You can model the exhaust fans as the Return fan. Set the
MIN-OUTSIDE-AIR to 1. To model VAV you need to set a
MIN-CFM-SCHEDULE to match the behaviour of the fume hoods opening and
closing (it is tricky to determine exactly this behavior). This way
you can attempt to capture any heat recovery available.<br><br>
<br>
<blockquote type=cite class=cite cite>"urn:schemas-microsoft-com:office:office"
xmlns:w = "urn:schemas-microsoft-com:office:word" xmlns:st1 =
"urn:schemas-microsoft-com:office:smarttags"> <br>
<font face="arial" size=2>Unless you can predict exactly how the fume
cupbards will be utilised, is there a need to model them as VAV? I
used DOE-2.2 a couple of years ago to look at a similar arrangement and
we diversified the fume cupboards so that we effectively modelled a
constant exhaust rate. Set this up as a parameter and then run for
different values to see how sensitive performane is to fume cupboard use
/ diversity ...<br>
Graham<br>
</font>
<dl>
<dd>----- Original Message ----- <br>
<dd>From:</b> <a href="mailto:razerbegi@rmhgroup.com">Azerbegi, Renee</a>
<br>
<dd>To:</b> <a href="mailto:BLDG-SIM@gard.com">BLDG-SIM@gard.com</a> <br>
<dd>Sent:</b> Saturday, March 20, 2004 3:13 AM<br>
<dd>Subject:</b> [BLDG-SIM] VAV fume hood exhaust<br><br>
<dd><font face="arial" size=2 color="#0000FF">Has anyone modeled a VAV fume hood exhaust for a laboratory in eQuest? Since the laboratory requires 100% outside air, a return fan is not simulated obviously. The exhaust fan part on the air-handling unit fan page of eQuest doesn't seem to be able to be modeled. If I put the exhaust in each zone, then I can't specify that the fans are VAV. Please let me know if you have had luck with modeling this type of system in eQuest.<br>
<dd>Thanks,<br>
<dd>Renee<br>
</font>
<dd> <br>
<dd> <br>
<dd><font face="arial" size=2 color="#0000FF">Renee Azerbegi<br>
<dd>RMH Group<br>
<dd>Lakewood, Colorado<br>
<dd>303-239-0909<br>
</font>
<dd> <br>
<dd> <br>
<dd> <br><br>
</dl><br><br>
<br>
This email was scanned by SC E-mail Anti-Virus Agent at 9:13:14 AM 3/19/2004 the RMH Group, Inc.<br><br>
<br><br>
----><br>
This email and any files transmitted with it are confidential and intended solely for the use<br>
of the individual or entity to whom they are addressed. If you have received this email in<br>
error please immediately notify the RMH Group Inc. by telephone at (303) 239-0909 or<br>
send a reply to Services@RMHgroup.com with "Return to sender" in the subject line.<br>
<----<br><br>
<pre>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</pre><font face="Courier New, Courier"></font><br>
<pre>
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</pre><font face="Courier New, Courier"></blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones, P.Eng.<br>
14 Oneida Avenue<br>
Toronto, ON M5J2E3<br>
Tel. 416 203-7465<br>
Fax. 416 946-1005</font><PRE>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@GARD.COM
</PRE></body>
</html>