style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Alec,</SPAN><?xml:namespace prefix = 
o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT size=3><FONT 
face="Times New Roman"> <o:p></o:p></FONT></FONT></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I think the intent of the code is 
exactly to penalize an HVAC system (or equipment) that is less 
efficient than the Code one. The choice of local floor DX unit brings about 
issues of a less efficient refrigeration, less efficient economizer control 
(i.e., waterside vs. air side), that must be offset somewhere else in the 
building, i.e. more efficient glazing...Furthermore, nowhere in the code it is 
mentioned that the consistent HVAC systems must be used. </SPAN><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">It has been my experience that for 
the ecb model an air-side economizer should be used.</SPAN><o:p></o:p></P>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">In 
general, the situation you have described is fairly common, and unfortunately 
the proposed design building is thus often penalized.</SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"></SPAN> </DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Konstantin 
Babets</SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Jaros 
Baum and Bolles</SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">(212) 
530 9455</SPAN></DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"></SPAN> </DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"></SPAN> </DIV>
<DIV><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"></SPAN></FONT>----- 
Original Message ----- </DIV>
<BLOCKQUOTE dir=ltr 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=astevens@dmiinc.com href="mailto:astevens@dmiinc.com">Alec 
  Stevens</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A title=BLDG-SIM@gard.com 
  href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Tuesday, July 13, 2004 12:04 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [BLDG-SIM] another 90.1 ECB 
  question</DIV>
  <DIV><BR></DIV>
  <DIV><FONT face=Arial size=2>Hello,</FONT></DIV>
  <DIV><FONT face=Arial size=2>In light of recent questions to the list on the 
  ASHRAE ECB method, here is one that we are working on: </FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>The proposed multi-story office building will 
  have a cooling tower serving a condenser water loop.  Each floor has a 
  VAV air handling unit with a water-cooled DX compressor, heat is rejected 
  to the CW loop.  Economizer cooling is provided on the water side via 
  separate WSE coils.  OA is provided to each floor's AHU, but 100% OA is 
  not provided.  The waterside economizer coils can pre-cool the mixed air 
  when the CW temperature is low enough, and can run in series with the DX 
  coils.  </FONT></DIV>
  <DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Regarding the base budget building, the system 
  map in 90.1 seems to indicate that a central chiller plant is required for 
  this type of building (System type 2).  However, in general I think we 
  are supposed to use consistent HVAC systems in the base budget building and 
  the proposed building.  I want to know if we can use the floor-by-floor 
  water cooled units in the base budget building so as to be consistent and to 
  not penalize the energy performance of the floor-by-floor DX units compared to 
  a chiller plant.</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Also, the language is confusing to us regarding 
  air vs. water side economizers.  In 11.4.3, we are directed to include an 
  economizer that meets the requirements of 6.3.1, where the standard 
  seems to indicate that a system must have either air <EM>or</EM> water side 
  economizers.  However, in 11.4.3e, the standard seems to say that system 
  type 2 must use airside economizers.  The proposed design seems to meet 
  the requirements for waterside economizers, but I don't want to penalize the 
  proposed design for not having 100% OA capability.  </FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Your thoughts on the above questions would be 
  appreciated.</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Thanks!</FONT></DIV>
  <DIV><FONT face=Arial size=2>Sincerely,</FONT></DIV>
  <DIV> </DIV>
  <DIV><FONT face=Arial size=2>Alec Stevens, PE, LEED AP<BR>DMI<BR>450 Lexington 
  St, Newton, MA 02466<BR>p: 617-527-1525 x105  f: 617-527-6606<BR>e: <A 
  href="mailto:astevens@dmiinc.com">astevens@dmiinc.com</A></FONT></DIV></DIV><PRE>
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BLOCKQUOTE><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>