 13.5pt; FONT-FAMILY: Arial">PBDewberry</SPAN></SPAN></P>
<P class=MsoNormal><?xml:namespace prefix = st1 ns = 
"urn:schemas-microsoft-com:office:smarttags" /><st1:Street><st1:address 
style="BACKGROUND-POSITION: left bottom; BACKGROUND-IMAGE: url(res://ietag.dll/#34/#1001); BACKGROUND-REPEAT: repeat-x"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">2101 Wilson 
Blvd.</SPAN></st1:address></st1:Street></P>
<P class=MsoNormal><st1:address 
style="BACKGROUND-POSITION: left bottom; BACKGROUND-IMAGE: url(res://ietag.dll/#34/#1001); BACKGROUND-REPEAT: repeat-x"><st1:Street><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Suite</SPAN></st1:Street><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> 200</SPAN></st1:address></P>
<P class=MsoNormal><st1:place><st1:City><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Arlington</SPAN></st1:City><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">, </SPAN><st1:State><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">VA</SPAN></st1:State><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </SPAN><st1:PostalCode><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">22201</SPAN></st1:PostalCode></st1:place></P>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">703-875-7642</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><A 
href="mailto:molinini.louis@dol.gov">molinini.louis@dol.gov</A></SPAN></P></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> postman@gard.com 
  [mailto:postman@gard.com] <B>On Behalf Of </B>Jeff Hirsch<BR><B>Sent:</B> 
  Tuesday, August 31, 2004 11:19 AM<BR><B>To:</B> 
  BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Modeling 100% OA VAV systems 
  in eQuest (and new EQUEST/DOE-2 versions)<BR><BR></FONT></DIV>
  <DIV><FONT face=Arial size=2>The problem being asked about arises due to the 
  different uses of the</FONT></DIV>
  <DIV>
  <DIV><FONT face=Arial size=2>alternative methods available in eQUEST freeware 
  </FONT><FONT face=Arial size=2>(a MS Windows implementation</FONT></DIV>
  <DIV><FONT face=Arial size=2>of </FONT><FONT face=Arial size=2>DOE-2.2) to 
  describe both the </FONT><FONT face=Arial size=2>minimum outside air (OA) 
  damper position</FONT></DIV>
  <DIV><FONT face=Arial size=2>as well as the minimum flow </FONT><FONT 
  face=Arial size=2>fraction setting of the VAV boxes in each zone.  
  </FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>The min-flow-ratio for a <FONT face=Arial 
  size=2>VAVS system </FONT>(DOE-2 keyword found on the SYSTEM</FONT></DIV>
  <DIV><FONT face=Arial size=2>properties sheet, </FONT><FONT face=Arial 
  size=2>fan tab, flow parameters sub tab in the eQUEST details 
mode</FONT></DIV>
  <DIV><FONT face=Arial size=2>interface) is the minimum VAV box flow fraction 
  for all boxes supplied by the "parent"</FONT></DIV>
  <DIV><FONT face=Arial size=2>air handler for the zone;</FONT><FONT face=Arial 
  size=2> this value can be specified for each individual box or 
for</FONT></DIV>
  <DIV><FONT face=Arial size=2>a system and thus "inherited" by all zone boxes 
  supplied by the system. If not given</FONT></DIV>
  <DIV><FONT face=Arial size=2>a value (min flow fraction </FONT><FONT 
  face=Arial size=2>control on the mentioned subtab) defaults </FONT><FONT 
  face=Arial size=2>to the larger of</FONT></DIV>
  <DIV><FONT face=Arial size=2>the minimum ventilation </FONT><FONT face=Arial 
  size=2>requirement, the flow required to satisfy </FONT><FONT face=Arial 
  size=2>the zone peak heating</FONT></DIV>
  <DIV><FONT face=Arial size=2>load heating, or other </FONT><FONT face=Arial 
  size=2>available minimum flow specifications (</FONT><FONT face=Arial 
  size=2>such as cfm/sqft, etc.)</FONT></DIV>
