<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=925493617-23072004>I'd 
like to summarize all the responses and my findings about PV modeling in 
eQuest.  Specially thank Scott Criswell for pointing me to the right 
directions on this simulation skill.  Basically three steps to model a PV 
array system in eQuest: </SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=925493617-23072004>Step 
1: Create PV Module under Utility and Rate Section</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=925493617-23072004><FONT 
color=#0000ff>Step 2: Create a corresponding Electric Generator <FONT 
face="Times New Roman" size=3>ELEC-GENERATOR on the same 
section</FONT></FONT></SPAN></FONT></DIV>
<DIV><FONT color=#0000ff><SPAN class=925493617-23072004>Step 3: Under the 
Utility Rate command, add Buy/Sell command if selling back electricity generated 
by PV systems to the grid</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=925493617-23072004><FONT 
face="Times New Roman" color=#000000 size=3>The description of PV module 
parameters is included in the DOE-2.2 Dictionary volume of documentation.  
And example of a small commercial PV system is included in the <U>2nd to last 
page (or there abouts)</U> of the same documentation.  </FONT><A 
class=moz-txt-link-freetext 
href="http://doe2.com/download/DOE-22/DOE22Vol2-Dictionary.pdf"><FONT 
face="Times New Roman" 
size=3>http://doe2.com/download/DOE-22/DOE22Vol2-Dictionary.pdf</FONT></A><FONT 
face="Times New Roman" color=#000000 size=3>   (~2.6 
MB)</FONT><BR></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=925493617-23072004>Happy 
Simulation!</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004>Bing</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=925493617-23072004><!-- Converted from text/rtf format -->
<P><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 
size=2>____________________</FONT></SPAN> <BR><SPAN lang=en-us><FONT 
face="Comic Sans MS" color=#808000 size=2>Bing Liu, PE, CEM</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 size=2>LEED 
Accredited Professional<U></U></FONT><U></U><U></U></SPAN> <BR><SPAN 
lang=en-us><FONT face="Comic Sans MS" color=#808000 size=1>Pacific Northwest 
National Lab</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Comic Sans MS" 
color=#808000 size=1>902 Battelle Blvd. MSIN: K5-16</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT face="Comic Sans MS" color=#808000 size=1>Richland, WA 
99352</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Comic Sans MS" 
color=#808000 size=1>Tel:     509.375.3710</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 
size=1>Fax:    509.375.3614</FONT></SPAN> 
</P></SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=925493617-23072004> </DIV></SPAN></FONT>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV></DIV>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT 
  face=Tahoma size=2>-----Original Message-----<BR><B>From:</B> postman@gard.com 
  [mailto:postman@gard.com] <B>On Behalf Of </B>Liu, Bing<BR><B>Sent:</B> 
  Wednesday, July 21, 2004 5:46 PM<BR><B>To:</B> 
  BLDG-SIM@gard.com<BR><B>Subject:</B> [BLDG-SIM] Photovoltaic Module in 
  eQuest<BR><BR></FONT></DIV><!-- Converted from text/rtf format -->
  <P><SPAN lang=en-us><FONT face=Arial size=2>I am trying to simulate the 
  electricity generated by using photovoltaic in eQuest.  After creating 
  the PV module under the Utility Section and making the simulation run, REPORT 
  PS-H (Loads and Energy Usage for Photovoltaic Module 1) shows ZERO kWh 
  generated by PV module.  Did I miss something here?  Anyone has 
  experience with PV module in eQuest?</FONT></SPAN></P>
  <P><SPAN lang=en-us><FONT face=Arial size=2>Thanks,</FONT></SPAN> </P>
  <P><SPAN lang=en-us><FONT face=Arial size=2>Bing</FONT></SPAN> </P>
  <P><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 
  size=2>____________________</FONT></SPAN> <BR><SPAN lang=en-us><FONT 
  face="Comic Sans MS" color=#808000 size=2>Bing Liu, PE, CEM</FONT></SPAN> 
  <BR><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 size=2>LEED 
  Accredited Professional<U></U></FONT><U></U><U></U></SPAN> <BR><SPAN 
  lang=en-us><FONT face="Comic Sans MS" color=#808000 size=1>Pacific Northwest 
  National Lab</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Comic Sans MS" 
  color=#808000 size=1>902 Battelle Blvd. MSIN: K5-16</FONT></SPAN> <BR><SPAN 
  lang=en-us><FONT face="Comic Sans MS" color=#808000 size=1>Richland, WA 
  99352</FONT></SPAN> <BR><SPAN lang=en-us><FONT face="Comic Sans MS" 
  color=#808000 size=1>Tel:     509.375.3710</FONT></SPAN> 
  <BR><SPAN lang=en-us><FONT face="Comic Sans MS" color=#808000 
  size=1>Fax:    509.375.3614</FONT></SPAN> </P><BR><BR><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>