size=2>Keir,</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>I 
tried to reproduce your error but cannot get eQuest to simulate a VAV with 100% 
OA as a constant volume system.  Without seeing your input file I suggest 
the following:</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>1. 
Check the version of eQuest you are using.  I used version 3.44 build 2930 
and had no problems.  Version 3.5 is also available but I haven't spent 
much time with it yet.</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>2. I 
assume you have checked the hourly reports to verify the constant airflow.  
If not run hourly reports to verify supply airflow rate and % 
OA.</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>3. 
Check to be sure you're not using a minimum OA 
schedule.</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>4. 
Verify that at the zone level you have reset all values for OA calculations 
to zero</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2>5. If you have manually entered a design CFM, it may not be large 
enough to meet the load and as a result the VAV is not modulating.  I 
suggest reseting the Design CFM to default and letting eQuest size the 
air-flow rate.  Another way to check this is to look at the SS-O 
reports.  If zone temp setpoint is not being met you will have a wide 
distribution of hours at different temp ranges.  This could happen if you 
have a large internal cooling load that isn't very sensitive to fluctuations in 
outdoor temperature.  </FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2>6.  Try changing the minimum outside air ratio to 0.25 or some value 
other than 1.0, does the hourly supply air flow change?  It shouldn't 
change because supply air flow is dependent on the loads at the zone 
level.  </FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>Those 
are some of the things I would try to help understand what is going on.  It 
may be that the model is doing what it is supposed to.  
</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff size=2>I hope 
this helps.</FONT></SPAN></DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=700380920-30082004><FONT face=Arial color=#0000ff 
size=2>Mike</FONT></SPAN></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV align=left><B><SPAN lang=en-us><FONT size=2>Michael Tillou, 
PE</FONT><BR></SPAN><SPAN lang=en-us><FONT size=2>etc Group, 
Inc.</FONT></SPAN><SPAN lang=en-us><BR></SPAN><SPAN lang=en-us><FONT size=2>PO 
Box 7, <SPAN class=700380920-30082004>Williamstown</SPAN>, MA 
01</FONT></SPAN></B><SPAN lang=en-us></SPAN><B><SPAN lang=en-us><FONT 
size=2>2<SPAN class=700380920-30082004>6</SPAN>7</FONT></SPAN><SPAN 
lang=en-us><BR><FONT size=2>ph. (413) 458-9870 </FONT></SPAN></B><B><SPAN 
lang=en-us><FONT color=#000080><FONT size=2><BR></FONT></FONT></SPAN><SPAN 
lang=en-us><FONT face="Arial Narrow"> </FONT></SPAN></B> </DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> postman@gard.com 
  [mailto:postman@gard.com] <B>On Behalf Of </B>Keir Howell<BR><B>Sent:</B> 
  Monday, August 30, 2004 11:26 AM<BR><B>To:</B> 
  BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Modeling 100% OA VAV systems 
  in eQuest<BR><BR></FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT><FONT face=Arial size=2>Hello. Whenever I 
  try to model a VAV system with 100% OA in eQuest, I end up with a constant 
  volume system. It seems to be multiplying the Minimum OA Ratio (which I have 
  set at 1.00) by the design air flow, rather than the hourly air flow, even 
  though I have set the Minimum OA Method to "Fraction of Hourly Flow". As far 
  as I know, I have not set any other variables (such as zonal settings) that 
  might override the system settings. Please help. Thanks,</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Keir Howell<BR>Bluestone Energy Services, 
  Inc.<BR>phone:    781-356-8865<BR>fax:    
  781-356-8864</FONT></DIV><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>