  <DIV><FONT face=Arial size=2>In dual duct or dual fan dual duct VAV systems 
  the boxes have many more controls</FONT></DIV>
  <DIV><FONT face=Arial size=2>including separate heat/cool and overall box 
  minimum flow; consult the DOE-2.2</FONT></DIV>
  <DIV><FONT face=Arial size=2>dictionary (<A 
  href="http://doe2.com/download/DOE-22/DOE22Vol2-Dictionary.pdf">http://doe2.com/download/DOE-22/DOE22Vol2-Dictionary.pdf</A>) 
  or eQUEST</FONT></DIV>
  <DIV><FONT face=Arial size=2>online help (although this is less complete and 
  not as up to date) for more detail.</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>When the outside air fraction 
  is set to </FONT><FONT face=Arial size=2>1 this is interpreted 
  as a minimum ventilation</FONT></DIV>
  <DIV><FONT face=Arial size=2>requirement and thus is found to be the 
  maximum value of the various defaults for</FONT></DIV>
  <DIV><FONT face=Arial size=2>the VAV box minimum flow value.  If the 
  </FONT><FONT face=Arial size=2>minimum cfm fraction is specified (on 
  the</FONT></DIV>
  <DIV><FONT face=Arial size=2>subtab mentioned above) rather than letting it 
  default, the specified value </FONT><FONT face=Arial size=2>will be 
  used</FONT></DIV>
  <DIV><FONT face=Arial size=2>for all ZONE VAV boxes in that 
  SYSTEM.</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>For example, on the system properties sheet the 
  fan tab and flow </FONT><FONT face=Arial size=2>parameters sub 
  tab,</FONT></DIV>
  <DIV><FONT face=Arial size=2>you can place a value for min flow ratio, and 
  that will become the min flow for all VAV</FONT></DIV>
  <DIV><FONT face=Arial size=2>boxes on the SV-A report </FONT><FONT 
  face=Arial size=2> ...</FONT></DIV>
  <DIV><FONT face=Arial size=2>the hourly OA fraction will then be governed by 
  the fraction of design vs. hourly values</FONT></DIV>
  <DIV><FONT face=Arial size=2>choice on the system properties sheet outdoor air 
  tab, outside air and economizer subtab.</FONT></DIV>
  <DIV><FONT face=Arial size=2>If (on the same properties sheet fans /flow 
  subtab) the min flow cfm/ft2 control is set instead,</FONT></DIV>
  <DIV><FONT face=Arial size=2>you would still </FONT><FONT face=Arial 
  size=2>get OA=1 all hours because this is one of the values compared to the 
  ventilation</FONT></DIV>
  <DIV><FONT face=Arial size=2>to choose the maximum needed minimum 
  box flow setting.  (I know the online help is a bit</FONT></DIV>
  <DIV><FONT face=Arial size=2>dated and poorly </FONT><FONT face=Arial 
  size=2>worded ... we are trying to get funding to improve it ... but this 
  information</FONT></DIV>
  <DIV><FONT face=Arial size=2>is all there, </FONT><FONT face=Arial size=2>just 
  requires a bit of a careful read.)</FONT></DIV></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>By the way, the SV-A, and other DOE-2 reports are 
  now easily examined: the eQUEST</FONT></DIV>
  <DIV><FONT face=Arial size=2>version 3.51 freeware pre-release <FONT 
  face=Arial size=2>posted on </FONT><FONT face=Arial size=2><A 
  href="http://DOE2.com/eQUEST/">http://DOE2.com/eQUEST/</A> has a new 
  simulation</FONT></FONT></DIV>
  <DIV><FONT face=Arial size=2><FONT face=Arial size=2>results details viewer 
  that </FONT><FONT face=Arial size=2>allows viewing of multiple .sim files with 
  direct access to reports through</FONT></FONT></DIV>
  <DIV><FONT face=Arial size=2><FONT face=Arial size=2>an index. This viewer can 
  be used to view .sim results file produced by any version of 
  DOE-2.2</FONT></FONT></DIV>
  <DIV><FONT face=Arial size=2><FONT face=Arial size=2>freeware, 
  </FONT></FONT><FONT face=Arial><FONT size=2>but is best used with versions 43 
  and beyond due to fully uniform report headers (in 
