<DIV><FONT face=Arial size=2>Hello,</FONT></DIV>
<DIV><FONT face=Arial size=2>In light of recent questions to the list on the 
ASHRAE ECB method, here is one that we are working on: </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>The proposed multi-story office building will have 
a cooling tower serving a condenser water loop.  Each floor has a 
VAV air handling unit with a water-cooled DX compressor, heat is rejected 
to the CW loop.  Economizer cooling is provided on the water side via 
separate WSE coils.  OA is provided to each floor's AHU, but 100% OA is not 
provided.  The waterside economizer coils can pre-cool the mixed air when 
the CW temperature is low enough, and can run in series with the DX coils.  
</FONT></DIV>
<DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Regarding the base budget building, the system map 
in 90.1 seems to indicate that a central chiller plant is required for this type 
of building (System type 2).  However, in general I think we are supposed 
to use consistent HVAC systems in the base budget building and the proposed 
building.  I want to know if we can use the floor-by-floor water cooled 
units in the base budget building so as to be consistent and to not penalize the 
energy performance of the floor-by-floor DX units compared to a chiller 
plant.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Also, the language is confusing to us regarding air 
vs. water side economizers.  In 11.4.3, we are directed to include an 
economizer that meets the requirements of 6.3.1, where the standard 
seems to indicate that a system must have either air <EM>or</EM> water side 
economizers.  However, in 11.4.3e, the standard seems to say that system 
type 2 must use airside economizers.  The proposed design seems to meet the 
requirements for waterside economizers, but I don't want to penalize the 
proposed design for not having 100% OA capability.  </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Your thoughts on the above questions would be 
appreciated.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thanks!</FONT></DIV>
<DIV><FONT face=Arial size=2>Sincerely,</FONT></DIV>
<DIV> </DIV>
<DIV><FONT face=Arial size=2>Alec Stevens, PE, LEED AP<BR>DMI<BR>450 Lexington 
St, Newton, MA 02466<BR>p: 617-527-1525 x105  f: 617-527-6606<BR>e: <A 
href="mailto:astevens@dmiinc.com">astevens@dmiinc.com</A></FONT></DIV></DIV><PRE>

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM@GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></BODY></HTML>