  those</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>versions) that the </FONT></FONT><FONT 
  face=Arial><FONT size=2>viewer uses to locate reports and error messages 
  within a .sim file.</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2></FONT></FONT> </DIV>
  <DIV><FONT face=Arial><FONT size=2>Version 3.51 of eQUEST has many other 
  improvements to both the simulation engine and interface</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>including: a 5-10 times speed increase of 
  project open and compliance simulation times, an first 
  version</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>of a BDL </FONT></FONT><FONT 
  face=Arial><FONT size=2>error manager to view an error tree to assist in 
  navigation to and fixing of model errors, and new DOE-2</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>simulation features that can be found 
  documented (with other post version 40 additions) in Volume 
  6</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>of the DOE-2.2 documentation 
  at</FONT></FONT></DIV>
  <DIV><FONT face=Arial><FONT size=2>       <A 
  href="http://doe2.com/download/DOE-22/DOE22Vol6-NewFeatures.pdf">http://doe2.com/download/DOE-22/DOE22Vol6-NewFeatures.pdf</A><FONT 
  size=+0></DIV>
  <DIV></FONT></FONT></FONT><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>This is a pre-release to allow extensive public 
  comment and review (followed by our fixing issues</FONT></DIV>
  <DIV><FONT face=Arial size=2>identified) prior to the retirement of older 
  versions; this version has been in wide use for some time</FONT></DIV>
  <DIV><FONT face=Arial size=2>now (starting with version 3.50) and appears to 
  be close to "ready for prime time."</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Happy simulating ...</FONT></DIV>
  <DIV><BR>---<BR>Jeff Hirsch<BR>James J. Hirsch & Associates<BR>Building 
  Performance Analysis Software & Consulting<BR>12185 Presilla 
  Road<BR>Camarillo, CA 93012-9243 USA<BR>phone: (805) 
  553-9000<BR>fax: (805) 532-2401<BR>email: <A 
  href="mailto:Jeff.Hirsch@DOE2.com">Jeff.Hirsch@DOE2.com</A><BR>web: <A 
  href="http://DOE2.com">http://DOE2.com</A></DIV>
  <DIV> </DIV>
  <DIV> </DIV>
  <BLOCKQUOTE dir=ltr 
  style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
    <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
    <DIV 
    style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
    <A title=keirh@bluestoneenergy.com 
    href="mailto:keirh@bluestoneenergy.com">Keir Howell</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
    href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, August 30, 2004 8:25 
    AM</DIV>
    <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] Modeling 100% OA 
    VAV systems in eQuest</DIV>
    <DIV><BR></DIV>
    <DIV><FONT face=Arial size=2></FONT><FONT face=Arial size=2>Hello. Whenever 
    I try to model a VAV system with 100% OA in eQuest, I end up with a constant 
    volume system. It seems to be multiplying the Minimum OA Ratio (which I have 
    set at 1.00) by the design air flow, rather than the hourly air flow, even 
    though I have set the Minimum OA Method to "Fraction of Hourly Flow". As far 
    as I know, I have not set any other variables (such as zonal settings) that 
    might override the system settings. Please help. Thanks,</FONT></DIV>
    <DIV><FONT face=Arial size=2></FONT> </DIV>
    <DIV><FONT face=Arial size=2>Keir Howell<BR>Bluestone Energy Services, 
    Inc.<BR>phone:    781-356-8865<BR>fax:    
    781-356-8864</FONT></DIV><PRE>==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>
=====================================================You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>